|
Energyplus does not model the HVAC system using a dead band. Meaning that the system does not turn on for a period of time and then turn off for a period of time as the zone temperature floats between two limits (i.e., a 1 or 2 degree dead band). Instead, Energyplus cycles the compressor on and off at a cycling rate that mimics a real system. The zone temperature will not change if the system has the capacity to meet the thermostat set point. If you really want the zone temperature to change, you will need to control the availability schedule of the HVAC system to turn on and off based on the zone temperature. This can be done using EMS programming. Here is a response to another user describing an EMS program used to control the ideal loads air system using a dead band. This EMS program can be applied to any HVAC system type with some modifications. Energyplus does not model a thermostat as you describe, instead it maintains the set point to meet a load. You can, however, create an EMS program to accomplish this type of control. The second input to the ideal loads air system is the availability schedule. ZoneHVAC:IdealLoadsAirSystem, Name, Availability Schedule Name, When the schedule is > 0, the system is "active". And if you choose the cooling/heating set points to be 24C and 19C, respectively, then the system will be on for cooling if the temp is above 24C, and on for heating if the temp is below 19C. Heating ON at 15 oC and OFF at 19 oC Cooling ON at 27 oC and OFF at 24 oC. The example file EMSCustomSchedule.idf shows how to use the EMS system to manipulate a schedule. In this example, the schedule values are the cooling/heating set points. In your file, the schedule values will determine if the ideal loads air system is "active" (values > 0). Your actuator will be the ideal loads air system "Availability Schedule" EnergyManagementSystem:Actuator, myIdealLoadsAirSys_SCH, !- Name ILAS_SCH, !- Actuated Component Unique Name Schedule:Constant, !- Actuated Component Type Schedule Value; !- Actuated Component Control Type You will also need to read the zone temperature, this is done using a sensor. EnergyManagementSystem:Sensor, ZoneTemp, !- Name East Zone, !- Output:Variable or Output:Meter Index Key Name Zone Mean Air Temperature; !- Output:Variable or Output:Meter Name And your program will set the availability schedule value to 0 when you want the system off, and to 1 when you want the system on. You may also be able to define the same control logic by changing the heating/cooling set point temperatures as the example file shows. But looking to control the availability of the ideal loads air system will look something like this. EnergyManagementSystem:ProgramCallingManager, ILAS OnOff Management, InsideHVACSystemIterationLoop, MyAvailSchSetpointProg; EnergyManagementSystem:Program, MyAvailSchSetpointProg, IF (ZoneTemp > 27), Set CoolingEnabled = 1.0, ENDIF, IF (ZoneTemp < 24.01), Set CoolingEnabled = 0.0, ENDIF, IF (ZoneTemp 18.99), Set HeatingEnabled = 0.0, ENDIF, IF (HeatingEnabled > 0.5 || CoolingEnabled > 0.5), Set myIdealLoadsAirSys_SCH = 1.0, ELSE, Set myIdealLoadsAirSys_SCH = 0.0, ENDIF; ! also turn on reporting to the edd file so you can review the execution of the EMS program. Output:EnergyManagementSystem, Verbose, !- Actuator Availability Dictionary Reporting Verbose, !- Internal Variable Availability Dictionary Reporting Verbose; !- EMS Runtime Language Debug Output Level I tried this using the example file PurchAirTables.idf. 1) I created a schedule to be used in the East Zone ideal loads air system object. Schedule:Constant,ILAS_SCH,Any Number,1.0; 2) I applied that scedule to the East Zone ideal loads air system ZoneHVAC:IdealLoadsAirSystem, Zone2Air, !- Name ILAS_SCH, !- Availability Schedule Name 3) I added the EMS program above to the input file and focused on the "East Zone" to get the program working. I added the data dictionary as output (turns on the rdd file)and this schedule report variable to the input file. Output:VariableDictionary,IDF; Output:Variable,ILAS_SCH,Schedule Value,timestep; When viewing the outputs (*.csv) I see that the ideal loads air system is turning on and off each time step. That is because the ideal loads air system has unlimited capacity. ZoneHVAC:IdealLoadsAirSystem, Zone2Air, !- Name ILAS_SCH, !- Availability Schedule Name NODE_2, !- Zone Supply Air Node Name , !- Zone Exhaust Air Node Name 50, !- Maximum Heating Supply Air Temperature {C} 13, !- Minimum Cooling Supply Air Temperature {C} 0.015, !- Maximum Heating Supply Air Humidity Ratio {kg-H2O/kg-air} 0.009, !- Minimum Cooling Supply Air Humidity Ratio {kg-H2O/kg-air} NoLimit, !- Heating Limit autosize, !- Maximum Heating Air Flow Rate {m3/s} , !- Maximum Sensible Heating Capacity {W} NoLimit, !- Cooling Limit autosize, !- Maximum Cooling Air Flow Rate {m3/s} , !- Maximum Total Cooling Capacity {W} I changed this object to: ZoneHVAC:IdealLoadsAirSystem, Zone2Air, !- Name ILAS_SCH, !- Availability Schedule Name NODE_2, !- Zone Supply Air Node Name , !- Zone Exhaust Air Node Name 50, !- Maximum Heating Supply Air Temperature {C} 13, !- Minimum Cooling Supply Air Temperature {C} 0.015, !- Maximum Heating Supply Air Humidity Ratio {kg-H2O/kg-air} 0.009, !- Minimum Cooling Supply Air Humidity Ratio {kg-H2O/kg-air} LimitCapacity, !- Heating Limit autosize, !- Maximum Heating Air Flow Rate {m3/s} 4500, !- Maximum Sensible Heating Capacity {W} LimitCapacity, !- Cooling Limit autosize, !- Maximum Cooling Air Flow Rate {m3/s} 4500, !- Maximum Total Cooling Capacity {W} The output (*.csv) now appears to have the control you described (see jpg). The V7 input file I used is also attached. I used the EMS_Application_Guide.pdf and InputOutputReference.pdf files as references. On 1/11/2012 4:10 AM, Tooran wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |