[EnergyPlus_Support] Re: Modeling single-side natural ventilation



Hi, use the "detailed opening" for bi-directional flow. One opening will be not enough for AFN, so you need to defind a secound one like a tiny crack on some other wall, which is too small to influence the simulation. That should work.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "JPE" <spincycle45@...> wrote:
>
> David -- Thank you for your response.
> 
> By "outside pressure node", are you referring to creating an External Node (under AirflowNetwork:MultiZone) for each window?
> 
> I understand that EnergyPlus does not like to do bi-directional flow through horizontal openings (E+ In/Output Reference, p.939) so I figured to try subdividing the larger windows into multiple horizontal stacking windows.  Doing so (theoretically) each window could have a uni-directional airflow, either in or out of the zone.
> 
> Using this methodology my model now consists of two window groups, each with five horizontal windows stacked above one another.
> 
> Thoughts?
> 
> Cheers -- James
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/