Actually the Zone/Sys Moisture Load Rate Predicted should be the same as either (2) or (3) or be equal to 0, but I don't see that using these numbers. To convert kgwater/s to Watts, multiply by the heat of vaporization of water. Approximately 2.2E6 - 2.5E6 depending on the zone temperature and humidity ratio. Did you read the report variable descriptions in the Input Output Reference document? Just search for the report variable name. Zone/Sys Moisture Load Rate Predicted[kgWater/sec] This is the predicted latent (moisture) load in kgwater/s required to meet the current zone humidistat setpoint. A positive value indicates a humidification load, a negative value indicates a dehumidification load. For a dual setpoint humidistat, the value is zero when the controlled zone’s relative humidity is between the defined humidifying and dehumidifying setpoints. This moisture load rate is calculated and reported from the Predict step in the Zone Predictor-Corrector module. For nearly all equipment types, the Predictor-Corrector evaluates the active humidistat setpoints, determines if the zone requires humidification or dehumidification, and then passes this single load to the equipment for the single setpoint humidistat case. This value is not multiplied by zone or group multipliers. Zone/Sys Moisture Load Rate Predicted to Humidifying Setpoint [kgWater/sec] This is the predicted latent (moisture) load in kgwater/s required to meet the current zone humidistat humidifying setpoint. This is calculated and reported from the Predict step in the Zone Predictor-Corrector module. For nearly all equipment types, the Predictor-Corrector evaluates the active humidistat humidifying setpoints, determines if the zone requires humidification or not, and then passes this load to the equipment for the case of a dual setpoint humidistat (see Zone/Sys Moisture Load Rate Predicted, above, for single setpoint humidistat case). This value is multiplied by zone or group multipliers. Zone/Sys Moisture Load Rate Predicted to Dehumidifying Setpoint [kgWater/sec] This is the predicted latent (moisture) load in kgwater/s required to meet the current zone humidistat dehumidifying setpoint. This is calculated and reported from the Predict step in the Zone Predictor-Corrector module. For nearly all equipment types, the Predictor-Corrector evaluates the active humidistat humidifying setpoints, determines if the zone requires dehumidification or not, and then passes this load to the equipment for a dual setpoint humidistat (see Zone/Sys Moisture Load Rate Predicted, above, for single setpoint humidistat case). This value is multiplied by zone or group multipliers. On 1/12/2012 3:27 PM, techneeer12 wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |