[EnergyPlus_Support] Re: Simple Heating System



Hello Lyuben,

i want the model the same as you modeled , but i want to know did you validate your results?i must be sure about my result but i dontknow how i can validate it ?

thanks

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Lyuben Barosow <lbarosow@...> wrote:
>
> Hello Everyone,
> I am new to EnergyPlus and I need your help!
> 
> Using OpenStudio I created a very simple single-zone building 10m x 10m x 2.85m. 
> I used the default constructions that OpenStudio assigned to the building 
> envelope.
> I am trying to model a very basic water heating system (no infiltration, 
> ventilation or cooling defined). The system consists of:
> 1) Boiler
> 2) Circulation pump
> 3) Radiators
> 
> I use the following components to model the system in EnergyPlus:
> 1) Boiler:HotWater
> 2) Pump:VariableSpeed
> 3) ZoneHVAC:Baseboard:Convective:Water
> 
> I set the elements to be autosized.
> I created a Heatign Setpoint Schedule, where I specified that during the 5:00 - 
> 19:00 period a temperature of 21 degrees should be maintained and also 15.6 
> degrees during the rest of the time.
> 
> As a result of the simulation I get this warning:
> ************* Beginning Zone Sizing Calculations
>    ** Warning ** Calculated design cooling load for zone=ZONE ONE is zero.
>    **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
> 
> Also the .eso file reports the Zone Mean Air Temperature, where the values 
> reported do not match the time and the corresponding temperature as specified in 
> the Heating Setpoint Schedule.
> 
> My questions are:
> 1) Is the system properly modeled using ZoneHVAC:Baseboard:Convective:Water?
> 2) Why am I getting this warning and what can I do about it?
> 3) Why the zone mean temperature values in results differ from the temperatures 
> set in the schedule?
> 
> Thank you very much!
> Lyuben Barosow
> 
> 
> Here is the .idf file.
> ----------------------------------------------------------------------------------------------------
> 
> 
> 
> !-Generator IDFEditor 1.38a
> !-Option SortedOrder
> 
> !-NOTE: All comments with '!-' are ignored by the IDFEditor and are generated 
> automatically.
> !-      Use '!' comments if they need to be retained when using the IDFEditor.
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: VERSION ===========
> 
> Version,
>     6.0;                     !- Version Identifier
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SIMULATIONCONTROL ===========
> 
> SimulationControl,
>     Yes,                     !- Do Zone Sizing Calculation
>     No,                      !- Do System Sizing Calculation
>     Yes,                     !- Do Plant Sizing Calculation
>     Yes,                     !- Run Simulation for Sizing Periods
>     Yes;                     !- Run Simulation for Weather File Run Periods
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: BUILDING ===========
> 
> Building,
>     BBH,                     !- Name
>     0.0,                     !- North Axis {deg}
>     City,                    !- Terrain
>     0.04,                    !- Loads Convergence Tolerance Value
>     0.4,                     !- Temperature Convergence Tolerance Value {deltaC}
>     FullInteriorAndExterior, !- Solar Distribution
>     25;                      !- Maximum Number of Warmup Days
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: TIMESTEP ===========
> 
> Timestep,
>     4;                       !- Number of Timesteps per Hour
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SITE:LOCATION ===========
> 
> Site:Location,
>     SOFIA_BGR Design_Conditions,  !- Name
>     42.73,                   !- Latitude {deg}
>     23.38,                   !- Longitude {deg}
>     2.00,                    !- Time Zone {hr}
>     595.00;                  !- Elevation {m}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SIZINGPERIOD:DESIGNDAY ===========
> 
> SizingPeriod:DesignDay,
>     SOFIA Ann Htg 99% Condns DB,  !- Name
>     -9.9,                    !- Maximum Dry-Bulb Temperature {C}
>     0.0,                     !- Daily Temperature Range {deltaC}
>     -9.9,                    !- Humidity Indicating Conditions at Maximum 
> Dry-Bulb
>     94378.,                  !- Barometric Pressure {Pa}
>     1.1,                     !- Wind Speed {m/s}
>     270,                     !- Wind Direction {deg}
>     0.00,                    !- Sky Clearness
>     0,                       !- Rain Indicator
>     0,                       !- Snow Indicator
>     21,                      !- Day of Month
>     1,                       !- Month
>     WinterDesignDay,         !- Day Type
>     0,                       !- Daylight Saving Time Indicator
>     WetBulb;                 !- Humidity Indicating Type
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SIZINGPERIOD:WEATHERFILEDAYS ===========
> 
> SizingPeriod:WeatherFileDays,
>     Winter,                  !- Name
>     10,                      !- Begin Month
>     14,                      !- Begin Day of Month
>     4,                       !- End Month
>     24,                      !- End Day of Month
>     Monday,                  !- Day of Week for Start Day
>     Yes,                     !- Use Weather File Daylight Saving Period
>     Yes;                     !- Use Weather File Rain and Snow Indicators
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: RUNPERIOD ===========
> 
> RunPeriod,
>     Winter,                  !- Name
>     10,                      !- Begin Month
>     15,                      !- Begin Day of Month
>     4,                       !- End Month
>     23,                      !- End Day of Month
>     UseWeatherFile,          !- Day of Week for Start Day
>     Yes,                     !- Use Weather File Holidays and Special Days
>     Yes,                     !- Use Weather File Daylight Saving Period
>     No,                      !- Apply Weekend Holiday Rule
>     Yes,                     !- Use Weather File Rain Indicators
>     Yes,                     !- Use Weather File Snow Indicators
>     1;                       !- Number of Times Runperiod to be Repeated
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SITE:GROUNDTEMPERATURE:BUILDINGSURFACE 
> ===========
> 
> Site:GroundTemperature:BuildingSurface,
>     20.03,                   !- January Ground Temperature {C}
>     20.03,                   !- February Ground Temperature {C}
>     20.13,                   !- March Ground Temperature {C}
>     20.30,                   !- April Ground Temperature {C}
>     20.43,                   !- May Ground Temperature {C}
>     20.52,                   !- June Ground Temperature {C}
>     20.62,                   !- July Ground Temperature {C}
>     20.77,                   !- August Ground Temperature {C}
>     20.78,                   !- September Ground Temperature {C}
>     20.55,                   !- October Ground Temperature {C}
>     20.44,                   !- November Ground Temperature {C}
>     20.20;                   !- December Ground Temperature {C}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SCHEDULETYPELIMITS ===========
> 
> ScheduleTypeLimits,
>     Any Number;              !- Name
> 
> ScheduleTypeLimits,
>     Fraction,                !- Name
>     0.0,                     !- Lower Limit Value
>     1.0,                     !- Upper Limit Value
>     CONTINUOUS;              !- Numeric Type
> 
> ScheduleTypeLimits,
>     Temperature,             !- Name
>     -60,                     !- Lower Limit Value
>     200,                     !- Upper Limit Value
>     CONTINUOUS;              !- Numeric Type
> 
> ScheduleTypeLimits,
>     On/Off,                  !- Name
>     0,                       !- Lower Limit Value
>     1,                       !- Upper Limit Value
>     DISCRETE;                !- Numeric Type
> 
> ScheduleTypeLimits,
>     Control Type,            !- Name
>     0,                       !- Lower Limit Value
>     4,                       !- Upper Limit Value
>     DISCRETE;                !- Numeric Type
> 
> ScheduleTypeLimits,
>     Humidity,                !- Name
>     10,                      !- Lower Limit Value
>     90,                      !- Upper Limit Value
>     CONTINUOUS;              !- Numeric Type
> 
> ScheduleTypeLimits,
>     Number;                  !- Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SCHEDULE:COMPACT ===========
> 
> Schedule:Compact,
>     Heating Setpoint Schedule,  !- Name
>     Temperature,             !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays,            !- Field 2
>     Until: 05:00,            !- Field 3
>     15.6,                    !- Field 4
>     Until: 19:00,            !- Field 5
>     21.0,                    !- Field 6
>     Until: 24:00,            !- Field 7
>     15.6;                    !- Field 8
> 
> Schedule:Compact,
>     Baseboard Operation Schedule,  !- Name
>     On/Off,                  !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays,            !- Field 2
>     Until: 24:00,            !- Field 3
>     1;                       !- Field 4
> 
> Schedule:Compact,
>     Zone One Control Type Schedule,  !- Name
>     Control Type,            !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays,            !- Field 2
>     Until: 24:00,            !- Field 3
>     1;                       !- Field 4
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: MATERIAL ===========
> 
> Material,
>     F08 Metal surface,       !- Name
>     Smooth,                  !- Roughness
>     0.0008,                  !- Thickness {m}
>     45.28,                   !- Conductivity {W/m-K}
>     7824,                    !- Density {kg/m3}
>     500;                     !- Specific Heat {J/kg-K}
> 
> Material,
>     I01 25mm insulation board,  !- Name
>     MediumRough,             !- Roughness
>     0.0254,                  !- Thickness {m}
>     0.03,                    !- Conductivity {W/m-K}
>     43,                      !- Density {kg/m3}
>     1210;                    !- Specific Heat {J/kg-K}
> 
> Material,
>     I02 50mm insulation board,  !- Name
>     MediumRough,             !- Roughness
>     0.0508,                  !- Thickness {m}
>     0.03,                    !- Conductivity {W/m-K}
>     43,                      !- Density {kg/m3}
>     1210;                    !- Specific Heat {J/kg-K}
> 
> Material,
>     G01a 19mm gypsum board,  !- Name
>     MediumSmooth,            !- Roughness
>     0.019,                   !- Thickness {m}
>     0.16,                    !- Conductivity {W/m-K}
>     800,                     !- Density {kg/m3}
>     1090;                    !- Specific Heat {J/kg-K}
> 
> Material,
>     M11 100mm lightweight concrete,  !- Name
>     MediumRough,             !- Roughness
>     0.1016,                  !- Thickness {m}
>     0.53,                    !- Conductivity {W/m-K}
>     1280,                    !- Density {kg/m3}
>     840;                     !- Specific Heat {J/kg-K}
> 
> Material,
>     F16 Acoustic tile,       !- Name
>     MediumSmooth,            !- Roughness
>     0.0191,                  !- Thickness {m}
>     0.06,                    !- Conductivity {W/m-K}
>     368,                     !- Density {kg/m3}
>     590;                     !- Specific Heat {J/kg-K}
> 
> Material,
>     M01 100mm brick,         !- Name
>     MediumRough,             !- Roughness
>     0.1016,                  !- Thickness {m}
>     0.89,                    !- Conductivity {W/m-K}
>     1920,                    !- Density {kg/m3}
>     790;                     !- Specific Heat {J/kg-K}
> 
> Material,
>     M15 200mm heavyweight concrete,  !- Name
>     MediumRough,             !- Roughness
>     0.2032,                  !- Thickness {m}
>     1.95,                    !- Conductivity {W/m-K}
>     2240,                    !- Density {kg/m3}
>     900;                     !- Specific Heat {J/kg-K}
> 
> Material,
>     M05 200mm concrete block,!- Name
>     MediumRough,             !- Roughness
>     0.2032,                  !- Thickness {m}
>     1.11,                    !- Conductivity {W/m-K}
>     800,                     !- Density {kg/m3}
>     920;                     !- Specific Heat {J/kg-K}
> 
> Material,
>     G05 25mm wood,           !- Name
>     MediumSmooth,            !- Roughness
>     0.0254,                  !- Thickness {m}
>     0.15,                    !- Conductivity {W/m-K}
>     608,                     !- Density {kg/m3}
>     1630;                    !- Specific Heat {J/kg-K}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: MATERIAL:AIRGAP ===========
> 
> Material:AirGap,
>     F04 Wall air space resistance,  !- Name
>     0.15;                    !- Thermal Resistance {m2-K/W}
> 
> Material:AirGap,
>     F05 Ceiling air space resistance,  !- Name
>     0.18;                    !- Thermal Resistance {m2-K/W}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: WINDOWMATERIAL:GLAZING ===========
> 
> WindowMaterial:Glazing,
>     Clear 3mm,               !- Name
>     SpectralAverage,         !- Optical Data Type
>     ,                        !- Window Glass Spectral Data Set Name
>     0.003,                   !- Thickness {m}
>     0.837,                   !- Solar Transmittance at Normal Incidence
>     0.075,                   !- Front Side Solar Reflectance at Normal Incidence
>     0.075,                   !- Back Side Solar Reflectance at Normal Incidence
>     0.898,                   !- Visible Transmittance at Normal Incidence
>     0.081,                   !- Front Side Visible Reflectance at Normal 
> Incidence
>     0.081,                   !- Back Side Visible Reflectance at Normal 
> Incidence
>     0,                       !- Infrared Transmittance at Normal Incidence
>     0.84,                    !- Front Side Infrared Hemispherical Emissivity
>     0.84,                    !- Back Side Infrared Hemispherical Emissivity
>     0.9;                     !- Conductivity {W/m-K}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: WINDOWMATERIAL:GAS ===========
> 
> WindowMaterial:Gas,
>     Air 13mm,                !- Name
>     Air,                     !- Gas Type
>     0.0127;                  !- Thickness {m}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: CONSTRUCTION ===========
> 
> Construction,
>     Exterior Floor,          !- Name
>     I02 50mm insulation board,  !- Outside Layer
>     M15 200mm heavyweight concrete;  !- Layer 2
> 
> Construction,
>     Interior Floor,          !- Name
>     F16 Acoustic tile,       !- Outside Layer
>     F05 Ceiling air space resistance,  !- Layer 2
>     M11 100mm lightweight concrete;  !- Layer 3
> 
> Construction,
>     Exterior Wall,           !- Name
>     M01 100mm brick,         !- Outside Layer
>     M15 200mm heavyweight concrete,  !- Layer 2
>     I02 50mm insulation board,  !- Layer 3
>     F04 Wall air space resistance,  !- Layer 4
>     G01a 19mm gypsum board;  !- Layer 5
> 
> Construction,
>     Interior Wall,           !- Name
>     G01a 19mm gypsum board,  !- Outside Layer
>     F04 Wall air space resistance,  !- Layer 2
>     G01a 19mm gypsum board;  !- Layer 3
> 
> Construction,
>     Exterior Roof,           !- Name
>     M11 100mm lightweight concrete,  !- Outside Layer
>     F05 Ceiling air space resistance,  !- Layer 2
>     F16 Acoustic tile;       !- Layer 3
> 
> Construction,
>     Interior Ceiling,        !- Name
>     M11 100mm lightweight concrete,  !- Outside Layer
>     F05 Ceiling air space resistance,  !- Layer 2
>     F16 Acoustic tile;       !- Layer 3
> 
> Construction,
>     Exterior Window,         !- Name
>     Clear 3mm,               !- Outside Layer
>     Air 13mm,                !- Layer 2
>     Clear 3mm;               !- Layer 3
> 
> Construction,
>     Interior Window,         !- Name
>     Clear 3mm;               !- Outside Layer
> 
> Construction,
>     Exterior Door,           !- Name
>     F08 Metal surface,       !- Outside Layer
>     I01 25mm insulation board;  !- Layer 2
> 
> Construction,
>     Interior Door,           !- Name
>     G05 25mm wood;           !- Outside Layer
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: GLOBALGEOMETRYRULES ===========
> 
> GlobalGeometryRules,
>     UpperLeftCorner,         !- Starting Vertex Position
>     Counterclockwise,        !- Vertex Entry Direction
>     Relative;                !- Coordinate System
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: ZONE ===========
> 
> Zone,
>     Zone One,                !- Name
>     0.0,                     !- Direction of Relative North {deg}
>     0.0,                     !- X Origin {m}
>     0.0,                     !- Y Origin {m}
>     0.0,                     !- Z Origin {m}
>     ,                        !- Type
>     1;                       !- Multiplier
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: BUILDINGSURFACE:DETAILED ===========
> 
> BuildingSurface:Detailed,
>     867E58,                  !- Name
>     Floor,                   !- Surface Type
>     Exterior Floor,          !- Construction Name
>     Zone One,                !- Zone Name
>     Ground,                  !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     ,                        !- View Factor to Ground
>     4,                       !- Number of Vertices
>     10.000000000000,         !- Vertex 1 X-coordinate {m}
>     10.000000000000,         !- Vertex 1 Y-coordinate {m}
>     0.000000000000,          !- Vertex 1 Z-coordinate {m}
>     10.000000000000,         !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     10.000000000000,         !- Vertex 4 Y-coordinate {m}
>     0.000000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     63F00D,                  !- Name
>     Wall,                    !- Surface Type
>     Exterior Wall,           !- Construction Name
>     Zone One,                !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     ,                        !- View Factor to Ground
>     4,                       !- Number of Vertices
>     10.000000000000,         !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     0.000000000000,          !- Vertex 1 Z-coordinate {m}
>     10.000000000000,         !- Vertex 2 X-coordinate {m}
>     10.000000000000,         !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     10.000000000000,         !- Vertex 3 X-coordinate {m}
>     10.000000000000,         !- Vertex 3 Y-coordinate {m}
>     2.850000000000,          !- Vertex 3 Z-coordinate {m}
>     10,                      !- Vertex 4 X-coordinate {m}
>     0,                       !- Vertex 4 Y-coordinate {m}
>     2.85;                    !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     BA8F9D,                  !- Name
>     Wall,                    !- Surface Type
>     Exterior Wall,           !- Construction Name
>     Zone One,                !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     ,                        !- View Factor to Ground
>     4,                       !- Number of Vertices
>     10.000000000000,         !- Vertex 1 X-coordinate {m}
>     10.000000000000,         !- Vertex 1 Y-coordinate {m}
>     2.850000000000,          !- Vertex 1 Z-coordinate {m}
>     10.000000000000,         !- Vertex 2 X-coordinate {m}
>     10.000000000000,         !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     10.000000000000,         !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     10.000000000000,         !- Vertex 4 Y-coordinate {m}
>     2.850000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     3C881D,                  !- Name
>     Wall,                    !- Surface Type
>     Exterior Wall,           !- Construction Name
>     Zone One,                !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     ,                        !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     2.850000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     10.000000000000,         !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     10,                      !- Vertex 4 X-coordinate {m}
>     0,                       !- Vertex 4 Y-coordinate {m}
>     2.85;                    !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     68E0A1,                  !- Name
>     Roof,                    !- Surface Type
>     Exterior Roof,           !- Construction Name
>     Zone One,                !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     ,                        !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     10.000000000000,         !- Vertex 1 Y-coordinate {m}
>     2.850000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     2.850000000000,          !- Vertex 2 Z-coordinate {m}
>     10.000000000000,         !- Vertex 3 X-coordinate {m}
>     0,                       !- Vertex 3 Y-coordinate {m}
>     2.850000000000,          !- Vertex 3 Z-coordinate {m}
>     10,                      !- Vertex 4 X-coordinate {m}
>     10,                      !- Vertex 4 Y-coordinate {m}
>     2.85;                    !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     69B6ED,                  !- Name
>     Wall,                    !- Surface Type
>     Exterior Wall,           !- Construction Name
>     Zone One,                !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     ,                        !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     10.000000000000,         !- Vertex 1 Y-coordinate {m}
>     2.850000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     10.000000000000,         !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     2.850000000000;          !- Vertex 4 Z-coordinate {m}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: FENESTRATIONSURFACE:DETAILED ===========
> 
> FenestrationSurface:Detailed,
>     31916B,                  !- Name
>     Window,                  !- Surface Type
>     Exterior Window,         !- Construction Name
>     3C881D,                  !- Building Surface Name
>     ,                        !- Outside Boundary Condition Object
>     ,                        !- View Factor to Ground
>     ,                        !- Shading Control Name
>     ,                        !- Frame and Divider Name
>     ,                        !- Multiplier
>     4,                       !- Number of Vertices
>     0.753403144491,          !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     2.165875131543,          !- Vertex 1 Z-coordinate {m}
>     0.753403144491,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.565875131543,          !- Vertex 2 Z-coordinate {m}
>     9.353403144491,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.565875131543,          !- Vertex 3 Z-coordinate {m}
>     9.353403144491,          !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     2.165875131543;          !- Vertex 4 Z-coordinate {m}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SIZING:ZONE ===========
> 
> Sizing:Zone,
>     Zone One,                !- Zone Name
>     14.,                     !- Zone Cooling Design Supply Air Temperature {C}
>     50.,                     !- Zone Heating Design Supply Air Temperature {C}
>     0.009,                   !- Zone Cooling Design Supply Air Humidity Ratio 
> {kg-H2O/kg-air}
>     0.004,                   !- Zone Heating Design Supply Air Humidity Ratio 
> {kg-H2O/kg-air}
>     flow/person,             !- Outdoor Air Method
>     0.00944,                 !- Outdoor Air Flow per Person {m3/s}
>     0.0,                     !- Outdoor Air Flow per Zone Floor Area {m3/s-m2}
>     0.0,                     !- Outdoor Air Flow per Zone {m3/s}
>     0.0,                     !- Zone Heating Sizing Factor
>     0.0,                     !- Zone Cooling Sizing Factor
>     DesignDay,               !- Cooling Design Air Flow Method
>     0,                       !- Cooling Design Air Flow Rate {m3/s}
>     ,                        !- Cooling Minimum Air Flow per Zone Floor Area 
> {m3/s-m2}
>     ,                        !- Cooling Minimum Air Flow {m3/s}
>     ,                        !- Cooling Minimum Air Flow Fraction
>     DesignDay,               !- Heating Design Air Flow Method
>     0,                       !- Heating Design Air Flow Rate {m3/s}
>     ,                        !- Heating Maximum Air Flow per Zone Floor Area 
> {m3/s-m2}
>     ;                        !- Heating Maximum Air Flow {m3/s}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SIZING:PLANT ===========
> 
> Sizing:Plant,
>     Hot Water Loop,          !- Plant or Condenser Loop Name
>     Heating,                 !- Loop Type
>     90,                      !- Design Loop Exit Temperature {C}
>     20;                      !- Loop Design Temperature Difference {deltaC}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: ZONECONTROL:THERMOSTAT ===========
> 
> ZoneControl:Thermostat,
>     Zone One Control,        !- Name
>     Zone One,                !- Zone or ZoneList Name
>     Zone One Control Type Schedule,  !- Control Type Schedule Name
>     ThermostatSetpoint:SingleHeating,  !- Control 1 Object Type
>     Single Heating;          !- Control 1 Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: THERMOSTATSETPOINT:SINGLEHEATING 
> ===========
> 
> ThermostatSetpoint:SingleHeating,
>     Single Heating,          !- Name
>     Heating Setpoint Schedule;  !- Setpoint Temperature Schedule Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: ZONEHVAC:BASEBOARD:CONVECTIVE:WATER 
> ===========
> 
> ZoneHVAC:Baseboard:Convective:Water,
>     Zone One Baseboard Heating,  !- Name
>     Baseboard Operation Schedule,  !- Availability Schedule Name
>     N9,                      !- Inlet Node Name
>     N10,                     !- Outlet Node Name
>     autosize,                !- U-Factor Times Area Value {W/K}
>     autosize;                !- Maximum Water Flow Rate {m3/s}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: ZONEHVAC:EQUIPMENTLIST ===========
> 
> ZoneHVAC:EquipmentList,
>     Zone One Equipment,      !- Name
>     ZoneHVAC:Baseboard:Convective:Water,  !- Zone Equipment 1 Object Type
>     Zone One Baseboard Heating,  !- Zone Equipment 1 Name
>     1,                       !- Zone Equipment 1 Cooling Sequence
>     1;                       !- Zone Equipment 1 Heating or No-Load Sequence
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: ZONEHVAC:EQUIPMENTCONNECTIONS 
> ===========
> 
> ZoneHVAC:EquipmentConnections,
>     Zone One,                !- Zone Name
>     Zone One Equipment,      !- Zone Conditioning Equipment List Name
>     ,                        !- Zone Air Inlet Node or NodeList Name
>     ,                        !- Zone Air Exhaust Node or NodeList Name
>     Zone One Node,           !- Zone Air Node Name
>     Zone One Out Node;       !- Zone Return Air Node Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: BRANCH ===========
> 
> Branch,
>     HS Inlet Branch,         !- Name
>     0,                       !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Pump:VariableSpeed,      !- Component 1 Object Type
>     Hot Water Circ Pump,     !- Component 1 Name
>     N1,                      !- Component 1 Inlet Node Name
>     N2,                      !- Component 1 Outlet Node Name
>     Active;                  !- Component 1 Branch Control Type
> 
> Branch,
>     Central Boiler Branch,   !- Name
>     0,                       !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Boiler:HotWater,         !- Component 1 Object Type
>     Central Boiler,          !- Component 1 Name
>     N3,                      !- Component 1 Inlet Node Name
>     N4,                      !- Component 1 Outlet Node Name
>     Active;                  !- Component 1 Branch Control Type
> 
> Branch,
>     HS Bypass Branch,        !- Name
>     0,                       !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Pipe:Adiabatic,          !- Component 1 Object Type
>     Heating Supply Side Bypass,  !- Component 1 Name
>     N5,                      !- Component 1 Inlet Node Name
>     N6,                      !- Component 1 Outlet Node Name
>     Passive;                 !- Component 1 Branch Control Type
> 
> Branch,
>     HS Outlet Branch,        !- Name
>     0,                       !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Pipe:Adiabatic,          !- Component 1 Object Type
>     Heating Supply Outlet,   !- Component 1 Name
>     N7,                      !- Component 1 Inlet Node Name
>     N8,                      !- Component 1 Outlet Node Name
>     Passive;                 !- Component 1 Branch Control Type
> 
> Branch,
>     Baseboard Branch,        !- Name
>     0,                       !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     ZoneHVAC:Baseboard:Convective:Water,  !- Component 1 Object Type
>     Zone One Baseboard Heating,  !- Component 1 Name
>     N9,                      !- Component 1 Inlet Node Name
>     N10,                     !- Component 1 Outlet Node Name
>     Active;                  !- Component 1 Branch Control Type
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: BRANCHLIST ===========
> 
> BranchList,
>     Supply Side Branches,    !- Name
>     HS Inlet Branch,         !- Branch 1 Name
>     Central Boiler Branch,   !- Branch 2 Name
>     HS Bypass Branch,        !- Branch 3 Name
>     HS Outlet Branch;        !- Branch 4 Name
> 
> BranchList,
>     Demand Side Branches,    !- Name
>     Baseboard Branch;        !- Branch 1 Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: CONNECTOR:SPLITTER ===========
> 
> Connector:Splitter,
>     Heating Supply Splitter, !- Name
>     HS Inlet Branch,         !- Inlet Branch Name
>     Central Boiler Branch,   !- Outlet Branch 1 Name
>     HS Bypass Branch;        !- Outlet Branch 2 Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: CONNECTOR:MIXER ===========
> 
> Connector:Mixer,
>     Heating Supply Mixer,    !- Name
>     HS Outlet Branch,        !- Outlet Branch Name
>     Central Boiler Branch,   !- Inlet Branch 1 Name
>     HS Bypass Branch;        !- Inlet Branch 2 Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: CONNECTORLIST ===========
> 
> ConnectorList,
>     Heating Supply Side Connectors,  !- Name
>     Connector:Splitter,      !- Connector 1 Object Type
>     Heating Supply Splitter, !- Connector 1 Name
>     Connector:Mixer,         !- Connector 2 Object Type
>     Heating Supply Mixer;    !- Connector 2 Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: NODELIST ===========
> 
> NodeList,
>     Zone One In Nodes,       !- Name
>     Zone One In Node;        !- Node 1 Name
> 
> NodeList,
>     Hot Water Loop Setpoint Node List,  !- Name
>     HW Supply Outlet Node;   !- Node 1 Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: PIPE:ADIABATIC ===========
> 
> Pipe:Adiabatic,
>     Heating Supply Side Bypass,  !- Name
>     N5,                      !- Inlet Node Name
>     N6;                      !- Outlet Node Name
> 
> Pipe:Adiabatic,
>     Heating Supply Outlet,   !- Name
>     N7,                      !- Inlet Node Name
>     N8;                      !- Outlet Node Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: PUMP:VARIABLESPEED ===========
> 
> Pump:VariableSpeed,
>     Hot Water Circ Pump,     !- Name
>     N1,                      !- Inlet Node Name
>     N2,                      !- Outlet Node Name
>     autosize,                !- Rated Flow Rate {m3/s}
>     179352,                  !- Rated Pump Head {Pa}
>     autosize,                !- Rated Power Consumption {W}
>     0.9,                     !- Motor Efficiency
>     0,                       !- Fraction of Motor Inefficiencies to Fluid Stream
>     0,                       !- Coefficient 1 of the Part Load Performance Curve
>     0,                       !- Coefficient 2 of the Part Load Performance Curve
>     0,                       !- Coefficient 3 of the Part Load Performance Curve
>     0,                       !- Coefficient 4 of the Part Load Performance Curve
>     0,                       !- Minimum Flow Rate {m3/s}
>     Intermittent;            !- Pump Control Type
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: BOILER:HOTWATER ===========
> 
> Boiler:HotWater,
>     Central Boiler,          !- Name
>     Diesel,                  !- Fuel Type
>     autosize,                !- Nominal Capacity {W}
>     0.8,                     !- Nominal Thermal Efficiency
>     ,                        !- Normalized Boiler Efficiency Curve Name
>     90,                      !- Design Water Outlet Temperature {C}
>     autosize,                !- Design Water Flow Rate {m3/s}
>     0,                       !- Minimum Part Load Ratio
>     1.2,                     !- Maximum Part Load Ratio
>     1,                       !- Optimum Part Load Ratio
>     N3,                      !- Boiler Water Inlet Node Name
>     N4,                      !- Boiler Water Outlet Node Name
>     100,                     !- Water Outlet Upper Temperature Limit {C}
>     VariableFlow;            !- Boiler Flow Mode
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: PLANTLOOP ===========
> 
> PlantLoop,
>     Hot Water Loop,          !- Name
>     Water,                   !- Fluid Type
>     Hot Loop Operation,      !- Plant Equipment Operation Scheme Name
>     N8,                      !- Loop Temperature Setpoint Node Name
>     100,                     !- Maximum Loop Temperature {C}
>     10,                      !- Minimum Loop Temperature {C}
>     autosize,                !- Maximum Loop Flow Rate {m3/s}
>     0.0,                     !- Minimum Loop Flow Rate {m3/s}
>     autocalculate,           !- Plant Loop Volume {m3}
>     N1,                      !- Plant Side Inlet Node Name
>     N8,                      !- Plant Side Outlet Node Name
>     Supply Side Branches,    !- Plant Side Branch List Name
>     Heating Supply Side Connectors,  !- Plant Side Connector List Name
>     N9,                      !- Demand Side Inlet Node Name
>     N10,                     !- Demand Side Outlet Node Name
>     Demand Side Branches,    !- Demand Side Branch List Name
>     ,                        !- Demand Side Connector List Name
>     Sequential;              !- Load Distribution Scheme
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: PLANTEQUIPMENTLIST ===========
> 
> PlantEquipmentList,
>     Heating Plant,           !- Name
>     Boiler:HotWater,         !- Equipment 1 Object Type
>     Central Boiler;          !- Equipment 1 Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: PLANTEQUIPMENTOPERATION:HEATINGLOAD 
> ===========
> 
> PlantEquipmentOperation:HeatingLoad,
>     Central Boiler Only,     !- Name
>     0,                       !- Load Range 1 Lower Limit {W}
>     1000000,                 !- Load Range 1 Upper Limit {W}
>     Heating Plant;           !- Range 1 Equipment List Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: PLANTEQUIPMENTOPERATIONSCHEMES 
> ===========
> 
> PlantEquipmentOperationSchemes,
>     Hot Loop Operation,      !- Name
>     PlantEquipmentOperation:HeatingLoad,  !- Control Scheme 1 Object Type
>     Central Boiler Only,     !- Control Scheme 1 Name
>     Baseboard Operation Schedule;  !- Control Scheme 1 Schedule Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SETPOINTMANAGER:SCHEDULED ===========
> 
> SetpointManager:Scheduled,
>     Plant Manager,           !- Name
>     Temperature,             !- Control Variable
>     Baseboard Operation Schedule,  !- Schedule Name
>     N8;                      !- Setpoint Node or NodeList Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: OUTPUT:VARIABLEDICTIONARY ===========
> 
> Output:VariableDictionary,
>     IDF;                     !- Key Field
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: OUTPUT:SURFACES:DRAWING ===========
> 
> Output:Surfaces:Drawing,
>     DXF,                     !- Report Type
>     RegularPolyline;         !- Report Specifications 1
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: OUTPUT:TABLE:SUMMARYREPORTS ===========
> 
> Output:Table:SummaryReports,
>     AllSummaryAndMonthly;    !- Report 1 Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: OUTPUTCONTROL:TABLE:STYLE ===========
> 
> OutputControl:Table:Style,
>     HTML,                    !- Column Separator
>     JtoKWH;                  !- Unit Conversion
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: OUTPUT:VARIABLE ===========
> 
> Output:Variable,
>     *,                       !- Key Value
>     Zone Mean Air Temperature,  !- Variable Name
>     Hourly;                  !- Reporting Frequency
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/