[EnergyPlus_Support] Re: availabilityManager:High temperaturTurnoff



this is my input :
!-Generator IDFEditor 1.41
!-Option OriginalOrderTop UseSpecialFormat

!-NOTE: All comments with '!-' are ignored by the IDFEditor and are generated automatically.
!-      Use '!' comments if they need to be retained when using the IDFEditor.

AvailabilityManager:HighTemperatureTurnOff,
    schedual boiler,         !- Name
    Central Boiler Outlet Node,  !- Sensor Node Name
    82;                      !- Temperature {C}

AvailabilityManager:LowTemperatureTurnOn,
    schedule boiler 2,       !- Name
    Central Boiler Outlet Node,  !- Sensor Node Name
    80;                      !- Temperature {C}

Sizing:Plant,
    Hot Water Loop,          !- Plant or Condenser Loop Name
    Heating,                 !- Loop Type
    82,                      !- Design Loop Exit Temperature {C}
    10;                      !- Loop Design Temperature Difference {deltaC}

ZoneControl:Thermostat,
    thermostat,              !- Name
    Block1:Zone1,            !- Zone or ZoneList Name
    Zone Control Type Sched, !- Control Type Schedule Name
    ThermostatSetpoint:SingleHeating,  !- Control 1 Object Type
    thermostat heating;      !- Control 1 Name

Schedule:Compact,
    Zone Control Type Sched, !- Name
    Control Type,            !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00, 1;         !- Field 4

ZoneHVAC:Baseboard:Convective:Water,
    radiator,                !- Name
    On,                      !- Availability Schedule Name
    inlet radiator,          !- Inlet Node Name
    outletradiator,          !- Outlet Node Name
    autosize,                !- U-Factor Times Area Value {W/K}
    autosize,                !- Maximum Water Flow Rate {m3/s}
    0.001;                   !- Convergence Tolerance

ZoneHVAC:EquipmentList,
    radiator,                !- Name
    ZoneHVAC:Baseboard:Convective:Water,  !- Zone Equipment 1 Object Type
    radiator,                !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1;                       !- Zone Equipment 1 Heating or No-Load Sequence

ZoneHVAC:EquipmentConnections,
    Block1:Zone1,            !- Zone Name
    radiator,                !- Zone Conditioning Equipment List Name
    ,                        !- Zone Air Inlet Node or NodeList Name
    ,                        !- Zone Air Exhaust Node or NodeList Name
    inlet air node,          !- Zone Air Node Name
    return air node;         !- Zone Return Air Node Name

Branch,
    Heating Supply Inlet Branch,  !- Name
    0,                       !- Maximum Flow Rate {m3/s}
    ,                        !- Pressure Drop Curve Name
    Pump:constantSpeed,      !- Component 1 Object Type
    HW Circ Pump,            !- Component 1 Name
    HW Supply Inlet Node,    !- Component 1 Inlet Node Name
    HW Pump Outlet Node,     !- Component 1 Outlet Node Name
    ACTIVE;                  !- Component 1 Branch Control Type

Branch,
    Central Boiler Branch,   !- Name
    0,                       !- Maximum Flow Rate {m3/s}
    ,                        !- Pressure Drop Curve Name
    Boiler:HotWater,         !- Component 1 Object Type
    Central Boiler,          !- Component 1 Name
    Central Boiler inlet Node,  !- Component 1 Inlet Node Name
    Central Boiler Outlet Node,  !- Component 1 Outlet Node Name
    ACTIVE;                  !- Component 1 Branch Control Type

Branch,
    Heating Supply Outlet Branch,  !- Name
    0,                       !- Maximum Flow Rate {m3/s}
    ,                        !- Pressure Drop Curve Name
    Pipe:Adiabatic,          !- Component 1 Object Type
    Heating Supply Outlet,   !- Component 1 Name
    heating supply exit pipe inlet node,  !- Component 1 Inlet Node Name
    HW Supply Outlet Node,   !- Component 1 Outlet Node Name
    PASSIVE;                 !- Component 1 Branch Control Type

Branch,
    Heating Demand Inlet Branch,  !- Name
    0,                       !- Maximum Flow Rate {m3/s}
    ,                        !- Pressure Drop Curve Name
    Pipe:Adiabatic,          !- Component 1 Object Type
    Heating Demand Inlet Pipe,  !- Component 1 Name
    HW Demand Inlet Node,    !- Component 1 Inlet Node Name
    HW Demand Entrance Pipe Outlet Node,  !- Component 1 Outlet Node Name
    PASSIVE;                 !- Component 1 Branch Control Type

Branch,
    zone1 Baseboard Branch,  !- Name
    0,                       !- Maximum Flow Rate {m3/s}
    ,                        !- Pressure Drop Curve Name
    ZoneHVAC:Baseboard:Convective:Water,  !- Component 1 Object Type
    radiator,                !- Component 1 Name
    inlet radiator,          !- Component 1 Inlet Node Name
    outletradiator,          !- Component 1 Outlet Node Name
    ACTIVE;                  !- Component 1 Branch Control Type

Branch,
    Heating Demand Outlet Branch,  !- Name
    0,                       !- Maximum Flow Rate {m3/s}
    ,                        !- Pressure Drop Curve Name
    Pipe:Adiabatic,          !- Component 1 Object Type
    Heating Demand Outlet Pipe,  !- Component 1 Name
    HW Demand Exit Pipe Inlet Node,  !- Component 1 Inlet Node Name
    HW Demand Outlet Node,   !- Component 1 Outlet Node Name
    PASSIVE;                 !- Component 1 Branch Control Type

BranchList,
    Heating Supply Side Branches,  !- Name
    Heating Supply Inlet Branch,  !- Branch 1 Name
    Central Boiler Branch,   !- Branch 2 Name
    Heating Supply Outlet Branch;  !- Branch 3 Name

BranchList,
    Heating Demand Side Branches,  !- Name
    Heating Demand Inlet Branch,  !- Branch 1 Name
    zone1 Baseboard Branch,  !- Branch 2 Name
    Heating Demand Outlet Branch;  !- Branch 3 Name

Pipe:Adiabatic,
    Heating Supply Outlet,   !- Name
    Heating Supply Exit Pipe Inlet Node,  !- Inlet Node Name
    HW Supply Outlet Node;   !- Outlet Node Name

Pipe:Adiabatic,
    Heating Demand Inlet Pipe,  !- Name
    HW Demand Inlet Node,    !- Inlet Node Name
    HW Demand Entrance Pipe Outlet Node;  !- Outlet Node Name

Pipe:Adiabatic,
    Heating Demand Outlet Pipe,  !- Name
    HW Demand Exit Pipe Inlet Node,  !- Inlet Node Name
    HW Demand Outlet Node;   !- Outlet Node Name

Pump:ConstantSpeed,
    HW Circ Pump,            !- Name
    HW Supply Inlet Node,    !- Inlet Node Name
    HW Pump Outlet Node,     !- Outlet Node Name
    ,                        !- Rated Flow Rate {m3/s}
    179352,                  !- Rated Pump Head {Pa}
    ,                        !- Rated Power Consumption {W}
    0.9,                     !- Motor Efficiency
    ,                        !- Fraction of Motor Inefficiencies to Fluid Stream
    Continuous;              !- Pump Control Type

Boiler:HotWater,
    Central Boiler,          !- Name
    NaturalGas,              !- Fuel Type
    autosize,                !- Nominal Capacity {W}
    0.8,                     !- Nominal Thermal Efficiency
    LeavingBoiler,           !- Efficiency Curve Temperature Evaluation Variable
    ,                        !- Normalized Boiler Efficiency Curve Name
    81.,                     !- Design Water Outlet Temperature {C}
    autosize,                !- Design Water Flow Rate {m3/s}
    0.0,                     !- Minimum Part Load Ratio
    1.2,                     !- Maximum Part Load Ratio
    1.0,                     !- Optimum Part Load Ratio
    Central Boiler inlet Node,  !- Boiler Water Inlet Node Name
    Central Boiler Outlet Node,  !- Boiler Water Outlet Node Name
    100.,                    !- Water Outlet Upper Temperature Limit {C}
    ConstantFlow;            !- Boiler Flow Mode

PlantEquipmentList,
    heating plant,           !- Name
    Boiler:HotWater,         !- Equipment 1 Object Type
    Central Boiler;          !- Equipment 1 Name

PlantEquipmentOperation:HeatingLoad,
    Central Boiler Only,     !- Name
    0,                       !- Load Range 1 Lower Limit {W}
    1000000,                 !- Load Range 1 Upper Limit {W}
    heating plant;           !- Range 1 Equipment List Name

PlantEquipmentOperationSchemes,
    Hot Loop Operation,      !- Name
    PlantEquipmentOperation:HeatingLoad,  !- Control Scheme 1 Object Type
    Central Boiler Only,     !- Control Scheme 1 Name
    PlantOnSched;            !- Control Scheme 1 Schedule Name

Schedule:Compact,
    plantonsched,            !- Name
    Fraction,                !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For : allDays,           !- Field 2
    Until: 24:00, 1;         !- Field 4

SetpointManager:Scheduled,
    Hot Water Loop Setpoint Manager,  !- Name
    Temperature,             !- Control Variable
    HW Loop Temp Schedule,   !- Schedule Name
    HW Supply Outlet Node;   !- Setpoint Node or NodeList Name

Schedule:Compact,
    HW Loop Temp Schedule,   !- Name
    Temperature,             !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: Alldays,            !- Field 2
    Until: 24:00, 60.0;      !- Field 4

Curve:Quadratic,
    BoilerEfficiency,        !- Name
    1.0,                     !- Coefficient1 Constant
    0.0,                     !- Coefficient2 x
    0.0,                     !- Coefficient3 x**2
    0,                       !- Minimum Value of x
    1;                       !- Maximum Value of x

ThermostatSetpoint:SingleHeating,
    thermostat heating,      !- Name
    schedula thermostat;     !- Setpoint Temperature Schedule Name

Schedule:Compact,
    schedula thermostat,     !- Name
    Temperature,             !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: Alldays,            !- Field 2
    Until: 24:00, 20;        !- Field 4

Sizing:Zone,
    Block1:Zone1,            !- Zone or ZoneList Name
    15,                      !- Zone Cooling Design Supply Air Temperature {C}
    50,                      !- Zone Heating Design Supply Air Temperature {C}
    0.009,                   !- Zone Cooling Design Supply Air Humidity Ratio {kg-H2O/kg-air}
    0.009,                   !- Zone Heating Design Supply Air Humidity Ratio {kg-H2O/kg-air}
    ,                        !- Design Specification Outdoor Air Object Name
    ,                        !- Zone Heating Sizing Factor
    ,                        !- Zone Cooling Sizing Factor
    DesignDay,               !- Cooling Design Air Flow Method
    ,                        !- Cooling Design Air Flow Rate {m3/s}
    0.000762,                !- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2}
    ,                        !- Cooling Minimum Air Flow {m3/s}
    ,                        !- Cooling Minimum Air Flow Fraction
    DesignDay,               !- Heating Design Air Flow Method
    ,                        !- Heating Design Air Flow Rate {m3/s}
    0.002032,                !- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2}
    0.1415762,               !- Heating Maximum Air Flow {m3/s}
    0.3,                     !- Heating Maximum Air Flow Fraction
    1,                       !- Design Zone Air Distribution Effectiveness in Cooling Mode
    1;                       !- Design Zone Air Distribution Effectiveness in Heating Mode

Connector:Splitter,
    Heating Demand Splitter, !- Name
    Heating Demand Inlet Branch,  !- Inlet Branch Name
    zone1 Baseboard Branch;  !- Outlet Branch 1 Name

Connector:Splitter,
    Heating Supply Splitter, !- Name
    Heating Supply Inlet Branch,  !- Inlet Branch Name
    Central Boiler Branch;   !- Outlet Branch 1 Name

Connector:Mixer,
    Heating Demand Mixer,    !- Name
    Heating Demand Outlet Branch,  !- Outlet Branch Name
    zone1 Baseboard Branch;  !- Inlet Branch 1 Name

Connector:Mixer,
    Heating Supply Mixer,    !- Name
    Heating Supply Outlet Branch,  !- Outlet Branch Name
    Central Boiler Branch;   !- Inlet Branch 1 Name

ConnectorList,
    Heating Supply Side Connectors,  !- Name
    Connector:Splitter,      !- Connector 1 Object Type
    Heating Supply Splitter, !- Connector 1 Name
    Connector:Mixer,         !- Connector 2 Object Type
    Heating Supply Mixer;    !- Connector 2 Name

ConnectorList,
    Heating Demand Side Connectors,  !- Name
    Connector:Splitter,      !- Connector 1 Object Type
    Heating Demand Splitter, !- Connector 1 Name
    Connector:Mixer,         !- Connector 2 Object Type
    Heating Demand Mixer;    !- Connector 2 Name

PlantLoop,
    Hot Water Loop,          !- Name
    Water,                   !- Fluid Type
    ,                        !- User Defined Fluid Type
    Hot Loop Operation,      !- Plant Equipment Operation Scheme Name
    HW Supply Outlet Node,   !- Loop Temperature Setpoint Node Name
    100,                     !- Maximum Loop Temperature {C}
    10,                      !- Minimum Loop Temperature {C}
    autosize,                !- Maximum Loop Flow Rate {m3/s}
    0.0,                     !- Minimum Loop Flow Rate {m3/s}
    autocalculate,           !- Plant Loop Volume {m3}
    HW Supply Inlet Node,    !- Plant Side Inlet Node Name
    HW Supply Outlet Node,   !- Plant Side Outlet Node Name
    Heating Supply Side Branches,  !- Plant Side Branch List Name
    Heating Supply Side Connectors,  !- Plant Side Connector List Name
    HW Demand Inlet Node,    !- Demand Side Inlet Node Name
    HW Demand Outlet Node,   !- Demand Side Outlet Node Name
    Heating Demand Side Branches,  !- Demand Side Branch List Name
    Heating Demand Side Connectors,  !- Demand Side Connector List Name
    Sequential;              !- Load Distribution Scheme

! File generated by DesignBuilder - 3.0.0.092 1/18/2012 - 8:33:36 PM
! Source file: C:\Users\Tooran\Desktop\boiler.dsb
Version,7.0.0.036;

RunPeriod,
    Untitled,                !- Name
    1,                       !- Begin Month
    1,                       !- Begin Day of Month
    1,                       !- End Month
    31,                      !- End Day of Month
    UseWeatherFile,          !- Day of Week for Start Day
    No,                      !- Use Weather File Holidays and Special Days
    No,                      !- Use Weather File Daylight Saving Period
    Yes,                     !- Apply Weekend Holiday Rule
    Yes,                     !- Use Weather File Rain Indicators
    Yes,                     !- Use Weather File Snow Indicators
    1;                       !- Number of Times Runperiod to be Repeated

RunPeriodControl:DaylightSavingTime,
    Last Sunday in March,    !- Start Date
    Last Sunday in October;  !- End Date

! Hourly weather file: C:\ProgramData\DesignBuilder\Weather Data\GBR_LONDON_GATWICK_IWEC.epw
Site:Location,
    Untitled,                !- Name
    51.15,                   !- Latitude {deg}
    -0.18,                   !- Longitude {deg}
    0,                       !- Time Zone {hr}
    62;                      !- Elevation {m}

Site:GroundTemperature:BuildingSurface,14,14,14,14,14,14,14,14,14,14,14,14;
Site:GroundReflectance,0.2,0.2,0.2,0.2,0.2,0.2,0.2,0.2,0.2,0.2,0.2,0.2;

Site:GroundReflectance:SnowModifier,
    1.0,                     !- Ground Reflected Solar Modifier
    1.0;                     !- Daylighting Ground Reflected Solar Modifier

SimulationControl,
    Yes,                     !- Do Zone Sizing Calculation
    Yes,                     !- Do System Sizing Calculation
    Yes,                     !- Do Plant Sizing Calculation
    No,                      !- Run Simulation for Sizing Periods
    Yes;                     !- Run Simulation for Weather File Run Periods

SizingPeriod:DesignDay,
    Summer Design Day in Untitled,  !- Name
    27,                      !- Maximum Dry-Bulb Temperature {C}
    9.7,                     !- Daily Dry-Bulb Temperature Range {deltaC}
    18.6,                    !- Humidity Indicating Conditions at Maximum Dry-Bulb
    100582.4,                !- Barometric Pressure {Pa}
    0,                       !- Wind Speed {m/s}
    0,                       !- Wind Direction {deg}
    0.98,                    !- Sky Clearness
    0,                       !- Rain Indicator
    0,                       !- Snow Indicator
    15,                      !- Day of Month
    7,                       !- Month
    SummerDesignDay,         !- Day Type
    1,                       !- Daylight Saving Time Indicator
    WetBulb;                 !- Humidity Indicating Type

SizingPeriod:DesignDay,
    Winter Design Day in Untitled,  !- Name
    -4.8,                    !- Maximum Dry-Bulb Temperature {C}
    0,                       !- Daily Dry-Bulb Temperature Range {deltaC}
    -4.8,                    !- Humidity Indicating Conditions at Maximum Dry-Bulb
    100582.4,                !- Barometric Pressure {Pa}
    12.7,                    !- Wind Speed {m/s}
    0,                       !- Wind Direction {deg}
    0,                       !- Sky Clearness
    0,                       !- Rain Indicator
    0,                       !- Snow Indicator
    15,                      !- Day of Month
    1,                       !- Month
    WinterDesignDay,         !- Day Type
    0,                       !- Daylight Saving Time Indicator
    WetBulb;                 !- Humidity Indicating Type

Timestep,12;

ConvergenceLimits,
    1,                       !- Minimum System Timestep {minutes}
    20;                      !- Maximum HVAC Iterations

! Not limited
ScheduleTypeLimits,
    Any Number;              !- Name

ScheduleTypeLimits,
    Fraction,                !- Name
    0.0,                     !- Lower Limit Value
    1.0,                     !- Upper Limit Value
    CONTINUOUS;              !- Numeric Type

ScheduleTypeLimits,
    Temperature,             !- Name
    -60,                     !- Lower Limit Value
    200,                     !- Upper Limit Value
    CONTINUOUS;              !- Numeric Type

ScheduleTypeLimits,
    Control Type,            !- Name
    0,                       !- Lower Limit Value
    4,                       !- Upper Limit Value
    DISCRETE;                !- Numeric Type

ScheduleTypeLimits,
    On/Off,                  !- Name
    0,                       !- Lower Limit Value
    1,                       !- Upper Limit Value
    DISCRETE;                !- Numeric Type

! Type
! Type
! All days in year
! All hours in day
Schedule:Compact,
    On,                      !- Name
    Any Number,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00, 1;         !- Field 4

! Type
! Type
! All days in year
! All hours in day
Schedule:Compact,
    Off,                     !- Name
    Any Number,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00, 0;         !- Field 4

! Type
! Type
! All days in year
! All hours in day
Schedule:Compact,
    Work efficiency,         !- Name
    Any Number,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00, 0;         !- Field 4

! Type
! Type
! All days in year
! All hours in day
Schedule:Compact,
    OpaqueShade,             !- Name
    Any Number,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00, 0;         !- Field 4

!Schedule:Compact, AirVelocitySchedule,
!      Any Number,                                 ! Type
!      Through: 12/31,                             ! Type
!      For: AllDays,                               ! All days in year
!      Until: 24:00,                               ! All hours in day
!       0.137;
! off heating day
Schedule:Day:Hourly,
    0,                       !- Name
    Any Number,              !- Schedule Type Limits Name
    0,                       !- Hour 1
    0,                       !- Hour 2
    0,                       !- Hour 3
    0,                       !- Hour 4
    0,                       !- Hour 5
    0,                       !- Hour 6
    0,                       !- Hour 7
    0,                       !- Hour 8
    0,                       !- Hour 9
    0,                       !- Hour 10
    0,                       !- Hour 11
    0,                       !- Hour 12
    0,                       !- Hour 13
    0,                       !- Hour 14
    0,                       !- Hour 15
    0,                       !- Hour 16
    0,                       !- Hour 17
    0,                       !- Hour 18
    0,                       !- Hour 19
    0,                       !- Hour 20
    0,                       !- Hour 21
    0,                       !- Hour 22
    0,                       !- Hour 23
    0;                       !- Hour 24

! off cooling day
Schedule:Day:Hourly,
    50,                      !- Name
    Any Number,              !- Schedule Type Limits Name
    50,                      !- Hour 1
    50,                      !- Hour 2
    50,                      !- Hour 3
    50,                      !- Hour 4
    50,                      !- Hour 5
    50,                      !- Hour 6
    50,                      !- Hour 7
    50,                      !- Hour 8
    50,                      !- Hour 9
    50,                      !- Hour 10
    50,                      !- Hour 11
    50,                      !- Hour 12
    50,                      !- Hour 13
    50,                      !- Hour 14
    50,                      !- Hour 15
    50,                      !- Hour 16
    50,                      !- Hour 17
    50,                      !- Hour 18
    50,                      !- Hour 19
    50,                      !- Hour 20
    50,                      !- Hour 21
    50,                      !- Hour 22
    50,                      !- Hour 23
    50;                      !- Hour 24

! used in seasonal schedules
Schedule:Day:Hourly,
    Off,                     !- Name
    Fraction,                !- Schedule Type Limits Name
    0,                       !- Hour 1
    0,                       !- Hour 2
    0,                       !- Hour 3
    0,                       !- Hour 4
    0,                       !- Hour 5
    0,                       !- Hour 6
    0,                       !- Hour 7
    0,                       !- Hour 8
    0,                       !- Hour 9
    0,                       !- Hour 10
    0,                       !- Hour 11
    0,                       !- Hour 12
    0,                       !- Hour 13
    0,                       !- Hour 14
    0,                       !- Hour 15
    0,                       !- Hour 16
    0,                       !- Hour 17
    0,                       !- Hour 18
    0,                       !- Hour 19
    0,                       !- Hour 20
    0,                       !- Hour 21
    0,                       !- Hour 22
    0,                       !- Hour 23
    0;                       !- Hour 24

Schedule:Week:Daily,
    Off,                     !- Name
    Off,                     !- Sunday Schedule:Day Name
    Off,                     !- Monday Schedule:Day Name
    Off,                     !- Tuesday Schedule:Day Name
    Off,                     !- Wednesday Schedule:Day Name
    Off,                     !- Thursday Schedule:Day Name
    Off,                     !- Friday Schedule:Day Name
    Off,                     !- Saturday Schedule:Day Name
    Off,                     !- Holiday Schedule:Day Name
    Off,                     !- SummerDesignDay Schedule:Day Name
    Off,                     !- WinterDesignDay Schedule:Day Name
    Off,                     !- CustomDay1 Schedule:Day Name
    Off;                     !- CustomDay2 Schedule:Day Name

! -------------------- Control type schedules (for heating & cooling) ----------------------
Schedule:Day:Hourly,
    Summer Control Type Day Sch,  !- Name
    Control Type,            !- Schedule Type Limits Name
    4,                       !- Hour 1
    4,                       !- Hour 2
    4,                       !- Hour 3
    4,                       !- Hour 4
    4,                       !- Hour 5
    4,                       !- Hour 6
    4,                       !- Hour 7
    4,                       !- Hour 8
    4,                       !- Hour 9
    4,                       !- Hour 10
    4,                       !- Hour 11
    4,                       !- Hour 12
    4,                       !- Hour 13
    4,                       !- Hour 14
    4,                       !- Hour 15
    4,                       !- Hour 16
    4,                       !- Hour 17
    4,                       !- Hour 18
    4,                       !- Hour 19
    4,                       !- Hour 20
    4,                       !- Hour 21
    4,                       !- Hour 22
    4,                       !- Hour 23
    4;                       !- Hour 24

Schedule:Day:Hourly,
    Winter Control Type Day Sch,  !- Name
    Control Type,            !- Schedule Type Limits Name
    4,                       !- Hour 1
    4,                       !- Hour 2
    4,                       !- Hour 3
    4,                       !- Hour 4
    4,                       !- Hour 5
    4,                       !- Hour 6
    4,                       !- Hour 7
    4,                       !- Hour 8
    4,                       !- Hour 9
    4,                       !- Hour 10
    4,                       !- Hour 11
    4,                       !- Hour 12
    4,                       !- Hour 13
    4,                       !- Hour 14
    4,                       !- Hour 15
    4,                       !- Hour 16
    4,                       !- Hour 17
    4,                       !- Hour 18
    4,                       !- Hour 19
    4,                       !- Hour 20
    4,                       !- Hour 21
    4,                       !- Hour 22
    4,                       !- Hour 23
    4;                       !- Hour 24

Schedule:Day:Hourly,
    Summer Control Type Day Sch - cool,  !- Name
    Control Type,            !- Schedule Type Limits Name
    2,                       !- Hour 1
    2,                       !- Hour 2
    2,                       !- Hour 3
    2,                       !- Hour 4
    2,                       !- Hour 5
    2,                       !- Hour 6
    2,                       !- Hour 7
    2,                       !- Hour 8
    2,                       !- Hour 9
    2,                       !- Hour 10
    2,                       !- Hour 11
    2,                       !- Hour 12
    2,                       !- Hour 13
    2,                       !- Hour 14
    2,                       !- Hour 15
    2,                       !- Hour 16
    2,                       !- Hour 17
    2,                       !- Hour 18
    2,                       !- Hour 19
    2,                       !- Hour 20
    2,                       !- Hour 21
    2,                       !- Hour 22
    2,                       !- Hour 23
    2;                       !- Hour 24

Schedule:Day:Hourly,
    Winter Control Type Day Sch - heat,  !- Name
    Control Type,            !- Schedule Type Limits Name
    1,                       !- Hour 1
    1,                       !- Hour 2
    1,                       !- Hour 3
    1,                       !- Hour 4
    1,                       !- Hour 5
    1,                       !- Hour 6
    1,                       !- Hour 7
    1,                       !- Hour 8
    1,                       !- Hour 9
    1,                       !- Hour 10
    1,                       !- Hour 11
    1,                       !- Hour 12
    1,                       !- Hour 13
    1,                       !- Hour 14
    1,                       !- Hour 15
    1,                       !- Hour 16
    1,                       !- Hour 17
    1,                       !- Hour 18
    1,                       !- Hour 19
    1,                       !- Hour 20
    1,                       !- Hour 21
    1,                       !- Hour 22
    1,                       !- Hour 23
    1;                       !- Hour 24

Schedule:Week:Daily,
    Summer Control Type Week Sch,  !- Name
    Summer Control Type Day Sch,  !- Sunday Schedule:Day Name
    Summer Control Type Day Sch,  !- Monday Schedule:Day Name
    Summer Control Type Day Sch,  !- Tuesday Schedule:Day Name
    Summer Control Type Day Sch,  !- Wednesday Schedule:Day Name
    Summer Control Type Day Sch,  !- Thursday Schedule:Day Name
    Summer Control Type Day Sch,  !- Friday Schedule:Day Name
    Summer Control Type Day Sch,  !- Saturday Schedule:Day Name
    Summer Control Type Day Sch,  !- Holiday Schedule:Day Name
    Summer Control Type Day Sch,  !- SummerDesignDay Schedule:Day Name
    Summer Control Type Day Sch,  !- WinterDesignDay Schedule:Day Name
    Summer Control Type Day Sch,  !- CustomDay1 Schedule:Day Name
    Summer Control Type Day Sch;  !- CustomDay2 Schedule:Day Name

Schedule:Week:Daily,
    Winter Control Type Week Sch,  !- Name
    Winter Control Type Day Sch,  !- Sunday Schedule:Day Name
    Winter Control Type Day Sch,  !- Monday Schedule:Day Name
    Winter Control Type Day Sch,  !- Tuesday Schedule:Day Name
    Winter Control Type Day Sch,  !- Wednesday Schedule:Day Name
    Winter Control Type Day Sch,  !- Thursday Schedule:Day Name
    Winter Control Type Day Sch,  !- Friday Schedule:Day Name
    Winter Control Type Day Sch,  !- Saturday Schedule:Day Name
    Winter Control Type Day Sch,  !- Holiday Schedule:Day Name
    Winter Control Type Day Sch,  !- SummerDesignDay Schedule:Day Name
    Winter Control Type Day Sch,  !- WinterDesignDay Schedule:Day Name
    Winter Control Type Day Sch,  !- CustomDay1 Schedule:Day Name
    Winter Control Type Day Sch;  !- CustomDay2 Schedule:Day Name

Schedule:Week:Daily,
    Summer Control Type Week Sch - cool,  !- Name
    Summer Control Type Day Sch - cool,  !- Sunday Schedule:Day Name
    Summer Control Type Day Sch - cool,  !- Monday Schedule:Day Name
    Summer Control Type Day Sch - cool,  !- Tuesday Schedule:Day Name
    Summer Control Type Day Sch - cool,  !- Wednesday Schedule:Day Name
    Summer Control Type Day Sch - cool,  !- Thursday Schedule:Day Name
    Summer Control Type Day Sch - cool,  !- Friday Schedule:Day Name
    Summer Control Type Day Sch - cool,  !- Saturday Schedule:Day Name
    Summer Control Type Day Sch - cool,  !- Holiday Schedule:Day Name
    Summer Control Type Day Sch - cool,  !- SummerDesignDay Schedule:Day Name
    Summer Control Type Day Sch - cool,  !- WinterDesignDay Schedule:Day Name
    Summer Control Type Day Sch - cool,  !- CustomDay1 Schedule:Day Name
    Summer Control Type Day Sch - cool;  !- CustomDay2 Schedule:Day Name

Schedule:Week:Daily,
    Winter Control Type Week Sch - heat,  !- Name
    Winter Control Type Day Sch - heat,  !- Sunday Schedule:Day Name
    Winter Control Type Day Sch - heat,  !- Monday Schedule:Day Name
    Winter Control Type Day Sch - heat,  !- Tuesday Schedule:Day Name
    Winter Control Type Day Sch - heat,  !- Wednesday Schedule:Day Name
    Winter Control Type Day Sch - heat,  !- Thursday Schedule:Day Name
    Winter Control Type Day Sch - heat,  !- Friday Schedule:Day Name
    Winter Control Type Day Sch - heat,  !- Saturday Schedule:Day Name
    Winter Control Type Day Sch - heat,  !- Holiday Schedule:Day Name
    Winter Control Type Day Sch - heat,  !- SummerDesignDay Schedule:Day Name
    Winter Control Type Day Sch - heat,  !- WinterDesignDay Schedule:Day Name
    Winter Control Type Day Sch - heat,  !- CustomDay1 Schedule:Day Name
    Winter Control Type Day Sch - heat;  !- CustomDay2 Schedule:Day Name

Material:InfraredTransparent,
    IRTMaterial;             !- Name

Construction,
    IRTSurface,              !- Name
    IRTMaterial;             !- Outside Layer

Schedule:Compact,
    AirVelocitySchedule,     !- Name
    Any Number,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00, 0.137;     !- Field 4

! Schedule: On
Schedule:Compact,
    2,                       !- Name
    Any Number,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00, 1 ;        !- Field 4

! Schedule: Hot Water flow set point temperature: Always 80.0 C
Schedule:Compact,
    41,                      !- Name
    Any Number,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00, 80 ;       !- Field 4

! Schedule: Heating set point schedule
Schedule:Compact,
    46,                      !- Name
    Any Number,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00, 20 ;       !- Field 4

! Schedule: Cooling set point schedule
Schedule:Compact,
    47,                      !- Name
    Any Number,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00, 24 ;       !- Field 4

! Schedule: Control type schedule: Always 4
Schedule:Compact,
    48,                      !- Name
    Any Number,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00, 4 ;        !- Field 4

! Schedule: Relative humidity setpoint schedule: Always 50.00
Schedule:Compact,
    63,                      !- Name
    Any Number,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00, 50 ;       !- Field 4

! Schedule: Office_OpenOff_Occ
Schedule:Compact,
    2864,                    !- Name
    Fraction,                !- Schedule Type Limits Name
    Through: 31 Dec,         !- Field 1
    For: Weekdays SummerDesignDay,  !- Field 2
    Until: 07:00, 0,         !- Field 4
    Until: 08:00, 0.25,      !- Field 6
    Until: 09:00, 0.5,       !- Field 8
    Until: 12:00, 1,         !- Field 10
    Until: 14:00, 0.75,      !- Field 12
    Until: 17:00, 1,         !- Field 14
    Until: 18:00, 0.5,       !- Field 16
    Until: 19:00, 0.25,      !- Field 18
    Until: 24:00, 0,         !- Field 20
    For: Weekends,           !- Field 21
    Until: 24:00, 0,         !- Field 23
    For: Holidays,           !- Field 24
    Until: 24:00, 0,         !- Field 26
    For: WinterDesignDay AllOtherDays,  !- Field 27
    Until: 24:00, 0;         !- Field 29

! Schedule: Office_OpenOff_Equip
Schedule:Compact,
    2867,                    !- Name
    Fraction,                !- Schedule Type Limits Name
    Through: 31 Dec,         !- Field 1
    For: Weekdays SummerDesignDay,  !- Field 2
    Until: 07:00, 0.053941909,
                             !- Field 4
    Until: 20:00, 1,         !- Field 6
    Until: 24:00, 0.053941909,
                             !- Field 8
    For: Weekends,           !- Field 9
    Until: 24:00, 0.053941909,
                             !- Field 11
    For: Holidays,           !- Field 12
    Until: 24:00, 0.053941909,
                             !- Field 14
    For: WinterDesignDay AllOtherDays,  !- Field 15
    Until: 24:00, 0;         !- Field 17

! Schedule: Office_OpenOff_Light
Schedule:Compact,
    2868,                    !- Name
    Fraction,                !- Schedule Type Limits Name
    Through: 31 Dec,         !- Field 1
    For: Weekdays SummerDesignDay,  !- Field 2
    Until: 07:00, 0,         !- Field 4
    Until: 19:00, 1,         !- Field 6
    Until: 24:00, 0,         !- Field 8
    For: Weekends,           !- Field 9
    Until: 24:00, 0,         !- Field 11
    For: Holidays,           !- Field 12
    Until: 24:00, 0,         !- Field 14
    For: WinterDesignDay AllOtherDays,  !- Field 15
    Until: 24:00, 0;         !- Field 17

WindowMaterial:Gas,
    1002,                    !- Name
    Air,                     !- Gas Type
    0.013;                   !- Thickness {m}

WindowMaterial:Gas,
    Half thickness 1002,     !- Name
    Air,                     !- Gas Type
    0.0065;                  !- Thickness {m}

WindowMaterial:Glazing,
    2,                       !- Name
    SpectralAverage,         !- Optical Data Type
    ,                        !- Window Glass Spectral Data Set Name
    0.003,                   !- Thickness {m}
    0.837,                   !- Solar Transmittance at Normal Incidence
    0.075,                   !- Front Side Solar Reflectance at Normal Incidence
    0.075,                   !- Back Side Solar Reflectance at Normal Incidence
    0.898,                   !- Visible Transmittance at Normal Incidence
    0.081,                   !- Front Side Visible Reflectance at Normal Incidence
    0.081,                   !- Back Side Visible Reflectance at Normal Incidence
    0.0,                     !- Infrared Transmittance at Normal Incidence
    0.84,                    !- Front Side Infrared Hemispherical Emissivity
    0.84,                    !- Back Side Infrared Hemispherical Emissivity
    0.9,                     !- Conductivity {W/m-K}
    1;                       !- Dirt Correction Factor for Solar and Visible Transmittance

WindowMaterial:Glazing,
    38,                      !- Name
    SpectralAverage,         !- Optical Data Type
    ,                        !- Window Glass Spectral Data Set Name
    0.003,                   !- Thickness {m}
    0.740,                   !- Solar Transmittance at Normal Incidence
    0.090,                   !- Front Side Solar Reflectance at Normal Incidence
    0.100,                   !- Back Side Solar Reflectance at Normal Incidence
    0.820,                   !- Visible Transmittance at Normal Incidence
    0.110,                   !- Front Side Visible Reflectance at Normal Incidence
    0.120,                   !- Back Side Visible Reflectance at Normal Incidence
    0.0,                     !- Infrared Transmittance at Normal Incidence
    0.84,                    !- Front Side Infrared Hemispherical Emissivity
    0.20,                    !- Back Side Infrared Hemispherical Emissivity
    0.9,                     !- Conductivity {W/m-K}
    1;                       !- Dirt Correction Factor for Solar and Visible Transmittance

! Urea Formaldehyde Foam- thickness 0.1327
Material,
    1_1_37,                  !- Name
    Rough,                   !- Roughness
    0.1327,                  !- Thickness {m}
    0.04,                    !- Conductivity {W/m-K}
    10,                      !- Density {kg/m3}
    1400,                    !- Specific Heat {J/kg-K}
    0.9,                     !- Thermal Absorptance
    0.6,                     !- Solar Absorptance
    0.6;                     !- Visible Absorptance

! Cast Concrete- thickness 0.1
Material,
    1_2_9,                   !- Name
    Rough,                   !- Roughness
    0.1,                     !- Thickness {m}
    1.1300,                  !- Conductivity {W/m-K}
    2000.00,                 !- Density {kg/m3}
    1000.00,                 !- Specific Heat {J/kg-K}
    0.9,                     !- Thermal Absorptance
    0.6,                     !- Solar Absorptance
    0.6;                     !- Visible Absorptance

! Floor/Roof Screed- thickness 0.07
Material,
    1_3_29,                  !- Name
    Rough,                   !- Roughness
    0.07,                    !- Thickness {m}
    0.4100,                  !- Conductivity {W/m-K}
    1200.00,                 !- Density {kg/m3}
    840.00,                  !- Specific Heat {J/kg-K}
    0.9,                     !- Thermal Absorptance
    0.73,                    !- Solar Absorptance
    0.73;                    !- Visible Absorptance

! Timber Flooring- thickness 0.03
Material,
    1_4_34,                  !- Name
    Rough,                   !- Roughness
    0.03,                    !- Thickness {m}
    0.1400,                  !- Conductivity {W/m-K}
    650.00,                  !- Density {kg/m3}
    1200.00,                 !- Specific Heat {J/kg-K}
    0.9,                     !- Thermal Absorptance
    0.78,                    !- Solar Absorptance
    0.78;                    !- Visible Absorptance

! Asphalt- thickness 0.01
Material,
    3_1_4,                   !- Name
    Rough,                   !- Roughness
    0.01,                    !- Thickness {m}
    0.7000,                  !- Conductivity {W/m-K}
    2100,                    !- Density {kg/m3}
    1000.00,                 !- Specific Heat {J/kg-K}
    0.9,                     !- Thermal Absorptance
    0.85,                    !- Solar Absorptance
    0.9;                     !- Visible Absorptance

! MW Glass Wool (rolls)- thickness 0.1445
Material,
    3_2_20,                  !- Name
    Rough,                   !- Roughness
    0.1445,                  !- Thickness {m}
    0.040,                   !- Conductivity {W/m-K}
    12,                      !- Density {kg/m3}
    840,                     !- Specific Heat {J/kg-K}
    0.9,                     !- Thermal Absorptance
    0.6,                     !- Solar Absorptance
    0.6;                     !- Visible Absorptance

! Plasterboard- thickness 0.013
Material,
    3_4_113,                 !- Name
    Rough,                   !- Roughness
    0.013,                   !- Thickness {m}
    0.25,                    !- Conductivity {W/m-K}
    2800,                    !- Density {kg/m3}
    896,                     !- Specific Heat {J/kg-K}
    0.9,                     !- Thermal Absorptance
    0.5,                     !- Solar Absorptance
    0.5;                     !- Visible Absorptance

! Brickwork, Outer Leaf- thickness 0.1
Material,
    5_1_5,                   !- Name
    Rough,                   !- Roughness
    0.1,                     !- Thickness {m}
    0.8400,                  !- Conductivity {W/m-K}
    1700.00,                 !- Density {kg/m3}
    800.00,                  !- Specific Heat {J/kg-K}
    0.9,                     !- Thermal Absorptance
    0.7,                     !- Solar Absorptance
    0.7;                     !- Visible Absorptance

! XPS Extruded Polystyrene  - CO2 Blowing- thickness 0.0795
Material,
    5_2_103,                 !- Name
    Rough,                   !- Roughness
    0.0795,                  !- Thickness {m}
    0.034,                   !- Conductivity {W/m-K}
    35,                      !- Density {kg/m3}
    1400,                    !- Specific Heat {J/kg-K}
    0.9,                     !- Thermal Absorptance
    0.6,                     !- Solar Absorptance
    0.6;                     !- Visible Absorptance

! Concrete Block (Medium)- thickness 0.1
Material,
    5_3_11,                  !- Name
    Rough,                   !- Roughness
    0.1,                     !- Thickness {m}
    0.51,                    !- Conductivity {W/m-K}
    1400,                    !- Density {kg/m3}
    1000,                    !- Specific Heat {J/kg-K}
    0.9,                     !- Thermal Absorptance
    0.6,                     !- Solar Absorptance
    0.6;                     !- Visible Absorptance

! Gypsum Plastering- thickness 0.013
Material,
    5_4_66,                  !- Name
    Rough,                   !- Roughness
    0.013,                   !- Thickness {m}
    0.4000,                  !- Conductivity {W/m-K}
    1000,                    !- Density {kg/m3}
    1000,                    !- Specific Heat {J/kg-K}
    0.9,                     !- Thermal Absorptance
    0.50,                    !- Solar Absorptance
    0.50;                    !- Visible Absorptance

! 'Project ground floor'
Construction,
    1,                       !- Name
    1_1_37,                  !- Outside Layer
    1_2_9,                   !- Layer 2
    1_3_29,                  !- Layer 3
    1_4_34;                  !- Layer 4

! <Previous reversed>
Construction,
    2,                       !- Name
    1_4_34,                  !- Outside Layer
    1_3_29,                  !- Layer 2
    1_2_9,                   !- Layer 3
    1_1_37;                  !- Layer 4

! Special material to represent an R-value for the next construction
Material:NoMass,
    3_RVAL_3,                !- Name
    Rough,                   !- Roughness
    0.18,                    !- Thermal Resistance {m2-K/W}
    0.9,                     !- Thermal Absorptance
    0.7,                     !- Solar Absorptance
    0.7;                     !- Visible Absorptance

! 'Project flat roof'
Construction,
    3,                       !- Name
    3_1_4,                   !- Outside Layer
    3_2_20,                  !- Layer 2
    3_RVAL_3,                !- Layer 3
    3_4_113;                 !- Layer 4

! Special material to represent an R-value for the next construction
Material:NoMass,
    4_RVAL_2,                !- Name
    Rough,                   !- Roughness
    0.18,                    !- Thermal Resistance {m2-K/W}
    0.9,                     !- Thermal Absorptance
    0.7,                     !- Solar Absorptance
    0.7;                     !- Visible Absorptance

! <Previous reversed>
Construction,
    4,                       !- Name
    3_4_113,                 !- Outside Layer
    4_RVAL_2,                !- Layer 2
    3_2_20,                  !- Layer 3
    3_1_4;                   !- Layer 4

! 'Project wall'
Construction,
    5,                       !- Name
    5_1_5,                   !- Outside Layer
    5_2_103,                 !- Layer 2
    5_3_11,                  !- Layer 3
    5_4_66;                  !- Layer 4

! <Previous reversed>
Construction,
    6,                       !- Name
    5_4_66,                  !- Outside Layer
    5_3_11,                  !- Layer 2
    5_2_103,                 !- Layer 3
    5_1_5;                   !- Layer 4

Construction,
    1001,                    !- Name
    38,                      !- Outside Layer
    1002,                    !- Layer 2
    2;                       !- Layer 3

HeatBalanceAlgorithm,ConductionTransferFunction,2000;

ShadowCalculation,
    20,                      !- Calculation Frequency
    15000,                   !- Maximum Figures in Shadow Overlap Calculations
    SutherlandHodgman,       !- Polygon Clipping Algorithm
    SimpleSkyDiffuseModeling;!- Sky Diffuse Modeling Algorithm

SurfaceConvectionAlgorithm:Inside,TARP;
SurfaceConvectionAlgorithm:Outside,DOE-2;
ZoneCapacitanceMultiplier:ResearchSpecial,1.0,,;

Building,
    Building,                !- Name
    0,                       !- North Axis {deg}
    Suburbs,                 !- Terrain
    0.04,                    !- Loads Convergence Tolerance Value
    0.4,                     !- Temperature Convergence Tolerance Value {deltaC}
    FullExterior,            !- Solar Distribution
    25,                      !- Maximum Number of Warmup Days
    ;                        !- Minimum Number of Warmup Days

GlobalGeometryRules,
    LowerLeftCorner,         !- Starting Vertex Position
    CounterClockWise,        !- Vertex Entry Direction
    Relative;                !- Coordinate System

! Block 1 - Zone 1
Zone,
    Block1:Zone1,            !- Name
    0,                       !- Direction of Relative North {deg}
    0, 0, 0,                            !- X,Y,Z  {m}
    1,                       !- Type
    1,                       !- Multiplier
    ,                        !- Ceiling Height {m}
    1700.6506,               !- Volume {m3}
    485.9002,                !- Floor Area {m2}
    TARP;                    !- Zone Inside Convection Algorithm

People,
    People Block1:Zone1,     !- Name
    Block1:Zone1,            !- Zone or ZoneList Name
    2864,                    !- Number of People Schedule Name
    People,                  !- Number of People Calculation Method
    53.9349222,              !- Number of People
    ,                        !- People per Zone Floor Area {person/m2}
    ,                        !- Zone Floor Area per Person {m2/person}
    0.3,                     !- Fraction Radiant
    AUTOCALCULATE,           !- Sensible Heat Fraction
    Activity Schedule 16,    !- Activity Level Schedule Name
    3.82E-8,                 !- Carbon Dioxide Generation Rate {m3/s-W}
    No,                      !- Enable ASHRAE 55 Comfort Warnings
    ZoneAveraged,            !- Mean Radiant Temperature Calculation Type
    ,                        !- Surface Name/Angle Factor List Name
    Work efficiency,         !- Work Efficiency Schedule Name
    Clothing Schedule 16,    !- Clothing Insulation Schedule Name
    AirVelocitySchedule;     !- Air Velocity Schedule Name

Schedule:Compact,
    Activity Schedule 16,    !- Name
    Any Number,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00, 110.7;     !- Field 4

Schedule:Compact,
    Clothing Schedule 16,    !- Name
    Any Number,              !- Schedule Type Limits Name
    Through: 4/1,            !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00, 1,         !- Field 4
    Through: 9/30,           !- Field 5
    For: AllDays,            !- Field 6
    Until: 24:00, .5,        !- Field 8
    Through: 12/31,          !- Field 9
    For: AllDays,            !- Field 10
    Until: 24:00, 1;         !- Field 12

Lights,
    Block1:Zone1 General lighting,  !- Name
    Block1:Zone1,            !- Zone or ZoneList Name
    2868,                    !- Schedule Name
    LightingLevel,           !- Design Level Calculation Method
    9718.004,                !- Lighting Level {W}
    ,                        !- Watts per Zone Floor Area {W/m2}
    ,                        !- Watts per Person {W/person}
    0,                       !- Return Air Fraction
    0.42,                    !- Fraction Radiant
    0.18,                    !- Fraction Visible
    1,                       !- Fraction Replaceable
    ELECTRIC EQUIPMENT#Block1:Zone1#GeneralLights;  !- End-Use Subcategory

! Equipment 1
ElectricEquipment,
    Block1:Zone1 Equipment 1,!- Name
    Block1:Zone1,            !- Zone or ZoneList Name
    2867,                    !- Schedule Name
    EquipmentLevel,          !- Design Level Calculation Method
    5719.0454,               !- Design Level {W}
    ,                        !- Watts per Zone Floor Area {W/m2}
    ,                        !- Watts per Person {W/person}
    0,                       !- Fraction Latent
    0.2,                     !- Fraction Radiant
    0,                       !- Fraction Lost
    ELECTRIC EQUIPMENT#Block1:Zone1#05;  !- End-Use Subcategory

ZoneInfiltration:DesignFlowRate,
    Block1:Zone1 Infiltration,  !- Name
    Block1:Zone1,            !- Zone or ZoneList Name
    On,                      !- Schedule Name
    Flow/zone,               !- Design Flow Rate Calculation Method
    0.330682,                !- Design Flow Rate {m3/s}
    ,                        !- Flow per Zone Floor Area {m3/s-m2}
    ,                        !- Flow per Exterior Surface Area {m3/s-m2}
    ,                        !- Air Changes per Hour
    1,                       !- Constant Term Coefficient
    0,                       !- Temperature Term Coefficient
    0,                       !- Velocity Term Coefficient
    0;                       !- Velocity Squared Term Coefficient

! Block 1, Zone 1, Ground floor - 485.900 m2 (Ground), Surface Area: 485.900m2
BuildingSurface:Detailed,
    Block1:Zone1_GroundFloor_0_0_0,  !- Name
    Floor,                   !- Surface Type
    1,                       !- Construction Name
    Block1:Zone1,            !- Zone Name
    Ground,                  !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    1,                       !- View Factor to Ground
    4,                       !- Number of Vertices
    8.9473207075, -13.0191344575, 0,    !- X,Y,Z  1 {m}
    -10.2051528139, -13.0191344575, 0,  !- X,Y,Z  2 {m}
    -10.2051528139, 12.3509653712, 0,   !- X,Y,Z  3 {m}
    8.9473207075, 12.3509653712, 0;     !- X,Y,Z  4 {m}

! Block 1, Zone 1, Roof - 485.900 m2, Surface Area: 485.900m2
BuildingSurface:Detailed,
    Block1:Zone1_Roof_1_0_0, !- Name
    Roof,                    !- Surface Type
    3,                       !- Construction Name
    Block1:Zone1,            !- Zone Name
    Outdoors,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    0,                       !- View Factor to Ground
    4,                       !- Number of Vertices
    -10.2051528139, -13.0191344575, 3.5,
                                        !- X,Y,Z  1 {m}
    8.9473207075, -13.0191344575, 3.5,  !- X,Y,Z  2 {m}
    8.9473207075, 12.3509653712, 3.5,   !- X,Y,Z  3 {m}
    -10.2051528139, 12.3509653712, 3.5; !- X,Y,Z  4 {m}

! Block 1, Zone 1, Wall - 88.795 m2 - 90.0°, Surface Area: 88.795m2
BuildingSurface:Detailed,
    Block1:Zone1_Wall_2_0_0, !- Name
    Wall,                    !- Surface Type
    5,                       !- Construction Name
    Block1:Zone1,            !- Zone Name
    Outdoors,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Vertices
    8.9473207075, -13.0191344575, 0,    !- X,Y,Z  1 {m}
    8.9473207075, 12.3509653712, 0,     !- X,Y,Z  2 {m}
    8.9473207075, 12.3509653712, 3.5,   !- X,Y,Z  3 {m}
    8.9473207075, -13.0191344575, 3.5;  !- X,Y,Z  4 {m}

! Window, 4.930m2 X 5
FenestrationSurface:Detailed,
    Block1:Zone1_Wall_2_0_0_0_0_0_Win,  !- Name
    Window,                  !- Surface Type
    1001,                    !- Construction Name
    Block1:Zone1_Wall_2_0_0, !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    0.5,                     !- View Factor to Ground
    ,                        !- Shading Control Name
    1,                       !- Frame and Divider Name
    5,                       !- Multiplier
    4,                       !- Number of Vertices
    8.9473207075, 8.0740483989, 0.84,   !- X,Y,Z  1 {m}
    8.9473207075, 11.5458623751, 0.84,  !- X,Y,Z  2 {m}
    8.9473207075, 11.5458623751, 2.26,  !- X,Y,Z  3 {m}
    8.9473207075, 8.0740483989, 2.26;   !- X,Y,Z  4 {m}

! Block 1, Zone 1, Wall - 67.034 m2 - 0.0°, Surface Area: 67.034m2
BuildingSurface:Detailed,
    Block1:Zone1_Wall_3_0_0, !- Name
    Wall,                    !- Surface Type
    5,                       !- Construction Name
    Block1:Zone1,            !- Zone Name
    Outdoors,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Vertices
    8.9473207075, 12.3509653712, 0,     !- X,Y,Z  1 {m}
    -10.2051528139, 12.3509653712, 0,   !- X,Y,Z  2 {m}
    -10.2051528139, 12.3509653712, 3.5, !- X,Y,Z  3 {m}
    8.9473207075, 12.3509653712, 3.5;   !- X,Y,Z  4 {m}

! Window, 6.232m2 X 3
FenestrationSurface:Detailed,
    Block1:Zone1_Wall_3_0_0_0_0_0_Win,  !- Name
    Window,                  !- Surface Type
    1001,                    !- Construction Name
    Block1:Zone1_Wall_3_0_0, !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    0.5,                     !- View Factor to Ground
    ,                        !- Shading Control Name
    1,                       !- Frame and Divider Name
    3,                       !- Multiplier
    4,                       !- Number of Vertices
    -4.8152853127, 12.3509653712, 0.84, !- X,Y,Z  1 {m}
    -9.2041958007, 12.3509653712, 0.84, !- X,Y,Z  2 {m}
    -9.2041958007, 12.3509653712, 2.26, !- X,Y,Z  3 {m}
    -4.8152853127, 12.3509653712, 2.26; !- X,Y,Z  4 {m}

! Block 1, Zone 1, Wall - 88.795 m2 - 270.0°, Surface Area: 88.795m2
BuildingSurface:Detailed,
    Block1:Zone1_Wall_4_0_0, !- Name
    Wall,                    !- Surface Type
    5,                       !- Construction Name
    Block1:Zone1,            !- Zone Name
    Outdoors,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Vertices
    -10.2051528139, 12.3509653712, 0,   !- X,Y,Z  1 {m}
    -10.2051528139, -13.0191344575, 0,  !- X,Y,Z  2 {m}
    -10.2051528139, -13.0191344575, 3.5,
                                        !- X,Y,Z  3 {m}
    -10.2051528139, 12.3509653712, 3.5; !- X,Y,Z  4 {m}

! Window, 4.930m2 X 5
FenestrationSurface:Detailed,
    Block1:Zone1_Wall_4_0_0_0_0_0_Win,  !- Name
    Window,                  !- Surface Type
    1001,                    !- Construction Name
    Block1:Zone1_Wall_4_0_0, !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    0.5,                     !- View Factor to Ground
    ,                        !- Shading Control Name
    1,                       !- Frame and Divider Name
    5,                       !- Multiplier
    4,                       !- Number of Vertices
    -10.2051528139, -8.7422174889, 0.84,
                                        !- X,Y,Z  1 {m}
    -10.2051528139, -12.2140314651, 0.84,
                                        !- X,Y,Z  2 {m}
    -10.2051528139, -12.2140314651, 2.26,
                                        !- X,Y,Z  3 {m}
    -10.2051528139, -8.7422174889, 2.26;
                                        !- X,Y,Z  4 {m}

! Block 1, Zone 1, Wall - 67.034 m2 - 180.0°, Surface Area: 67.034m2
BuildingSurface:Detailed,
    Block1:Zone1_Wall_5_0_0, !- Name
    Wall,                    !- Surface Type
    5,                       !- Construction Name
    Block1:Zone1,            !- Zone Name
    Outdoors,                !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Vertices
    -10.2051528139, -13.0191344575, 0,  !- X,Y,Z  1 {m}
    8.9473207075, -13.0191344575, 0,    !- X,Y,Z  2 {m}
    8.9473207075, -13.0191344575, 3.5,  !- X,Y,Z  3 {m}
    -10.2051528139, -13.0191344575, 3.5;
                                        !- X,Y,Z  4 {m}

! Window, 6.232m2 X 3
FenestrationSurface:Detailed,
    Block1:Zone1_Wall_5_0_0_0_0_0_Win,  !- Name
    Window,                  !- Surface Type
    1001,                    !- Construction Name
    Block1:Zone1_Wall_5_0_0, !- Building Surface Name
    ,                        !- Outside Boundary Condition Object
    0.5,                     !- View Factor to Ground
    ,                        !- Shading Control Name
    1,                       !- Frame and Divider Name
    3,                       !- Multiplier
    4,                       !- Number of Vertices
    3.5574532127, -13.0191344575, 0.84, !- X,Y,Z  1 {m}
    7.9463637007, -13.0191344575, 0.84, !- X,Y,Z  2 {m}
    7.9463637007, -13.0191344575, 2.26, !- X,Y,Z  3 {m}
    3.5574532127, -13.0191344575, 2.26; !- X,Y,Z  4 {m}

WindowProperty:FrameAndDivider,
    1,                       !- Name
    0.040,                   !- Frame Width {m}
    0.0,                     !- Frame Outside Projection {m}
    0.0,                     !- Frame Inside Projection {m}
    9.5,                     !- Frame Conductance {W/m2-K}
    1.0,                     !- Ratio of Frame-Edge Glass Conductance to Center-Of-Glass Conductance
    0.5,                     !- Frame Solar Absorptance
    0.5,                     !- Frame Visible Absorptance
    0.9,                     !- Frame Thermal Hemispherical Emissivity
    DividedLite,             !- Divider Type
    0.020,                   !- Divider Width {m}
    1,                       !- Number of Horizontal Dividers
    1,                       !- Number of Vertical Dividers
    0.0,                     !- Divider Outside Projection {m}
    0.0,                     !- Divider Inside Projection {m}
    9.5,                     !- Divider Conductance {W/m2-K}
    1.0,                     !- Ratio of Divider-Edge Glass Conductance to Center-Of-Glass Conductance
    0.5,                     !- Divider Solar Absorptance
    0.5,                     !- Divider Visible Absorptance
    0.9,                     !- Divider Thermal Hemispherical Emissivity
    0.5,                     !- Outside Reveal Solar Absorptance
    0.0,                     !- Inside Sill Depth {m}
    0.5,                     !- Inside Sill Solar Absorptance
    0.0,                     !- Inside Reveal Depth {m}
    0.5;                     !- Inside Reveal Solar Absorptance

! Curve: <None>
Curve:Linear,
    <None>,                  !- Name
    0,                       !- Coefficient1 Constant
    0,                       !- Coefficient2 x
    0,                       !- Minimum Value of x
    1;                       !- Maximum Value of x

Output:Table:SummaryReports,
    AnnualBuildingUtilityPerformanceSummary,  !- Report 1 Name
    InputVerificationandResultsSummary,  !- Report 2 Name
    ClimaticDataSummary,     !- Report 3 Name
    EquipmentSummary,        !- Report 4 Name
    EnvelopeSummary,         !- Report 5 Name
    LightingSummary,         !- Report 6 Name
    HVACSizingSummary,       !- Report 7 Name
    SystemSummary,           !- Report 8 Name
    ComponentSizingSummary,  !- Report 9 Name
    OutdoorAirSummary,       !- Report 10 Name
    ObjectCountSummary;      !- Report 11 Name

OutputControl:Table:Style,
    CommaAndHTML,            !- Column Separator
    JtoKWH;                  !- Unit Conversion

OutputControl:IlluminanceMap:Style,
    Comma;                   !- Column Separator

Output:Variable,*,Outdoor Dry Bulb,timestep;
Output:Variable,Block1:Zone1,Zone Mean Air Temperature,timestep,On;
Output:Variable,Block1:Zone1,Zone Mean Radiant Temperature,timestep,On;
Output:Variable,Block1:Zone1,Zone Air Relative Humidity,timestep,On;
Output:Variable,*,Outdoor Dry Bulb,hourly;
Output:Variable,Block1:Zone1,Zone Mean Air Temperature,hourly,On;
Output:Variable,Block1:Zone1,Zone Mean Radiant Temperature,hourly,On;
Output:Variable,Block1:Zone1,Zone Air Relative Humidity,hourly,On;
Output:Variable,*,Outdoor Dry Bulb,daily;
Output:Variable,Block1:Zone1,Zone Mean Air Temperature,daily,On;
Output:Variable,Block1:Zone1,Zone Mean Radiant Temperature,daily,On;
Output:Variable,Block1:Zone1,Zone Air Relative Humidity,daily,On;
Output:Variable,*,Outdoor Dry Bulb,monthly;
Output:Variable,Block1:Zone1,Zone Mean Air Temperature,monthly,On;
Output:Variable,Block1:Zone1,Zone Mean Radiant Temperature,monthly,On;
Output:Variable,Block1:Zone1,Zone Air Relative Humidity,monthly,On;
Output:Variable,Block1:Zone1,Zone Infiltration Air Change Rate,timestep;
Output:Variable,Block1:Zone1,Zone Infiltration Air Change Rate,hourly;
Output:Variable,Block1:Zone1,Zone Infiltration Air Change Rate,daily;
Output:Variable,Block1:Zone1,Zone Infiltration Air Change Rate,monthly;
Output:Variable,*,Pump Electric Consumption,timestep;
Output:Variable,*,Sensible Water Cooling Coil Rate,timestep;
Output:Variable,*,Boiler Electric Consumption Rate,timestep;
Output:Variable,*,Boiler Gas Consumption Rate,timestep;
Output:Variable,Block1:Zone1,Zone/Sys Sensible Heating Rate,timestep;
Output:Variable,Block1:Zone1Baseboard Heat,Baseboard Heating Rate,timestep;
Output:Variable,*,Sensible Water Cooling Coil Rate,hourly;
Output:Variable,*,Boiler Electric Consumption Rate,hourly;
Output:Variable,*,Boiler Gas Consumption Rate,hourly;
Output:Variable,*,Water Use Equipment Heating Rate,hourly;
Output:Variable,*,Water Heater Gas Consumption Rate,hourly;
Output:Variable,*,Water Heater FuelOil#1 Consumption Rate,hourly;
Output:Variable,*,Constant Flow Low Temp Radiant Cooling Energy,hourly;
Output:Variable,*,Constant Flow Low Temp Radiant Heating Energy,hourly;
Output:Variable,*,BaseBoard Electric Consumption,hourly;
Output:Variable,Block1:Zone1,Zone/Sys Sensible Heating Rate,hourly;
Output:Variable,Block1:Zone1,Zone/Sys Sensible Cooling Rate,hourly;
Output:Variable,Block1:Zone1Baseboard Heat,Baseboard Heating Rate,hourly;
Output:Variable,*,Pump Electric Consumption,daily;
Output:Variable,*,Total Water Heating Coil Rate,daily;
Output:Variable,*,Boiler Gas Consumption Rate,daily;
Output:Variable,*,Constant Flow Low Temp Radiant Heating Energy,daily;
Output:Variable,*,BaseBoard Electric Consumption,daily;
Output:Variable,Block1:Zone1,Zone/Sys Sensible Heating Rate,daily;
Output:Variable,Block1:Zone1,Zone/Sys Sensible Cooling Rate,daily;
Output:Variable,Block1:Zone1Baseboard Heat,Baseboard Heating Rate,daily;
Output:Variable,*,Heating Coil Electric Consumption,monthly;
Output:Variable,*,Heating Coil Gas Consumption,monthly;
Output:Variable,*,Boiler Gas Consumption Rate,monthly;
Output:Variable,*,Boiler Propane Consumption Rate,monthly;
Output:Variable,*,Boiler FuelOil#1 Consumption Rate,monthly;
Output:Variable,*,Boiler FuelOil#2 Consumption Rate,monthly;
Output:Variable,*,Boiler Coal Consumption Rate,monthly;
Output:Variable,*,Boiler Diesel Consumption Rate,monthly;
Output:Variable,*,Boiler Gasoline Consumption Rate,monthly;
Output:Variable,*,Chiller Electric Power,monthly;
Output:Variable,*,Chiller Cond Fan Electric Consumption,monthly;
Output:Variable,*,Tower Fan Electric Consumption,monthly;
Output:Variable,*,Heat Exchanger Sensible Heating Rate,monthly;
Output:Variable,*,Heat Exchanger Total Heating Rate,monthly;
Output:Variable,*,Heat Exchanger Sensible Cooling Rate,monthly;
Output:Variable,*,Heat Exchanger Total Cooling Rate,monthly;
Output:Variable,*,Humidifier Electric Power,monthly;
Output:Variable,*,Air Loop Evap Cooler Electric Consumption,monthly;
Output:Variable,*,Air Loop Desiccant Dehumidifier Electric Consumption,monthly;
Output:Variable,*,Fan Electric Consumption,monthly;
Output:Variable,*,Water Use Equipment Heating Rate,monthly;
Output:Variable,*,Water Heater Electric Consumption Rate,monthly;
Output:Variable,*,Water Heater Gas Consumption Rate,monthly;
Output:Variable,*,Water Heater Propane Consumption Rate,monthly;
Output:Variable,*,Water Heater FuelOil#1 Consumption Rate,monthly;
Output:Variable,*,Water Heater FuelOil#2 Consumption Rate,monthly;
Output:Variable,*,Water Heater Coal Consumption Rate,monthly;
Output:Variable,*,Water Heater Diesel Consumption Rate,monthly;
Output:Variable,*,Water Heater Gasoline Consumption Rate,monthly;
Output:Variable,*,Constant Flow Low Temp Radiant Cooling Energy,monthly;
Output:Variable,*,Constant Flow Low Temp Radiant Heating Energy,monthly;
Output:Variable,*,BaseBoard Electric Consumption,monthly;
Output:Variable,Block1:Zone1,Zone/Sys Sensible Heating Rate,monthly;
Output:Variable,Block1:Zone1,Zone/Sys Sensible Cooling Rate,monthly;
Output:Variable,Block1:Zone1Baseboard Heat,Baseboard Heating Rate,monthly;
Output:Variable,Block1:Zone1,Zone People Sensible Heat Gain,timestep;
Output:Variable,Block1:Zone1,Zone Transmitted Solar,timestep;
Output:Variable,Block1:Zone1,Zone Diff Solar from Interior Windows,timestep;
Output:Variable,Block1:Zone1,Zone Beam Solar from Interior Windows,timestep;
Output:Variable,Block1:Zone1,Zone Infiltration Sensible Heat Loss,timestep;
Output:Variable,Block1:Zone1,Zone Infiltration Sensible Heat Gain,timestep;
Output:Variable,Block1:Zone1,Zone Ventilation Sensible Heat Loss,timestep;
Output:Variable,Block1:Zone1,Zone Ventilation Sensible Heat Gain,timestep;
Output:Variable,Block1:Zone1,Zone Mixing Sensible Heat Loss,timestep;
Output:Variable,Block1:Zone1,Zone Mixing Sensible Heat Gain,timestep;
Output:Variable,Block1:Zone1,Zone Other Equipment Total Heat Gain,timestep;
Output:Meter,ELECTRIC EQUIPMENT#Block1:Zone1#05:InteriorEquipment*,timestep;
Output:Meter,ELECTRIC EQUIPMENT#Block1:Zone1#GeneralLights*,timestep;
Output:Variable,Block1:Zone1,Zone People Sensible Heat Gain,hourly;
Output:Variable,Block1:Zone1,Zone Transmitted Solar,hourly;
Output:Variable,Block1:Zone1,Zone Diff Solar from Interior Windows,hourly;
Output:Variable,Block1:Zone1,Zone Beam Solar from Interior Windows,hourly;
Output:Variable,Block1:Zone1,Zone Infiltration Sensible Heat Loss,hourly;
Output:Variable,Block1:Zone1,Zone Infiltration Sensible Heat Gain,hourly;
Output:Variable,Block1:Zone1,Zone Ventilation Sensible Heat Loss,hourly;
Output:Variable,Block1:Zone1,Zone Ventilation Sensible Heat Gain,hourly;
Output:Variable,Block1:Zone1,Zone Mixing Sensible Heat Loss,hourly;
Output:Variable,Block1:Zone1,Zone Mixing Sensible Heat Gain,hourly;
Output:Variable,Block1:Zone1,Zone Other Equipment Total Heat Gain,hourly;
Output:Meter,ELECTRIC EQUIPMENT#Block1:Zone1#05:InteriorEquipment*,hourly;
Output:Meter,ELECTRIC EQUIPMENT#Block1:Zone1#GeneralLights*,hourly;
Output:Variable,Block1:Zone1,Zone People Sensible Heat Gain,daily;
Output:Variable,Block1:Zone1,Zone Transmitted Solar,daily;
Output:Variable,Block1:Zone1,Zone Diff Solar from Interior Windows,daily;
Output:Variable,Block1:Zone1,Zone Beam Solar from Interior Windows,daily;
Output:Variable,Block1:Zone1,Zone Infiltration Sensible Heat Loss,daily;
Output:Variable,Block1:Zone1,Zone Infiltration Sensible Heat Gain,daily;
Output:Variable,Block1:Zone1,Zone Ventilation Sensible Heat Loss,daily;
Output:Variable,Block1:Zone1,Zone Ventilation Sensible Heat Gain,daily;
Output:Variable,Block1:Zone1,Zone Mixing Sensible Heat Loss,daily;
Output:Variable,Block1:Zone1,Zone Mixing Sensible Heat Gain,daily;
Output:Variable,Block1:Zone1,Zone Other Equipment Total Heat Gain,daily;
Output:Meter,ELECTRIC EQUIPMENT#Block1:Zone1#05:InteriorEquipment*,daily;
Output:Meter,ELECTRIC EQUIPMENT#Block1:Zone1#GeneralLights*,daily;
Output:Variable,Block1:Zone1,Zone People Sensible Heat Gain,monthly;
Output:Variable,Block1:Zone1,Zone Transmitted Solar,monthly;
Output:Variable,Block1:Zone1,Zone Diff Solar from Interior Windows,monthly;
Output:Variable,Block1:Zone1,Zone Beam Solar from Interior Windows,monthly;
Output:Variable,Block1:Zone1,Zone Infiltration Sensible Heat Loss,monthly;
Output:Variable,Block1:Zone1,Zone Infiltration Sensible Heat Gain,monthly;
Output:Variable,Block1:Zone1,Zone Ventilation Sensible Heat Loss,monthly;
Output:Variable,Block1:Zone1,Zone Ventilation Sensible Heat Gain,monthly;
Output:Variable,Block1:Zone1,Zone Mixing Sensible Heat Loss,monthly;
Output:Variable,Block1:Zone1,Zone Mixing Sensible Heat Gain,monthly;
Output:Variable,Block1:Zone1,Zone Other Equipment Total Heat Gain,monthly;
Output:Meter,ELECTRIC EQUIPMENT#Block1:Zone1#05:InteriorEquipment*,monthly;
Output:Meter,ELECTRIC EQUIPMENT#Block1:Zone1#GeneralLights*,monthly;
Output:Surfaces:Drawing,DXF,Triangulate3DFace;
Output:Surfaces:List,Details;
Output:Constructions,Construction;
Output:VariableDictionary,Regular;

Output:Diagnostics,
    DisplayAdvancedReportVariables;  !- Key 1



--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Tooran" <t.t111ir@...> wrote:
>
> Dear memebers ,
> ref : Document  :EngineeringRefrence.pdf -983
> "High temperature turn off :
> The input object availabilityManager:High temperaturTurnoff is used to turn off  a central air system or a plant loop if a sensed node temperature exceeds a temperature limit."
> 
> i want to know  availabilityManager:High temperaturTurnoff , turn off the plant loop or just the turn off the component ?
>  for example :  i set field :Sensor Node name : at the outlet of boiler .. in this plant loop there is pump and boiler as a component.
> 
> then availabilityManager:High temperaturTurnoff  turn off boiler or plant loop ?if it turn off the plant loop it means it turned off pump too?
> 
> thanks
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/