[EnergyPlus_Support] Regarding an error





Hi,
 
I'm working with the hospital prototype of DOE-2 in Phoenix climate. I'm having problem to identify the following error message. If someone can give me any feedback on that it would be a great help.
 
Thanks,
Sadia Haque 
 
Program Version,EnergyPlus-64 7.0.0.036, 2/8/2012 6:31 PM,IDD_Version 7.0.0.036
   ************* Beginning Zone Sizing Calculations
   ** Warning ** CheckUsedConstructions: There are 1 nominally unused constructions in input.
   **   ~~~   ** For explicit details on each unused construction, use Output:Diagnostics,DisplayExtraWarnings;
   ** Warning ** Calculated design heating load for zone=CORRIDOR_NW_FLR_3 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design heating load for zone=CORRIDOR_NW_FLR_4 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design heating load for zone=CORRIDOR_SE_FLR_3 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design heating load for zone=CORRIDOR_SE_FLR_4 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design heating load for zone=ER_EXAM3_MULT4_FLR_1 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design heating load for zone=ER_NURSESTN_LOBBY_FLR_1 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design heating load for zone=ICU_FLR_2 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design heating load for zone=ICU_NURSESTN_LOBBY_FLR_2 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design heating load for zone=LAB_FLR_3 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design heating load for zone=LAB_FLR_4 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design heating load for zone=NURSESTN_LOBBY_FLR_3 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design heating load for zone=NURSESTN_LOBBY_FLR_4 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design heating load for zone=OR2_MULT5_FLR_2 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design heating load for zone=OR3_FLR_2 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design heating load for zone=OR4_FLR_2 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design heating load for zone=PHYSTHERAPY_FLR_3 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design heating load for zone=RADIOLOGY_FLR_4 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ************* Beginning System Sizing Calculations
   ************* Beginning Plant Sizing Calculations
   ************* Testing Individual Branch Integrity
   ************* All Branches passed integrity testing
   ************* Testing Individual Supply Air Path Integrity
   ************* All Supply Air Paths passed integrity testing
   ************* Testing Individual Return Air Path Integrity
   ************* All Return Air Paths passed integrity testing
   ************* No node connection errors were found.
   ************* Beginning Simulation
   ** Warning ** SolveAirLoopControllers: Maximum iterations (50) exceeded for VAV_2, at Phoenix Sky Harbor Intl Ap AZ USA TMY3 WMO#=722780, 01/03 05:13 - 05:15
   ** Warning ** SolveAirLoopControllers: Maximum iterations (50) exceeded for VAV_2, at Phoenix Sky Harbor Intl Ap AZ USA TMY3 WMO#=722780, 01/03 05:15 - 05:30
   ** Warning ** SolveAirLoopControllers: Maximum iterations (50) exceeded for VAV_2, at Phoenix Sky Harbor Intl Ap AZ USA TMY3 WMO#=722780, 01/12 05:11 - 05:13
   ** Warning ** SolveAirLoopControllers: Maximum iterations (50) exceeded for VAV_2, at Phoenix Sky Harbor Intl Ap AZ USA TMY3 WMO#=722780, 01/12 05:11 - 05:13
   ** Warning ** SolveAirLoopControllers: Maximum iterations (50) exceeded for VAV_2, at Phoenix Sky Harbor Intl Ap AZ USA TMY3 WMO#=722780, 01/12 05:11 - 05:13
   ** Warning ** SolveAirLoopControllers: Maximum iterations (50) exceeded for VAV_2, at Phoenix Sky Harbor Intl Ap AZ USA TMY3 WMO#=722780, 01/23 22:00 - 22:15
   ** Warning ** SolveAirLoopControllers: Maximum iterations (50) exceeded for VAV_2, at Phoenix Sky Harbor Intl Ap AZ USA TMY3 WMO#=722780, 01/30 03:00 - 03:15
   ** Warning ** SolveAirLoopControllers: Maximum iterations (50) exceeded for VAV_2, at Phoenix Sky Harbor Intl Ap AZ USA TMY3 WMO#=722780, 02/23 05:30 - 05:45
   ** Warning ** SolveAirLoopControllers: Maximum iterations (50) exceeded for VAV_2, at Phoenix Sky Harbor Intl Ap AZ USA TMY3 WMO#=722780, 02/23 05:30 - 05:45
   ** Warning ** SolveAirLoopControllers: Maximum iterations (50) exceeded for VAV_2, at Phoenix Sky Harbor Intl Ap AZ USA TMY3 WMO#=722780, 02/23 05:30 - 05:45
   ** Warning ** SolveAirLoopControllers: Maximum iterations (50) exceeded for VAV_2, at Phoenix Sky Harbor Intl Ap AZ USA TMY3 WMO#=722780, 03/02 03:30 - 03:45
   ** Warning ** SolveAirLoopControllers: Maximum iterations (50) exceeded for VAV_2, at Phoenix Sky Harbor Intl Ap AZ USA TMY3 WMO#=722780, 03/02 05:00 - 05:15
   ** Warning ** SolveAirLoopControllers: Maximum iterations (50) exceeded for VAV_2, at Phoenix Sky Harbor Intl Ap AZ USA TMY3 WMO#=722780, 03/02 05:00 - 05:15
   ** Warning ** SolveAirLoopControllers: Maximum iterations (50) exceeded for VAV_2, at Phoenix Sky Harbor Intl Ap AZ USA TMY3 WMO#=722780, 03/02 05:00 - 05:15
   ** Warning ** WriteVeriSumTable: InputVerificationsAndResultsSummary: Wall area based on [>=60,<=120] degrees (tilt) as walls
   **   ~~~   ** differs ~11.6% from user entered Wall class surfaces. Degree calculation based on ASHRAE 90.1 wall definitions.
   **   ~~~   ** Calculated based on degrees=[5786.591] m2, Calculated from user entered Wall class surfaces=[5184.431] m2.
   **   ~~~   ** Check classes of surfaces and tilts for discrepancies.
   ************* Simulation Error Summary *************
   ************* There are 1 unused schedules in input.
   ************* Use Output:Diagnostics,DisplayUnusedSchedules; to see them.
   *************
   ************* ===== Recurring Error Summary =====
   ************* The following recurring error messages occurred.
   *************
   *************  ** Warning ** SolveAirLoopControllers: Exceeding Maximum iterations for VAV_2 during Phoenix Sky Harbor Intl Ap AZ USA TMY3 WMO#=722780 continues
   *************  **   ~~~   **   This error occurred 29 total times;
   *************  **   ~~~   **   during Warmup 0 times;
   *************  **   ~~~   **   during Sizing 0 times.
   *************
   *************
   ************* ===== Final Error Summary =====
   ************* The following error categories occurred.  Consider correcting or noting.
   ************* Nominally Unused Constructions
   ************* ..The nominally unused constructions warning is provided to alert you to potential conditions that can cause
   ************* ..extra time during simulation. Each construction is calculated by the algorithm indicated in the HeatBalanceAlgorithm
   ************* ..object. You may remove the constructions indicated (when you use the DisplayExtraWarnings option).
   *************
   ************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
   ************* EnergyPlus Sizing Error Summary. During Sizing: 18 Warning; 0 Severe Errors.
   ************* EnergyPlus Completed Successfully-- 62 Warning; 0 Severe Errors; Elapsed Time=00hr 08min 12.00sec


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___