All your real equipment are in the simulation. There are warnings on building, etc.
The following is the water tank portion of the boiler. Boiler:HotWater, Central Boiler, !- Name NaturalGas, !- Fuel Type autosize, !- Nominal Capacity {W} 0.8, !- Nominal Thermal Efficiency LeavingBoiler, !- Efficiency Curve Temperature Evaluation Variable , !- Normalized Boiler Efficiency Curve Name 81., !- Design Water Outlet Temperature {C} (This is the build in thermostat) autosize, !- Design Water Flow Rate {m3/s} 0.0, !- Minimum Part Load Ratio 1.2, !- Maximum Part Load Ratio (Did you put this in?) 1.0, !- Optimum Part Load Ratio Central Boiler inlet Node, !- Boiler Water Inlet Node Name Central Boiler Outlet Node, !- Boiler Water Outlet Node Name 100., !- Water Outlet Upper Temperature Limit {C} Safety temperature ConstantFlow; !- Boiler Flow Mode Because you define it as a natural gas boiler, the heat required will calculated in terms of the cost of gas supply in the report.
Only one boiler is defined. This the furnace part of the real system which has the water jacket to heat the HW. ===================
=================== PlantEquipmentOperationSchemes,Hot Loop Operation, !- Name PlantEquipmentOperation:HeatingLoad, !- Control Scheme 1 Object Type Central Boiler Only, !- Control Scheme 1 Name PlantOnSched; !- Control Scheme 1 Schedule Name
This is where shut the boiler off in Summer, if you want. =======================
ã?? !- =========== ALL OBJECTS IN CLASS: AVAILABILITYMANAGER:HIGHTEMPERATURETURNOFF =========== AvailabilityManager:HighTemperatureTurnOff, schedual boiler, !- Name Central Boiler Outlet Node, !- Sensor Node Name 82; !- Temperature {C} ã?? !- =========== ALL OBJECTS IN CLASS: AVAILABILITYMANAGER:LOWTEMPERATURETURNON =========== AvailabilityManager:LowTemperatureTurnOn, schedule boiler 2, !- Name Central Boiler Outlet Node, !- Sensor Node Name 80; !- Temperature {C} !- ============================= SetpointManager:Scheduled,Hot Water Loop Setpoint Manager, !- Name Temperature, !- Control Variable HW Loop Temp Schedule, !- Schedule Name HW Supply Outlet Node; !- Setpoint Node or NodeList Name
You added these two objects in because you wanted to control the furnace to turn on and off at these temperatures. I told you that I am not check all the node names.
Normally, the set point manager alone is sufficient.
==================== The 65°C pipe is on another loop the DHW loop.
You cannot use the low temperature radiant panel model to simulate your system.
You do not have a air loop system. The coil is in the DHW tank. You may have an heater in the DHW tank which is not shown in your schematic.
The thermometer on the furnace is for temperature indication. A safety valve will be a whistle when the furnace temperature reaches the boiling point. The model of radiator in EPlus is the one you have. I am a retired EE Proffessor, yes. (Universities in Kuala Lumpur, Malaysia 1969, Toronto, and Polytechnics in Singapore 1996.) I stopped over in Tehran in 1953. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: t.t111ir@xxxxxxxxx Date: Sat, 18 Feb 2012 18:56:01 +0000 Subject: Re: [EnergyPlus_Support] water heater
From: Tooran T <t.t111ir@xxxxxxxxx> To: "EnergyPlus_Support@xxxxxxxxxxxxxxx" <EnergyPlus_Support@xxxxxxxxxxxxxxx> Sent: Saturday, February 18, 2012 10:23 PM Subject: Re: [EnergyPlus_Support] water heater Dear Dr.Li , i think i cant say my problem in english :(
Dr.Li ,
i have building that there is tank that there is gas natural heater and heat water and then this water circulate to both radiator and coil , in the coil this hot water exchange heat to domostic water and make hot domostic water ,
i think at first i do wrong i use boiler in HW loop and water heater in DHW , but in my building there is only water heater and coil ,
when i read document of energy plus i think i must use water heater that heat water for both radiator and coil and zone:hvac:low temperature radiant constant flow (for simulating radiator ) i hope i can say my problem correctly in english
by the way Dr.Li do you teach at university?
nice too meet you Dr.Li
From: YuanLu Li <yli006@xxxxxxxxxxx> To: EnergyPlus_Support <energyplus_support@xxxxxxxxxxxxxxx> Sent: Saturday, February 18, 2012 9:56 PM Subject: RE: [EnergyPlus_Support] water heater See reply in Blue background. Dr. Li
To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: t.t111ir@xxxxxxxxx Date: Sat, 18 Feb 2012 14:39:08 +0000 Subject: Re: [EnergyPlus_Support] water heater
From: YuanLu Li <yli006@xxxxxxxxxxx> To: EnergyPlus_Support <energyplus_support@xxxxxxxxxxxxxxx> Sent: Saturday, February 18, 2012 4:47 PM Subject: RE: [EnergyPlus_Support] water heater For T.t: If you are referring to the same project. The answer is yes and no.
Dear Dr.Li
the building that i have modeled there is boiler that has tank ,how can i simulate it? i think the boiler onject in energyplus there is no tank ,
if it is right how i can simulate this?
HW loop is a class in the program. water heater is an object in a class. The radiators are branch objects connected to the HW loop and not to a water heater, but may be a water heater tank. what you mean by may be a water heater tank? As I said before, you have to use the name and meaning of EPlus. Radiator is a the same as a water coil, but it radiates heat in a Zone directly. It is branch of the water loop and is therefore part of the loop as a water heater tank.
Heater is the fire, the heating source, the heating element.
There are many water heater types, electric, gas, oil, etc. It is a boiler in the HW Plant Loop. Water heater tank is a storage tank, (and need not have any volume, instantaneous tank.) you mean when tank voulme is zero then it is tankless ( instantaneous tank) and if its tank volume is not zero then it is storage tank? I am sure you have seen a small electric water heater which can be connected in line with a shower. The element is immersed in water, but the water volume is so small, the water flowing through the pipe is heated up instantaneously. As soon as the water stops, the element is switched off. You can also set a maximum temperatur.To simulate this, you use a tank with very small volume.
ALL OBJECTS IN CLASS: WATERHEATER:MIXED ===========
WaterHeater:Mixed,
Indirect Water Heater, !- Name AUTOSIZE, !- Tank Volume {m3} Leave it as autosized, as you do not know the size of the tank nor the furnace. After the simulation, you can find the size used from the .EIO file.
if i put zero in tank volume , then water heater will be with out tank storage, yes? May be zero is too small, as it must wrap around the electric heater.
That is why I suggested that you need to learn the names from the EPlus manual and not from the Wiki link.
The DHW tank can be part of the same HW loop, to get the heat source from one boiler, but the water is not in the same HW loop, because the hot water loop for radiator does not want to be connected to the water main water. HW is a closed loop. The water is circulated to the coils, radiators, and heating coils. In DHW (domestic HW) the inlet to the tank is the water main cold water the outlet is to the tap and used and then to the drain (sewer). The EPlus objects are different for the shows, etc. Dr. Li
To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: t.t111ir@xxxxxxxxx Date: Sat, 18 Feb 2012 10:30:00 +0000 Subject: [EnergyPlus_Support] water heater can i use water heater to inculde hot water for radiator ?
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.