[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: Σχετ: [EnergyPlus_Support] Validation -> Zone Mean Air Temperature





Simos,

First of all, thank you for the quick response. The truth is that each office equipment list consists of 2 elements with the following sequence
  1. ZoneHVAC:Baseboard:RadiantConvective:Water
  2. ZoneHVAC:PackagedTerminalHeatPump

Hence, the storage effect should be observed since the major system is a radiation system. Am I right? Maybe I should have a more detailed analysis on how the fractions of radiant energy goes to each surface are calculated.

Best Regards,

Giorgos



2012/2/20 Simeon Oxizidis <simeonagas@xxxxxxxx>
 

Hi George,

what type of heating system do you have?

If you have an air system obviously it cannot charge the thermal mass of the building since as soon as the room air temperature reaches the setpoint the system turns off (there is not time to add heat by convection to the buildings elements).

The storage effect can be experienced with a radiation system since in that case first the building elements are being charged (by radiation) and then by convection the room air warms up (which triggers the thermostat operation).

I hope that helps.


Simos


Áðï: Georgios Giannakis <giannakis.georgios@xxxxxxxxx>
Ðñïò: EnergyPlus_Support@xxxxxxxxxxxxxxx
ÓôÜëèçêå: 4:35 ì.ì. ÄåõôÝñá, 20 Öåâñïõáñßïõ 2012
Èåìá: [EnergyPlus_Support] Validation -> Zone Mean Air Temperature

 
Dear forum

In the framework of a fp7 project, we have to validate the simulation model of a building located at Greece-Chania, to check whether the model leads to the same results as specified in terms of provided measurement data. What seems absurd is that once the heating system turns off a sharp 2 C zone air temperature decrease is occured, which in my opinion means that building does not store heat energy, although the inner layer of the buildings envelop consists of materials with high density. We tried to define an extraterrestrial furniture thermal mass (~35 m^2 - it is not exist in the real building) for each office room and it seems that the simulated temperature curve converges to the measured temperature curve. Any answer would really help.

Thanks in advance,
Giannakis G.





__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___