[EnergyPlus_Support] Re: Warning Message shown as Zone XXX is not accounted for by controller:mechnicalv"
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] Re: Warning Message shown as Zone XXX is not accounted for by controller:mechnicalv"
- From: "Ke Xu" <xukevin24@xxxxxxxxx>
- Date: Fri, 24 Feb 2012 03:06:33 -0000
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Thu, 23 Feb 2012 20:06:38 -0700
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=lima; t=1330052797; bh=qqKEjiL2FR98dytw/EcXRzhV9Sht8tNQb4sa3NgQf5Y=; h=Received:Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:In-Reply-To:User-Agent:X-Mailer:X-Originating-IP:X-eGroups-Msg-Info:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=m+zDmqAUZRmBJTGAJKAOJgwIjyqzB1LSQ5q4fryFBZwTrYTgg/M2ZYmlgNdbs1WDFJ3ZFMU0eqykXWLaktljvMhsxm2tuIzKAXyIVzm3HVXftwSrC/Hw5WnF13RhB8Ix
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=lima; d=yahoogroups.com; b=VcwfxHUVF1cHRkbFLtib0fGLehmK12ch4xWStI5iB+J+cSrrt5Tb2vDkmsqNtTg2QEJwtu9dBp7YFb0zeddBCf/yEOFXS0GtDorfwNn8pHyrPHKZL6myBxpKIdsY9C6W;
- Envelope-to: linda@xxxxxxxxxxxxxx
- In-reply-to: <ji6tt4+dgqk@eGroups.com>
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
I used Notepad++ to revise idf file.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "L Lawrie" <linda@...> wrote:
>
> Send the file to the helpdesk and we'll try to help.
>
> You didn't make the change in IDF Editor, right? You used Notepad or something?
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Ke Xu" <xukevin24@> wrote:
> >
> > Linda, I did the changes as you suggested, but the same warning message still pops out~~~~~~~
> >
> > Other solutions? Ideas?
> >
> > Thanks.
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Linda Lawrie <linda@> wrote:
> > >
> > > This is most likely a problem we need to address in the code. However,
> > > I think you can get around it by (and you'll have to do this by hand,
> > > not in idf editor):
> > >
> > > Perim_bot_ZN_7, !- Zone 9 Name
> > > CM DSOA Perim_bot_ZN_7, !- Design Specification Outdoor Air Object
> > > Name 9
> > > 1, !- Zone Air Distribution Effectiveness in
> > > Cooling Mode 9 {dimensionless}
> > > 1, !- Zone Air Distribution Effectiveness in
> > > Heating Mode 9 {dimensionless}
> > > ; !- Zone Air Distribution Effectiveness
> > > Schedule Name 9
> > >
> > > In other words, add the field for the schedule name at the end of each
> > > of those objects even though it is blank.
> > >
> > > IDF Editor will truncate it so you can't use IDF Editor.
> > >
> >
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/