RE: [EnergyPlus_Support] Time heating setpoint not met






Setting the zone thermostat value to a different  value to observe the result is a very powerful degugging tool. 


 
"if i set heating setpoint =25C then i see in the winter design day the zone mean air temperaure is nearly 24-25C . "
 
In this case, the highest temperaute is the same as the set point.  The system is controlling the temperature.  For the 24°C period, the system is under capacity.  If the sizing was doen with people, lighting , and equipment, removing these would need more heating.


"if i set heating setpoint =30C then i see in the winter design day the zone mean air temperaure is nearly 24-25C".
 
 
In this case, the system under capacity, and the thermosat is not controlling the temperature. 
 
If the desired Winter temperature is 15-20°C, the system capacity can be reduced some more.


The above two cases assume that the heating setpoint is for the zone thermostat.



However, if the value is for the HW heater outlet feeding the radiator, the 25°C set point will have lower zone emperatures as given below,  nearly 20-21-19°C. 

 

This is because the exit temperature of a radiator is always below the inlet temperature of 25°C.  When the water is not following, a radiator  will transfer heat slowly to or from the zone by conduction and convection, until the temperature is the same.


When you run the sizing simulation, the flowrate for the radiator  is adjusted to the worse case of that day or period for that zone only.  In your case, the solar radiation is also turned off.   Therefore, the flow rate obtained is only good for that outdoor and indoor condition


The zone temperature is expected not to me the setpoint temperature of the zone, for all hours of a day.

 

 Dr. Li  

 
 
 
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: t.t111ir@xxxxxxxxx
Date: Sat, 3 Mar 2012 12:00:38 +0000
Subject: Re: [EnergyPlus_Support] Time heating setpoint not met

 
i wrote wrong in the   yellow highlighted line ,  the red line in correct
 

From: Tooran <t.t111ir@xxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Saturday, March 3, 2012 3:26 PM
Subject: [EnergyPlus_Support] Time heating setpoint not met

 
dear members ,

i want to design the hot water plant loop and i wnat to know what size pump and boiler must have to that their capacity is engough for keeping the zone mean air temperature = 25 C ( i set heating setpoint =25C) for winter design day , but when i run it i see in the winter design day i have time heating setpoint not met and the zone mean air temperature is nearly 20-21-19 C.
if i set heating setpoint =25C then i see in the winter design day the zone mean air temperaure is nearly 24-25C .
if i set heating setpoint =30C then i see in the winter design day the zone mean air temperaure is nearly 24-25C .
could you help me and describe it why this happens?
thanks









ExternalClassecxygrp-mkpd8d8d8;font-family:Arial;padding:010pxExternalClassecxygrp-mkpExternalClassecxygrp-mkpExternalClassecxygrp-mkpecxads10pxExternalClassecxygrp-mkpExternalClassecxygrp-mkpExternalClassecxygrp-mkpExternalClassExternalClassExternalClass10pxExternalClassExternalClass10pxExternalClass10px10pxExternalClassExternalClassExternalClassff7900ExternalClassExternalClass10pxExternalClassExternalClassExternalClassExternalClassExternalClassExternalClassExternalClassExternalClassExternalClass10pxExternalClassExternalClassExternalClassExternalClassExternalClassExternalClassExternalClassExternalClassExternalClassExternalClassExternalClassExternalClassecxygrp-msg10pxExternalClassExternalClassExternalClassExternalClassExternalClassExternalClass10pxExternalClassExternalClassExternalClassExternalClassExternalClassExternalClassExternalClassExternalClassfont:99ExternalClassExternalClassExternalClassExternalClass10pxExternalClassExternalClassecxygrp-msgExternalClassecxygrp-msgExternalClassff7900ExternalClassExternalClassExternalClassExternalClassExternalClassExternalClassExternalClass


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___