|
It appears that the Energy+ DX model does not include simulation of what is commonly called a low ambient control for a DX cooling system. Basically the low
ambient control monitors the system operation and turns off the condenser fan if the outdoor air conditions push the system too far. The DX system continues to operate with the condenser fan either off or cycling on and off. This could be programmed with
the EMS as a capacity reduction for the condenser coil, but I am not sure how to do this or if it can be done with the current DX cooling model. Ned Lyon, P.E. (MA) SIMPSON GUMPERTZ & HEGER
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
On Behalf Of CleanTech Analytics Once again thank you Jim this EMS routine is very interesting.. Richard, thank you kindly. Your explanations where very clear and useful.. A part of the problem was that I had used an HVAC system sized for one climate, and had moved it from one location to another, so the system was incorrectly sized...
Jeremiah D. Crossett CleanTech Analytics 503-688-8951 This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential.
It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics
On Tue, Mar 20, 2012 at 6:14 AM, Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx> wrote: Dear Jeremiah, Your DX coil is trying to operate in cool weather. When it does, it applies its full capacity to the airstream and cools it down to
freezing temperature. This is the same error that Joe Huang posted about the other day (I think). You’ll need to : 1.
Ignore it (after confirming that it’s not indicating some other problem) 2.
Turn off the coil during cold weather (after looking at the weather file to see when weather is below about 55-60F) 3.
Run an EMS script to turn off the coil whenever outdoor temp is lower than a set value p.s., Certain “baseline” systems (e.g., a heat pump serving an interior zone) don’t handle the situation well where an economizer is
not used such as is the case in a warm climate zone. They need cooling in the
cold weather, but the DX system doesn’t like operation then. (This is not a likely “real” system, since engineers know these things. But a “baseline” is not real…) Here’s an EMS routine (grateful credit for which goes to Jean Marais and somebody at the Help desk a few months back): DX coils that you want OFF via this routine must have their Unitary object specified with the same schedule which the EMS routine is
turning on and off (“SchCpct_LowTempOFF” in this example)
The Building Performance Team From:
EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
On Behalf Of CleanTech Analytics
Dear List, Any advise on how to approach this error? Thanks ************* ===== Recurring Error Summary ===== ************* The following recurring error messages occurred. ************* ************* ** Warning ** Coil:Cooling:DX:SingleSpeed "BLOCK1:ZONE1 AHU COOLING COIL" - Full load outlet temperature indicates a possibility of
frost/freeze error continues. Outlet air temperature statistics follow: ************* ** ~~~ ** This error occurred 3849 total times; ************* ** ~~~ ** during Warmup 0 times; ************* ** ~~~ ** during Sizing 0 times. ************* ** ~~~ ** Max=1.999729 Min=0.701477 *************
Jeremiah D. Crossett CleanTech Analytics This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential.
It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |