Here is the issue.

I want my unit ventilator (Group Name: Zone HVAC Forced Air Units, Object Name: ZoneHVAC:UnitVentilator) and radiant cooling to work simultaneously, in this case I want unit ventilator to act as DOAS taking care of entire latent load of zone and partially sensible load. Thus,  you can see in the .eio file that 100% OA air is conditioned through cooling coil installed in unit ventilator. I have the following queries:

1. Autosizing my Zone1Unt Vent Outlet air temp. gives 13°C, however, the output variable sheet shows indoor air temp. as high close to 28°C (thermostat has been set to 24°C).
2. Sizing Zone Cooling Design SAT has been mentioned as 13°C, when I reduce it to 11 or 12 °C, zone air temp. increases from 28° to 33°C (on a particular day in June).
3. Sizing Plant Design Loop exit temp. is mentioned as 10°C and in CHW Loop temp schedule I have mentioned 15°C. So, on which temp. my loop is running. Is it that because of this my indoor room air temp. is not coming close to setpoint. When I increase this loop exit temp. from 10°C to 15°C again the same thing happens zone air temp. increases from 28° to 33°C (on a particular day in June).

Can anyone suggest the mistakes which I am making. Why the room air temperature is not getting close to the setpoint?

regards,
SACHIN SHARMA



--- On Sat, 3/24/12, Jean marais <jeannieboef@xxxxxxxxx> wrote:

From: Jean marais <jeannieboef@xxxxxxxxx>
Subject: [EnergyPlus_Support] Re: How does unit ventilator work
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Date: Saturday, March 24, 2012, 1:12 AM

 

Please post the section of the idf code where you specified the object. in the mean time output the variables for the water and air nodes that connect up to the unit ventilator. Check your rdd file for the correct syntax. you will have an rdd file if you have specified it (make sure to specify it with the idf option) as an output already. If you have not, check the ioRef for the line of code to be included.



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___
Attachment not found:
d:\eudora\attach\test chamber practical model DV + RC1.svg
Attachment not found:
d:\eudora\attach\test chamber practical model DV + RC.eio