[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Design Days
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] Design Days
- From: "hnoboam" <homero.noboa@xxxxxxxxx>
- Date: Tue, 27 Mar 2012 18:23:46 -0000
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Tue, 27 Mar 2012 12:23:50 -0600
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=lima; t=1332872628; bh=UA9wdHnnPDd7owYG2A6tzrd+ivTCxWzygwzatmdiGas=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:User-Agent:X-Mailer:X-Originating-IP:X-eGroups-Msg-Info:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=em3GqUp0WO5SNF/lW1lgG0edyA4F1M1PKA0PdnTMyRn1aegFuXpcVszlLIBrkz4tonoSfhGyILfQan9tXrWvzLNM4kASanBpRXMSMMpba6swTNpmBxKj5Imm+uoVL9BC
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=lima; d=yahoogroups.com; b=FU1oX0FjiDuypjbQqbH+LdUSL81Kfw9OD7BRzhZkhWD76HuELFJ49INT9Wjytz25vsUsRyDNAq3NYkxzsDZO5vRdNofoL/lXTLbq5+9Ib1w4HPx8CAFw63YzdqassUH5;
- Envelope-to: linda@xxxxxxxxxxxxxx
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
Dear List.
In many many example idfs I have seen only two design days used, one for summer, one for winter. However, in the weather file package for any site, for example for Beijing, the ddy file contains many design day definitions.
My questions are:
1. All the choices of design days are for me to choose one that I like?
2. What happens if I include more than one winter design day and/or more than one summer design day? I just did this and E+ ran, not sure what it did with the different autosized values.
Thanks
Homero
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/