Re: [EnergyPlus_Support] Slab program crashes





evapotranspiration does not seem to work well at the dryer climates.  not sure why -- we don't have a lot of resources to look into it.

Ignore the \obsolete message for now.  That is a legal flag, not sure why idf editor is complaining.

At 11:34 AM 4/10/2012, Homero Noboa wrote:


Thanks Linda. Turning off this flag allowed the program to run. I assume we (users) cannot do anything to allow the evapotraspiration model to work.

Also, is the "\obsolete=>EquivalentSlab" a bogus message? Anything we should be concerned about?

Thanks again.

Homero.

On Tue, Apr 10, 2012 at 12:17 PM, Linda Lawrie <linda@xxxxxxxxxxxxxx> wrote:
 

Try setting evapo transpiration to False.


At 11:04 AM 4/10/2012, hnoboam wrote:
I am trying to use the Slab program to generate meaningful ground temperature values. I am using the sample IDF file shown in the "AuxililaryPrograms" document (with few modifications to suit my needs) and I run into two problems.
First, when I try to open the IDF in the EP Launch, it shows an "Invalid Slash Codes Found" window. The message says:
\obsolete=>EquivalentSlab
\obsolete=>EquivalentSlab

It also crashes when I run using the Phoenix,AZ epw file
My IDF is this:

Materials,
    2, !- NMAT: Number of materials
    0.158, !- ALBEDO: Surface Albedo: No Snow
    0.379, !- ALBEDO: Surface Albedo: Snow
    0.9, !- EPSLW: Surface Emissivity: No Snow
    0.9, !- EPSLW: Surface Emissivity: Snow
    0.75, !- Z0: Surface Roughness: No Snow
    0.03, !- Z0: Surface Roughness: Snow
    6.13, !- HIN: Indoor HConv: Downward Flow {W/m2-K}
    9.26; !- HIN: Indoor HConv: Upward {W/m2-K}

!- =========== ALL OBJECTS IN CLASS: MATLPROPS ===========

MatlProps,
    2300, !- RHO: Slab Material density {kg/m3}
    1200, !- RHO: Soil Density {kg/m3}
    653, !- CP: Slab CP {J/kg-K}
    1200, !- CP: Soil CP {J/kg-K}
    0.93, !- TCON: Slab k {W/m-K}
    1; !- TCON: Soil k {W/m-K}

!- =========== ALL OBJECTS IN CLASS: BOUNDCONDS ===========
BoundConds,
    TRUE, !- EVTR: Is surface evapotranspiration modeled
    FALSE; !- FIXBC: is the lower boundary at a fixed temperature
!HN removed to use Fasle FIXBC    FALSE; !- OLDTG: is there an old ground temperature file

!- =========== ALL OBJECTS IN CLASS: BLDGPROPS ===========
BldgProps,
    10, !- IYRS: Number of years to iterate
    0,  !- Shape: Slab shape
    4, !- HBLDG: Building height {m}
!hn The indoor temp setpoints adjusted for the results to match (+-) the Chicago Site:GroundTemperature:BuildingSurface
    21, !- TIN1: January Indoor Average temperature set point {C}
    21, !- TIN2: February Indoor Average temperature set point {C}
    21, !- TIN3: March Indoor Average temperature set point {C}
    21, !- TIN4: April Indoor Average temperature set point {C}
    22, !- TIN5: May Indoor Average temperature set point {C}
    23, !- TIN6: June Indoor Average temperature set point {C}
    24, !- TIN7: July Indoor Average temperature set point {C}
    24, !- TIN8: August Indoor Average temperature set point {C}
    22, !- TIN9: September Indoor Average temperature set point {C}
    22, !- TIN10: October Indoor Average temperature set point {C}
    21, !- TIN11: NovemberIndoor Average temperature set point {C}
    21, !- TIN12: December Indoor Average temperature set point {C}
    0, !- TINAmp: Daily sine wave variation amplitude {C}
    0.10; !- ConvTol: Convergence Tolerance

!- =========== ALL OBJECTS IN CLASS: INSULATION ===========
Insulation,
    0., !- RINS: R value of under slab insulation {m2-K/W}
    0., !- DINS: Width of strip of under slab insulation {m}
    2.0, !- RVINS: R value of vertical insulation {m2-K/W}
    0.2, !- ZVINS: Depth of vertical insulation {m} hn changed. 2 meters is too much.
    1; !- IVINS: Flag: Is there vertical insulation

!- =========== ALL OBJECTS IN CLASS: EQUIVSLAB ===========
EquivalentSlab,
    10, !- APRatio: The area to perimeter ratio for this slab {m}
    0.13, !- SLABDEPTH: Thickness of slab on grade {m} hn changed to fix error
    15, !- CLEARANCE: Distance from edge of slab to domain edge {m}
    10; !-ZCLEARANCE: Distance from bottom of slab to domain bottom

Any suggestion?

Thanks.

Homero.




------------------------------------


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/




--
Homero Noboa, Ph. D.





__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___