[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: Simple Glazing, Complex Glazing and frames
Correction: FullExterior assigns all incomming radiation to the floor. And that which is relected from the floor is equally divided on zone surfaces per area. As I have a roof zone with a IRTsurface floor, it should not reflect any energy, but pass all radiation energy to the main zone below, all be it not direct beam radiation.
Strangely, the out of bounds negative temps also occur between adjacent roof zones.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Jean marais" <jeannieboef@...> wrote:
>
> Dear Group,
> 1) in the simple glazing material specification there is no parameter for the density of the glass. is this a "no mass" material, i.e. the surface temperature of the glass is assumed to be that of the air in contact with that surface?
>
> 2) is this the same for complex glazing?
>
> 3) is this the same for frames/dividers?
>
> Background: I'm modelling a large factory hall with an almost fully glazed roof. It is a very light weight structure where the only heavy contruction is the slab. During a summer type run period over a day, I get fatal errors because IRTsurfaces that I am using to virtually partition the hall, are reporting negative 120 deg C temperatures at 09:00.
>
> Due to the concave nature of some of the factory roof, I am limited to using the FullExterior solar distribution model which divides equally the incoming radiation on all surfaces in that zone. Instead of the majority of radiation hitting the slab, the sum is equally split and too much of it is assigned to my no mass type IRTsurface partitions. I have to use the CTF heat transfer algorithm with this type of material. I suspect that the algorithm is trying to see what delta T is required to transfer a large amount of energy over to the other side and comes up with -120 deg C in some cases. Although the CTF object has a temp upper limit, there is no lower limit for me to relax and hence the program errors out.
>
> I can get it to run by using internal mass objects, because when I increase the total surfaces in the zone less energy gets put on the no mass IRTsurfaces.
>
> Any other thoughts are appreciated. I wish users did not have to worry about this kind of issue (too much or too little internal mass, or too thick walls either)
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/