[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Node Connection Error





Your plant will connect according to these objects. Notice that the Cooling Supply Outlet Branch is not listed in the mixer or splitter. I agree with the last comment, the pump should be on the inlet to the supply side of the plant. Look at some example files.

PlantLoop,
    Chilled Water Loop,      !- Name

    Return Pipe Inlet Node,  !- Plant Side Inlet Node Name
    ChW Supply Outlet Node,  !- Plant Side Outlet Node Name
    Cooling Supply Side Branches,  !- Plant Side Branch List Name
    Cooling Supply Side Connectors,  !- Plant Side Connector List Name

BranchList,
    Cooling Supply Side Branches,  !- Name
    Return Pipe Branch,      !- Branch 1 Name
    CU-1 Chilled Water Branch,  !- Branch 2 Name
    CU-2 Chilled Water Branch,  !- Branch 3 Name
    CU-3 Chilled Water Branch,  !- Branch 4 Name
    CU-4 Chilled Water Branch,  !- Branch 5 Name
    Cooling Supply Pump Branch,  !- Branch 6 Name
    Cooling Supply Outlet Branch;  !- Branch 7 Name

ConnectorList,
    Cooling Supply Side Connectors,  !- Name
    Connector:Splitter,      !- Connector 1 Object Type
    Cooling Supply Splitter, !- Connector 1 Name
    Connector:Mixer,         !- Connector 2 Object Type
    Cooling Supply Mixer;    !- Connector 2 Name

Connector:Splitter,
    Cooling Supply Splitter ,!- Name
    Return Pipe Branch,      !- Inlet Branch Name
    CU-1 Chilled Water Branch,  !- Outlet Branch 1 Name
    CU-2 Chilled Water Branch,  !- Outlet Branch 2 Name
    CU-3 Chilled Water Branch,  !- Outlet Branch 3 Name
    CU-4 Chilled Water Branch;  !- Outlet Branch 4 Name

Connector:Mixer,
    Cooling Supply Mixer,    !- Name
    Cooling Supply Pump Branch,  !- Outlet Branch Name
    CU-1 Chilled Water Branch,  !- Inlet Branch 1 Name
    CU-2 Chilled Water Branch,  !- Inlet Branch 2 Name
    CU-3 Chilled Water Branch,  !- Inlet Branch 3 Name
    CU-4 Chilled Water Branch;  !- Inlet Branch 4 Name





On 4/30/2012 11:08 AM, em@xxxxxxxxxxxxxxxxxxxx wrote:

I can't seem to understand why I am still getting a node connection error for a connected inlet and outlet node. I am working on a custom HVAC design. The CHW Supply inlet and outlet node is an adiabatic pipe. attached is the idf and err file. I couldn't find a solution searching the web. Thanks in advance. 

Laurent 

** Severe  ** Node Connection Error, Node="CHW SUPPLY INLET NODE", Inlet node did not find an appropriate matching "outlet" node.

**   ~~~   ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
**   ~~~   ** Reference Object=BRANCH, Name=COOLING SUPPLY OUTLET BRANCH
** Severe  ** Node Connection Error, Node="CHW SUPPLY INLET NODE", Inlet node did not find an appropriate matching "outlet" node.
**   ~~~   ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
**   ~~~   ** Reference Object=PIPE:ADIABATIC, Name=COOLING SUPPLY OUTLET

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___