[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

RE: [EnergyPlus_Support] G3.1.2.8 Design Airflow Rate - supply-air-to-room-air temperature difference





I re-read your question…

Yes.

Room temp – System cooling design supply air temperature = 11

Maximum (System Heating design supply air temperature, Zone Heating design supply air temperature)  - Room temp = 11

The Building Performance Team
James V. Dirkes II, P.E., BEMP , LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Leticia Neves
Sent: Wednesday, May 02, 2012 4:44 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] G3.1.2.8 Design Airflow Rate - supply-air-to-room-air temperature difference

 

 

Hi,

 

I would like to clarify the following doubt:

- the 11°C of supply-air-to-room-air temperature difference specified by Appendix G of ASHRAE 90.1 must be between the room air and sizing:zone or sizing:system?

 

Thanks,

Leticia



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___