Gerard,

Be sure to change the  solar distribution in the 'Building' object to FullExteriorWithReflections or FullInteriorandExteriorWithReflections

You should be able to set the shadings reflectance in the 'material' object that you have used to define the shade.

Material,
    F08 Metal surface,       !- Name
    Smooth,                !- Roughness
    0.0008,                  !- Thickness {m}
    45.28,                    !- Conductivity {W/m-K}
    7824,                     !- Density {kg/m3}
    500,                        !- Specific Heat {J/kg-K}
    0.90,                       ! Thermal Absorptance
    0.3,                         ! Solar Absorptance
    0.3;                         ! Visible Absorptance

Where reflectance = 1 -  absorptance

The ShadingProperty:Refectance can also be used to redefine the properties for the material, but you still need to have the 'WithReflections' solar distribution option.  Possibly you mistyped 'ShadingProperty:Reflectance' as 'SurfaceProperty:Reflectance' but that should have resulted in a fatal error.

Hope this helps,

Jason






__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___