[EnergyPlus_Support] Slab pre-processor warning





Dear all,

I tried to invoke the slab pre-processor within the .IDF file. I went over the auxiliary programs document and also over the 52ZoneAirCooledWithSlab.idf from the example file. However, when I try to run test.idf (attached to this email), I keep getting these warnings.

Program Version,EnergyPlus-64 7.0.0.036, 09/05/2012 10:40 AM,IDD_Version 7.0.0.036
   ** Warning ** Output:PreprocessorMessage="GroundTempCalc - Slab" has the following Warning condition:
   **   ~~~   ** Slab thickness [0.122 m] reset to 0.122 m  for computational stability.
   ** Severe  ** Output:PreprocessorMessage="GroundTempCalc - Slab" has the following Severe condition:
   **   ~~~   ** The calculated ground temperature exceeds -100 C [-204.07 C]
   ** Severe  ** Output:PreprocessorMessage="GroundTempCalc - Slab" has the following Fatal condition:
   **   ~~~   ** Program terminates due to preceding condition.
   **  Fatal  ** Preprocessor condition(s) cause termination.
   ...Summary of Errors that led to program termination:
   ..... Reference severe error count=2
   ..... Last severe error=Output:PreprocessorMessage="GroundTempCalc - Slab" has the following Fatal condition:
   ************* Warning:  Node connection errors not checked - most system input has not been read (see previous warning).
   ************* Fatal error -- final processing.  Program exited before simulations began.  See previous error messages.
   ************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
   ************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors.
   ************* EnergyPlus Terminated--Fatal Error Detected. 1 Warning; 2 Severe Errors; Elapsed Time=00hr 00min  0.67sec

This happens with weatherfiles from Atlanta, Greenville, Chicago, WashingtonDulles etc. I am not quite sure what I am doing wrong. Could someone, with experience using the slab program (within the .IDF) point me in the right direction.

I look forward to hearing from you at your earliest of convenience.
Sincerely yours'
Niraj Poudel
Clemson University





__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___
Attachment not found:
d:\eudora\attach\Test8.idf