EP Macro is described in the Auxiliary Programs document.

If you are using EP-Launch, there is a "inc" that can be set and tested in each subsequent simulation. (I believe there is a simple example shown in the files area here).

The output files from EP-Macro are put as "epmidf" and "epmdet" extensions -- usually in the output files area. It looks like there was a previous set of messages about this -- I will catch up to them tomorrow.

Linda

On 13.05.2012 16:46, CleanTech Analytics wrote:
Jean, 
Thank you kindly for the advise;

I have done as you advised, but I can not seem to find the output
tables or csv files from the macro simulation. 
I have attached my files, could you please help me out and point me in
the right direction to use the EP Macro funtonality? My use is to be
able to add PCM's to Energy Plus files in JE+ runs. I have it working
by using 8 IDF's, but would much rather use the IMF/EP Macro
method.. 

Questions: Should I use single file, or group with all IMF's? Should I
click repeat simulation for IMF in the number (8) of IMF files? 

Many thanks 

! File generated by DesignBuilder - 3.0.0.104 3/18/2012 - 9:46:52 PM
! Source file: C:UsersJeremiahDocumentsDesignBuilder DataASHRAE Room
Study.dsb
Version,
    7.1;                     !- Version Identifier

##include C:UsersJeremiahDesktopBioPCM IMF'sM27.IMF

!##include C:UsersJeremiahDesktopBioPCM IMF'sM51.IMF

!##include C:UsersJeremiahDesktopBioPCM IMF'sM91.IMF

!##include C:UsersJeremiahDesktopBioPCM IMF'sM182.IMF

!##include C:UsersJeremiahDesktopBioPCM IMF'sQ21.IMF

!##include C:UsersJeremiahDesktopBioPCM IMF'sQ23.IMF

!##include C:UsersJeremiahDesktopBioPCM IMF'sQ25.IMF

!##include C:UsersJeremiahDesktopBioPCM IMF'sQ27.IMF

!-   ===========  ALL OBJECTS IN CLASS: SIMULATIONCONTROL
===========

Program Version,EnergyPlus-32-MP 7.1.0.009+, 5/13/2012 3:39
PM,IDD_Version 7.1.0.009+
   ************* IP: IDF Line~15 ##include
C:UsersJeremiahDesktopBioPCM IMF'sM27.IMF
   ** Severe  ** , or ; expected on this line
   ************* Beginning Zone Sizing Calculations
   ************* Testing Individual Branch Integrity
   ************* All Branches passed integrity testing
   ************* Testing Individual Supply Air Path Integrity
   ************* All Supply Air Paths passed integrity testing
   ************* Testing Individual Return Air Path Integrity
   ************* All Return Air Paths passed integrity testing
   ************* No node connection errors were found.
   ************* Beginning Simulation
   ************* Simulation Error Summary *************
   ************* EnergyPlus Warmup Error Summary. During Warmup: 0
Warning; 0 Severe Errors.
   ************* EnergyPlus Sizing Error Summary. During Sizing: 0
Warning; 0 Severe Errors.
   ************* EnergyPlus Completed Successfully-- 0 Warning; 1
Severe Errors; Elapsed Time=00hr 03min 36.24sec

_Jeremiah D. Crossett_
_CleanTech Analytics_
_503-688-8951_

_www.cleantechanalytics.com_ [1]

 This document may contain valuable information proprietary to
CleanTech Analytics which is private and confidential. It may not be
shared, copied, stored or transmitted in any form without the prior
written consent of CleanTech Analytics

On Sun, Mar 25, 2012 at 10:23 PM, Jean marais  wrote:

 

And to illistrate...here is a bit of code epmacro i used to create
the CO2 part of my idf for the different zones to which it must be
applied.
I ran this sepperately (still using eplaunch and just exchanged the
include file for the CO2 for this one. It expands into the CO2 idf
that I then later included...if that makes sense. Unfortunately it
expands with a character that has to be manually removed with find
and replace. I can't remember what the character was...possibly a
'#' or a space?

##DEF CO2_EMS_FOR_ZONES[mmZone]


!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!
!EMS for Damper Control by CO2 Level
!*****THIS FILE IS USED TO GENERATE A FILE THAT HAS "" THAT NEED TO
BE REMOVED******!


!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!
! CC = CurrentCO2Concentration
! CCSP = CurrentCO2SP
! CDP = CurrentDamperPos
! CO2SPUL = CO2_SP_Sensor UPPER LIMIT
! CO2SPLL = CO2_SP_Sensor LOWER LIMIT
! ODACO2SPUL = ODA CO2_SP_Sensor
! ZDCS = ZDC_Sensor
! ZDC = Zone_Damper_Changer
! MDF = MINDAMPERFRACTION
! CMM = CO2ModificationManager
! CMMPr = CO2ModificationManager Program
! CS = CO2_Sensor
! DaLL = Damper Lower Limit

EnergyManagementSystem:GlobalVariable,
#[mmZone // _CC] ,
#[mmZone // _CCSP ] ,
#[mmZone // _CDP ] ,
#[mmZone // _dDamper ] ,
#[mmZone // _dCO2 ] ,
#[mmZone // _MM ] ,
#[mmZone // _ODACO2SPULV ],
#[mmZone // _CO2SPULV ],
#[mmZone // _CO2SPLLV ],
#[mmZone // _DaLLV ]; !- Erl Variable 2 Name

EnergyManagementSystem:Sensor,
#[mmZone // _CS] , ! Sensor Name...reporting temperature
mmZone ,! Output:Variable or Output:Meter Index Key Name
Output:Variable,*,Outdoor Dry Bulb,hourly; !- Zone Average [C]
Zone Air Carbon Dioxide Concentration ; ! Output:Variable or
Output:Meter Name

EnergyManagementSystem:Sensor,
#[mmZone // _ODACO2SPUL] , ! Sensor Name...reporting temperature
Outdoor CO2 Schedule , ! Output:Variable or Output:Meter Index Key
Name Zone/Sys Thermostat Cooling Setpoint Output:Variable,*,Zone/Sys
Thermostat Cooling Setpoint,hourly; !- Zone Average [C]
Schedule Value ; ! Output:Variable or Output:Meter Name

!Setpoint Value
EnergyManagementSystem:Sensor,
#[mmZone // _CO2SPLL] , ! Sensor Name...reporting schedule
properties
CO2SPLL , ! Output:Variable or Output:Meter Index Key Name Zone/Sys
Thermostat Cooling Setpoint Output:Variable,*,Zone/Sys Thermostat
Cooling Setpoint,hourly; !- Zone Average [C]
Schedule Value ; ! Output:Variable or Output:Meter Name

!Setpoint Value
EnergyManagementSystem:Sensor,
#[mmZone // _CO2SPUL] , ! Sensor Name...reporting schedule
properties
CO2SPUL , ! Output:Variable or Output:Meter Index Key Name Zone/Sys
Thermostat Cooling Setpoint Output:Variable,*,Zone/Sys Thermostat
Cooling Setpoint,hourly; !- Zone Average [C]
Schedule Value ; ! Output:Variable or Output:Meter Name

EnergyManagementSystem:Sensor,
#[mmZone // _DaLL] , !- Name
DaLL , ! Output:Variable or Output:Meter Index Key Name...in this
case !-EnergyManagementSystem:Actuator Available,COOLING SP
SCH,Schedule:Compact,Schedule Value,[ ]
Schedule Value ;!Damper Lower Limit Schedule

EnergyManagementSystem:Sensor,
#[mmZone // _ZDCS] , !- Name
mmZone MDF , ! Output:Variable or Output:Meter Index Key Name...in
this case !-EnergyManagementSystem:Actuator Available,COOLING SP
SCH,Schedule:Compact,Schedule Value,[ ]
Schedule Value ;!VAV Terminal Damper Position ; ! Output:Variable
or Output:Meter Name

! , Component Unique Name, Component Type, Control Type, Units
!EnergyManagementSystem:Actuator
Available,MDF,Schedule:Compact,Schedule Value,[ ]
EnergyManagementSystem:Actuator,
#[mmZone // _ZDC] , !- Name
mmZone MDF , !- Actuated Component Unique Name...in this case
!-EnergyManagementSystem:Actuator Available,COOLING SP
SCH,Schedule:Compact,Schedule Value,[ ]
Schedule:Compact, !- Actuated Component Type
Schedule Value ; !- Actuated Component Control Type

!***Program Calling Proceedure***
EnergyManagementSystem:ProgramCallingManager,
#[mmZone // _CMM] , ! Name
AfterPredictorAfterHVACManagers,!BeginTimestepBeforePredictor , !
EnergyPlus Model Calling Point
#[mmZone // _CMMPr] ; ! Program 1 Name

!***Main Program***
!******************
EnergyManagementSystem:Program,
#[mmZone // _CMMPr] , ! Program 1 Name
SET #[mmZone // _ODACO2SPULV ] = #[mmZone // _ODACO2SPUL],
SET #[mmZone // _CO2SPULV ] = #[mmZone // _CO2SPUL],
SET #[mmZone // _CO2SPLLV ] = #[mmZone // _CO2SPLL],
SET #[mmZone // _DaLLV ] = #[mmZone // _DaLL] ,
SET #[mmZone // _CC] = #[mmZone // _CS] ,
SET #[mmZone // _CDP] = #[mmZone // _ZDCS] ,
SET #[mmZone // _dDamper ] = (1 - #[mmZone // _DaLLV ]), !max min
damper positions
SET #[mmZone // _dCO2 ] = #[mmZone // _CO2SPULV] - #[mmZone //
_CO2SPLLV] , !max min CO2 levels, i.e. SP and ODA CO2
SET #[mmZone // _MM ] = 1 - (#[mmZone // _dDamper ] / #[mmZone //
_dCO2 ] * #[mmZone // _CO2SPULV] ) ,

IF (#[mmZone // _CC] >= #[mmZone // _CO2SPLLV ] ) && (#[mmZone //
_CC] #[mmZone // _CO2SPULV ] ,
SET #[mmZone // _ZDC] = 1 ,
ENDIF;

!***End Main Program***
!**********************
##EndDEF
CO2_EMS_FOR_ZONES [U12]
CO2_EMS_FOR_ZONES [PE00WN]
CO2_EMS_FOR_ZONES [PE00WS]
CO2_EMS_FOR_ZONES [PE00WW]
CO2_EMS_FOR_ZONES [PE0Z02W]
CO2_EMS_FOR_ZONES [PE03W]
CO2_EMS_FOR_ZONES [HE00]
CO2_EMS_FOR_ZONES [HE0Z03]
CO2_EMS_FOR_ZONES [PavN]
CO2_EMS_FOR_ZONES [PavS]

!*******************************************DEFINE DAMPER SCHEDULES
FOR ZONES*****************************
##def DAMPER_SCH_ZONES[mmZone]

Schedule:Compact,
mmZone MDF,
Fraction,
Through: 12/31,
For: AllDays,
Until: 05:00, 0.3,!0,
Until: 23:00, 0.7,
Until: 24:00, 0.3;

##EndDef

DAMPER_SCH_ZONES [U12]
DAMPER_SCH_ZONES [PE00WN]
DAMPER_SCH_ZONES [PE00WS]
DAMPER_SCH_ZONES [PE00WW]
DAMPER_SCH_ZONES [PE0Z02W]
DAMPER_SCH_ZONES [PE03W]
DAMPER_SCH_ZONES [HE00]
DAMPER_SCH_ZONES [HE0Z03]
DAMPER_SCH_ZONES [PavN]
DAMPER_SCH_ZONES [PavS]
!*******************************************END DEFINE DAMPER
SCHEDULES FOR ZONES **********************

__._,_.___

  Primary EnergyPlus support is found at:
 http://energyplus.helpserve.com [3] or send a message to
energyplus-support@xxxxxxxx

 The primary EnergyPlus web site is found at:
 http://www.energyplus.gov [4]

 The group web site is:
 http://groups.yahoo.com/group/EnergyPlus_Support/ [5]

 Attachments are currently allowed but be mindful that not everyone
has a high speed connection. Limit attachments to small files.

 EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under
the Documentation link and press the "search" button.

 Your email settings: Individual Email|Traditional
 Change settings via the Web [6] (Yahoo! ID required)
 Change settings via email: Switch delivery to Daily Digest [7] |
Switch to Fully Featured
  Visit Your Group  [8] |  Yahoo! Groups Terms of Use  [9] |
Unsubscribe  [10]

__,_._,___

Links:
------
[1] http://www.cleantechanalytics.com
[2] mailto:jeannieboef@xxxxxxxxx
[3] http://energyplus.helpserve.com
[4] http://www.energyplus.gov
[5] http://groups.yahoo.com/group/EnergyPlus_Support/
[6]

http://groups.yahoo.com/group/EnergyPlus_Support/join;_ylc=X3oDMTJmNzFiZ3NhBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3N0bmdzBHN0aW1lAzEzMzY5NDkxODQ-
[7]

mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx?subject=EmailDelivery:Digest
[8]

http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJkYnN0NGdsBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2hwZgRzdGltZQMxMzM2OTQ5MTg0
[9] http://docs.yahoo.com/info/terms/
[10]

mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe