RE: [EnergyPlus_Support] Re: Extremely High Cooling Load due to Ventilation





This is input is far too high “ Flow/AreaFlow Rate per Zone Floor Area: 2.3 m3/s-m2”

 

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of tgha_ray
Sent: Friday, May 18, 2012 8:32 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Re: Extremely High Cooling Load due to Ventilation

 

 

Hi all. I've got a similar situation. When I look at the Results Viewer under "Average Outdoor Air During Occupied Hours", infiltration shows 286.153 ach for each of the 4 zones! (All with exterior walls and window subsurfaces.) How did that happen? I used the Outpatient Facility schedules without modification. Is this the result of some basic oversight on my part. It's just a test building with ASHRAE constructions.

Thanks!
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Ng Poh Khai <ng_khai@...> wrote:
>
>
> Dear All, I am trying to do a parametric simulation on the Window-Wall-Ratio of a semi-transparent BIPV. I started with 90% WWR just to make sure that all the values/results make sense. From the 90% WWR simulation run, i received a ideal cooling loads of 77555 kWh/m2 of energy consumption which is too high! From my investigation, I believe that it is due to my zone ventilation or infiltration. As my zone infiltration is only 0.1ACH, i suspect it is the zone ventilation. Without the zone ventilation, the cooling load is only 394 kWh/m2. My input fields for ZoneVentilation:DesignFlowRate are described briefly: Schedule: 0800 - 2000 hrsDesign Flow Rate Calculation Method: Flow/AreaFlow Rate per Zone Floor Area: 2.3 m3/s-m2Ventilation Type: IntakeFan Pressure Rise: nilFan Total Efficiency: 1Constant Term Coefficient: 1 The rest of the fields are default values when I created the object. Can anyone explain to me where did I go wrong to obtain such a high cooling load? Thanks and Best Regards,Poh Khai
>



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___