[EnergyPlus_Support] Re: Setpoint Managers are driving me crazy!



Hi James,

Thanks for the info. 

In your case then (no recirculation), you could quite possibly put a second setpoint manager on the outlet of the dehumidifying coil, but this one will not overwrite the other's temperature variable as it will be a humidification variable.

Secondly, I would give the dehumidification more "freedom" to deturmine its temperature outlet by using a SetpointManager:SingleZone:Cooling where you can define a temperature band (instead of the rigid SMScheduled).

I bet you are starting to enjoy this.

Regards,

Jean.



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/