I have recently submitted a hotel project for LEED review. The Proposed
system uses a guest room management system which places guest rooms in the
unoccupied mode when the room is vacant or not rented.
The typical usage schedule for a hotel room is a fractional schedule, such
as shown in the ASHRAE User Manual, and this does not reflect well the
benefits of the guest room management system because the system
essentially turns equipment OFF instead of operating at partial load.
To approximate the guest room system, I created two schedule sets, one for
the Baseline using ASHRAE data and another for the Proposed system. The
Proposed system makes the same presumption as is used for lighting
occupancy sensors, which is that a 10% reduction will occur for automatic
ON / OFF compared to manual operation.
The Proposed schedules:
? Use discrete occupied / unoccupied temperature setpoints
? Change the People schedules to all ?1? (100%) and ?0? (0%). These
schedules were based on discussion with the Owner. Keep in mind that E+
assumes ?occupied? when people are present and ?unoccupied? when they are
not.
? Maintain 90% of the total occupancy hours over a year?s time compare to
the Baseline.
The final result was to model an HVAC system as occupied for 90% of the
hours compared to the Baseline.
> Hi guys.
>
> Does anybody have experience doing an exceptional calculation for lighting
> on hotel rooms due to card keepers?
>
> Any help would be appreciated
>
> Oscar.
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/