[EnergyPlus_Support] Re: Unitary DX for cooling - not sizing well
Firstly, setback SP temps are required by 90.1, baring the few exception, for example for radiant heating or cooling. Secondly, they are quite severe, I.e. 13degC if I remember right.
Thirdly, it appears that ASHRAE does not distinguish during occupied and non-occupied hours setpoint not met. As for LEED, if I remember right, you fill in both on the form.
Lastly, I think the 55 Std wording of "peak to peak" should probably mean max peak to troff...I imagine fluxuations over a .25 hr period and measuring the lowest temp and highest temp over that period...if I half that to get a max deviation from the average of the two extream values, I get (supprise) 0.505.
So I think I could settle on a tolerance of 0.5.
And my gut feeling is that pulldown time should be an issue...I'll run the parametric study and let you know what pulldown time gives me 300 unmet hours total. It will be interesting to compare to your 2 F/hr.
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/