[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: Partially opened windows modulated by a schedule
Correction. The temperature limits are schedules. You don't have to change them with EMS...they can stay set. I was looking at velocity modulation.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Jean marais" <jeannieboef@...> wrote:
>
> Very good point. Venting availability is on/off regardless of whether you use "constant", "temperature" or other venting schemes. I don't think there is a way to change the opening area with a schedule directly. The only way that I can think of is to use the temperature scheme and change the temperature limits via EMS...I looked into this a while ago, due to another problem I was having. The problem was solved without imploying the EMS so I didn't have to complete it...VERY time consuming to do this at zone level.
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "k.rosemeier" <k.rosemeier@> wrote:
> >
> > It is my understanding that with ventilation control mode "Constant" in AirflowNetwork:MultiZone:Zone a venting availability schedule can only be on or off.
> > A way I found for altering the window opening fraction with control mode "Constant" is by changing the factor in AirflowNetwork:MultiZone:Surface for the LVO in question. Yet: while this seems to work with an on/off venting availability schedule, I cannot modulate the opening fraction with it.
> > Is there a way of modulating the opening fraction based on a schedule (regardless of temperatures and comfort parameters)?
> >
> > I want model: windows fully opened at certain times during the day, but only left ajar over night.
> >
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/