one of the earlier warnings mentioned Hot Water Loop. Could there be a node connection mistake?
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Javed Iqbal <eee.javed@...> wrote:
>
> Hi,
>
> I am using Constant Primary and Variable secondary chilled water
> pump. Condenser water pump is also *variable* but hot water pump is *
> constant speed*. All fields are autosize..
>
> thanks
>
> On Wed, Jul 4, 2012 at 10:52 AM, Mário <mneves32@...> wrote:
>
> > **
> >
> >
> > Hello,
> >
> > What kind of pumps, are you using?
> > What is your pump head set to?
> > How are you controling the pump operation?
> >
> > Sometimes when I get these kind of errors in the cooling plant it´s
> > because of the pumps.
> >
> > Best
> >
> > MN
> >
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Edwin Lee <leeed2001@>
> > wrote:
> > >
> > > Are you getting any other errors or warnings? Looks like the loop is out
> > > of control. Some more information on your loop is really needed to
> > > identify the problem.
> > >
> > > Edwin
> > >
> > > On Wed, Jul 4, 2012 at 10:37 AM, Javed Iqbal <eee.javed@> wrote:
> > >
> > > > **
> >
> > > >
> > > >
> > > > Hi All,
> > > >
> > > > I am getting following warning.What could be the possible reason? I am
> > > > trying to model central plant with VAV.
> > > >
> > > > Thanks!
> > > >
> > > > ** Warning ** GetDensityGlycol: Temperature out of range (too high) for
> > > > fluid density
> > > > ************* ** ~~~ ** This error occurred 106213 total times;
> > > > ************* ** ~~~ ** during Warmup 0 times;
> > > > ************* ** ~~~ ** during Sizing 0 times.
> > > > ************* ** ~~~ ** Max=173.136908 {C} Min=100.001832 {C}
> > > > *************
> > > > ************* ** Warning ** Plant loop exceeding upper temperature
> > > > limit, PlantLoop="HOT WATER LOOP HOT WATER LOOP"
> > > > ************* ** ~~~ ** This error occurred 95517 total times;
> > > > ************* ** ~~~ ** during Warmup 0 times;
> > > > ************* ** ~~~ ** during Sizing 0 times.
> > > > ************* ** ~~~ ** Max=173.15264
> > > > *************
> > > > ************* ** Warning ** GetSpecificHeatGlycol: Temperature out of
> > > > range (too high) for fluid specific heat
> > > > ************* ** ~~~ ** This error occurred 3928457 total times;
> > > > ************* ** ~~~ ** during Warmup 0 times;
> > > > ************* ** ~~~ ** during Sizing 0 times.
> > > > ************* ** ~~~ ** Max=173.195998 {C} Min=125.004998 {C}
> > > > *************
> > > > ************* ** Warning ** CoolingTower:VariableSpeed "MAIN TOWER" -
> > > > Tower approach temperature is out of range error continues...
> > > > ************* ** ~~~ ** This error occurred 21 total times;
> > > > ************* ** ~~~ ** during Warmup 0 times;
> > > > ************* ** ~~~ ** during Sizing 0 times.
> > > > ************* ** ~~~ ** Max=1.093516 Min=0.36124
> > > > --
> > > >
> > > >
> > > > Javed Iqbal, LEED AP, CEA
> > > > Energy Analyst
> > > >
> > > >
> > > >
> > > >
> > > >
> > > > --
> > > >
> > > >
> > > > Javed Iqbal, LEED AP, CEA
> > > > Energy Analyst
> > > >
> > > >
> > > >
> > > >
> > >
> > >
> > >
> > > --
> > > Edwin Lee
> > > Doctoral Candidate, Oklahoma State University
> > > ASHRAE Student Member, *Former* ASHRAE OSU Student Branch President
> > > Office: ATRC 303: 405-744-3727
> > >
> >
> >
> >
>
>
>
> --
>
>
> Javed Iqbal, LEED AP, CEA
> Energy Analyst
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/