[EnergyPlus_Support] Learn from my mistakes - EMS to avoid DX coil freeze - bad implementation
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] Learn from my mistakes - EMS to avoid DX coil freeze - bad implementation
- From: "Jean marais" <jeannieboef@xxxxxxxxx>
- Date: Fri, 06 Jul 2012 05:19:47 -0000
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Thu, 05 Jul 2012 23:19:52 -0600
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=lima; t=1341551991; bh=TVqp0hNUqOovfcibwxkljQh2moQkjqoRlGTm3dweC+g=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:User-Agent:X-Mailer:X-Originating-IP:X-eGroups-Msg-Info:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=ok7vExwCh8UCwHPFna7HFlU2ShdeE/+9DrOSoFKqTi/Ii6LQeXHtIHl+09hEc3W9YdbR61AJt3RaYwHkZVCyJr3jfvMev9u25gfu0LFD3i9X36KG3Ki9ChMapxHIDKN9
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=lima; d=yahoogroups.com; b=DR8LC9ueHz6Ybc64wCmtqDWA5NldJOxRWU75qMLKKZSy/4C1PMcnAyJR+RiTx9FXEUnkmvqS8N4K0NGVzg04Xld1Bq2u2JctC3tnAO6Uxk1Te8BDw9ULd+slScjJN8Hv;
- Envelope-to: linda@xxxxxxxxxxxxxx
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
Dear Group,
It's always better to learn from the mistakes of other. So I'm sharing my mistake with you all.
I implemented a simple EMS to avoid DX coil freeze. The situation occurs when you have a room with high loads that needs cooling when the ODA temp is in the minus region and the same space needs loads of ODA.
So the current bit of EMS floating around here on the forum monitors the ODA temp and turns off the coil below a certain ODA temp.
A better place to monitor would be the DX coil inlet node as it may take into account the mixed air stream temp if the DX is after the mixing box...why? Because cold climates should a) have a freeze protection heating coil to avoid air at minus deg C temperatures from entering any system, regardless. This is imperitive for start up and start up from setback.
It's difficalt to startup a system when everything is frozen up.
b) The coil may need to operate at very cold outdoor temps. Examples include
1) coming back from a very high setback temperature after the building is nice and warm after the weekend, and the change over from setback happens to be on a cold early morning before occupation.
2) a server room still needs cooling...ODA has been preheated from -14 deg C ODA to +2. The DX coil is still seeing a massive load in the server room and tries to operate at max with an inflow air temp of +2. This is a DOAS because someone decided that the exhaust air does not go back to this AHU but is exhausted elsewhere.
I hope this helps.
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/