Your concern depends on what you are trying to achieve. Using the "simple" infiltration objects, you could define leakage per outdoor bounding walls or per all outdoor bounding areas. Using the more complex AFN the user must manually define all flow paths. There is no automation to calculate the perimeter crack length of windows, doors, walls, etc. DesignBuilder can partly automate the AFN creation and can assign a flow path for each sub-surface element (door/window), as well as some of the controls and managers used in AFNetworks.

When simulating the air flows due to the opening of doors and windows, you'll need to make some sacrifices, assumptions, simplifications.

But if you're only concerned with energy usage due to leakage infiltration, in modern buildings that are mechanically ventilated, then the fraction of energy usage attributed to leakage infiltration is most likely very low, therefore accuracy is of lesser importance here (in my opinion).

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "r2baar" <ritwikraj@...> wrote:
>
> Hi Everyone,
> 
> I am a new user, and I am concerned about infiltration changes due to any gaps (even if they are very small) between walls or between a roof and a wall. Is the infiltration only dependent on the effective leakage area, or does it get affected by other "areas" that allow leakage?
> 
> Thanks very much.
> 
> Ritwik
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/