[EnergyPlus_Support] Re: SimHVAC: Maximum iterations (200) exceeded
I do not believe this is generally a serious error. I'd look thru all the output files and if you are getting "good values" then your data is likely not corrupt.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "FrancescoP" <direzionecontraria@...> wrote:
>
> I have found a discussion in which the same problem was discussed:
> http://tech.groups.yahoo.com/group/EnergyPlus_Support/message/11913
> In my case the problem is in AirLoops and in ZoneEq, but no idea why.
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "FrancescoP" <direzionecontraria@> wrote:
> >
> > Hello
> > I have the following warning. As you can see, I increased the maximum iterations but without success. Is it an important problem?
> >
> > ** Warning ** SimHVAC: Maximum iterations (200) exceeded for all HVAC loops, at SPINIGARDOLO, 01/01 06:00 - 06:02
> > ** ~~~ ** SimFlags=[TTFFF] AirLoops[T],ZoneEq[T],NonZoneEq[F],PlantLoops[F],ElecCircuits[F]..F=ok,T=fail
> > ** ~~~ ** HVAC Tolerance Flags=[0000000] Enthalpy[0],MassFlow[0],HumRat[0],Pressure[0],FlowQual[0],Energy[0],Temp[0]..0=ok,1=fail
> > ** ~~~ ** HVAC Tolerance Values, Most Recent listed first
> > ** ~~~ ** HVAC EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** HVAC side outlet node=[252 - LORAN CTL02 DEMAND SIDE OUTLET]
> > ** ~~~ ** HVAC EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** HVAC side outlet node=[2 - LORAN CTL02 SUPPLY SIDE OUTLET 1]
> > ** ~~~ ** HVAC EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** HVAC side outlet node=[252 - LORAN CTL02 DEMAND SIDE OUTLET]
> > ** ~~~ ** HVAC EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** HVAC side outlet node=[2 - LORAN CTL02 SUPPLY SIDE OUTLET 1]
> > ** ~~~ ** HVAC EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** HVAC side outlet node=[252 - LORAN CTL02 DEMAND SIDE OUTLET]
> > ** ~~~ ** Plant Tolerance Flags=[00000000] Enthalpy[0],MassFlow[0],HumRat[0],Pressure[0],FlowQual[0],Energy[0],Temp[0],PlantFlowMassFlow[0]..0=ok,1=fail
> > ** ~~~ ** Plant Tolerance Values, Most Recent listed first
> > ** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[166 - CONDENSER LOOP SUPPLY SIDE OUTLET]
> > ** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[158 - CONDENSER LOOP DEMAND SIDE OUTLET]
> > ** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[37 - STORAGE TANK SOURCE LOOP OUTLET NODE]
> > ** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=6.477E-008, HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=-1.011E-002, TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[35 - INSTANTANEOUS WATER HEATER OUTLET NODE]
> > ** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[150 - CHW LOOP SUPPLY SIDE OUTLET]
> > ** ~~~ ** Plant Flow Tolerance Values, Most Recent listed first
> >
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/