[EnergyPlus_Support] Re: Report about ventilation flows



Use Output:Variable,*,Zone Infiltration Mass,HOURLY; to get infiltration from each zone in kg. Divide by output time step (not simulation time step) in sec to get kg/(unit time step). You can divide by density to get m3/(unit time step).

Use Output:Variable,*,Zone Mechanical Ventilation Volume Flow Rate Current Density,Hourly; to get the hourly averaged mech vent to each zone.

Are you using airflow network and want the flow through each opening? You can read the Input Output Reference pdf under Airflow Network on guidance for this.

Hope this helps!

Lisa Ng
NIST
IAQ & Ventilation Group





--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "cia08jss" <cia08jss@...> wrote:
>
> I'm also looking at ventilation flows and ideally would like to output the volume of air flowing through each opening in the building for each timestep. How would I go about doing this?
> 
> I've looked at the OutdoorAirSummary but this seems to output average and minimum outdoor air.
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Griffith, Brent" <brent.griffith@> wrote:
> >
> > See the predefined table called OutdoorAirSummary
> > 
> > From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of FrancescoP
> > Sent: Wednesday, August 01, 2012 9:08 AM
> > To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> > Subject: [EnergyPlus_Support] Report about ventilation flows
> > 
> > 
> > 
> > I'm looking for a report that provides ventilation flows, concerning both mechanical and natural ventilation.
> > I'm using Output:Table:SummaryReports in order to produce reports in html format.
> > I found MechanicalVentilationLoadsMonthly but it doesn't regard natural ventilation.
> > Best Regards
> >
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/