Air Wall? Is this an eplus Object? I Wohls Look to the IRTsurface Object. Bear in mind it Works only with
1) IRTmaterial Object
2) Not with FullExteriorandInterior radiation modes
3) You should define an extra convection coeff using the object (I forget the name...something like SurfaceProperty:ConvectionCoeffecient) so that it is set to the lower limit
4) Use ZoneMixing objects (or crack objects if using AFN) to ensure air mixing between virtual zones.
This is all documented in the io ref, but the IRTSurface object has most of the explanation from memory.
Hope this helps and does not complicate instead. It's really not as complex as it sounds.
Jean Marais
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/