This looks like 3 independant problems. 1) Shading and geometery, 2) RoomAirModel and 3) AFN.
1) Try and simplify window and shading fin geometries. For example, if you have 3 windows to a zone, you may delete two of them and put a multiplier of 3 in the remaining window object. This may help with the overlapping shading problems that you have. Also you should not use certain radiation modes such as FullExteriorAndInterior... when you have non-convex zones. And it looks like your roof floor is slightly tilted.
2) I've not used the RoomAirModel you are using, but it looks like your crack on the horizontal surface is causing problems with the model's calculations. As a tip you should know that although a crack must be on a surface, the world co-ordinates of the surface are free to put it anywhere...also inside or outside of the zone it belongs to. This could be used when needing to create dummy zones.
3) AFN crack object type you are currently using may not be the best one to model large horizontal openings...there are some that do a better job. Look to the AFN section in the io ref.
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/