|
Vaibhav, A bypass is an EnergyPlus idiosyncrasy that helps E+ balance mass flows in a loop. They are not always needed, but also, they don’t get used or affect results in a balanced loop. I think of them as a way to avoid certain problems in the simulation while I am solving other problems. I review the flows in the bypass after a simulation, and if there is flow when I don’t expect it, I investigate to determine its cause. James V Dirkes II, PE, BEMP, LEED AP The Building Performance Team Inc 1631 Acacia Drive, Grand Rapids, MI 49504 616 450 8653 From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Vaibhav Jain Hello Group! Vaibhav Jain Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |