Then you either have large zone radiant loads or direct or diffuse solar on the surfaces that cause these high temps. Usually, bringing in infiltration will reduce the surface temps, something is causing them to be high. Since this is happening during warmup, you can't see the data in the csv file (your Output:Variables). Add: Output:Diagnostics,ReportDuringWarmup; This way you can see what's happening (in the csv file) and possibly diagnose the problem. Add report variables from the rdd file (use Output:Dictionary,IDF; to see the rdd) On 8/16/2012 10:28 AM, Eshagh wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.