In the Controller:OutdoorAir object, the input field called Minimum Outdoor Air Schedule Name, setup the schedule to be zero during unoccupied hours. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Carolina Galeazzi Hi All, To build an ASHRAE baseline model, it's said that 'supply and return fans should be cycled to meet heating and cooling loads during unoccupied hours'. I understand that fans should run for mechanical ventilation, but with zero outside airflow rate. How can I cycle the variable volume fan of the AHUs in Eplus, with zero outside airflow rate? Thank you for your help!! Carol __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.