Re: [EnergyPlus_Support] 3rdOrderBackwardDifference in Energy Plus



E+ saves the previous zone temps in history terms, t-1, t-2, t-3, and 
uses those as needed. Of course these are updated every time step (i.e., 
using first in last out).

On 8/16/2012 11:58 AM, bokelai1989 wrote:
> Hi, All,
> In the Engineering Manual of Energy Plus, it mentions a method of "3rdOrderBackwardDifference".
>
> It says "This algorithm requires zone air temperatures at three previous time steps and uses constant temperature coefficients. The assumption is that three previous time steps lengths are the same."
>
> I would like to know in terms of its inner calculation mechanism, how energy plus acquires the zone air temperature at three previous time steps?
>
> Thanks!
> Na
>
>
>
> ------------------------------------
>
> Primary EnergyPlus support is found at:
> http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/