To be exact, the by-pass path is required when the model requres one. If you think that the by-pass is the same as a electrical short circuit, it cannot be placed any where you want. A by-pass pipe has the characteristic "by-pass". It is not just a pipe. 1) In a real system, a by-pass pipe has a one-way valve and/or a pressure valve inside. The picture of a real by-pass pipe has been shown on this forum before. That was for a circulation pump of a furnace. Its use can save energy and allow the water to circulate without the pump.. 2) In simulation, it is a mandatory requirement when required. You may not need to enter it in your IDF, because the software knows how to add one and give you a warning. If you include a by-pass pipe in a wrong place, the simulation may crash. Dr. Li
To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: vaibhav.energyarchitect@xxxxxxxxx Date: Thu, 16 Aug 2012 16:17:37 +0200 Subject: Re: [EnergyPlus_Support] What ByPass component means?
Thank you for the discussion!
So in conclusion, I understood:
1. There is no harm in placing a ByPass in simulation. Perhaps in real world systems there could be some issues if it is not used. If in future I come across a ByPass then I will definitely collect its pictures or drawings to post it here.
2. It seems that in simulation it is not be a mandatory requirement, but its better to use it for further detailed check.
Thank you! Vaibhav
On 15 August 2012 03:02, YuanLu Li <yli006@xxxxxxxxxxx> wrote:
In simulation, by-pass is simply an extra register in the program. The constant speed pump and a variable speed pump are now in the same object. Whether you enter the by-pass or not is no longer an issue.
For the benefit of the original user who asked the question, I simbly listed all the possible use of the by-pass branch or pipe, as appeared in the SVG. Most of them are in a real system. If you think they are wrong, please correct them.
" A bypass is an EnergyPlus idiosyncrasy that helps E+ balance mass flows in a loop." Does not this imply that by-pass is there for EPlus simulatin use only? May be I missed the real meaning of idiosyncracy.
There is no need to discuss this matter any further.
I said that the air loop does not need a by-pass. Actually, using one can solve many simulation problems as well. I am not going to explain this here
. Dr. Li Date: Tue, 14 Aug 2012 16:34:04 -0500 Subject: RE: [EnergyPlus_Support] What ByPass component means?
Dear Dr. Li,I respectfully disagree regarding how commonly a bypass is used in real systems. Other than primary ? secondary piping systems, I almost never have seen a bypass. For primary ? secondary systems (which use a bypass), EnergyPlus uses the ?CommonPipe? for the bypass function.
The use of a bypass in real systems is not the primary issue here, though, so it?s probably not worth going into great detail in the forum, but I would welcome discussion it further privately.
Now that I am thinking about this in more detail, I believe that I had some input from one of the Help Desk wizards that an upcoming release may make bypasses unnecessary (but I am not sure about that and cannot find the message).
Finally, I have a feeling that Vaibhav is using DesignBuilder or something similar. The bypass does not appear accidentally, someone has to put it there! As hinted / mentioned earlier, I think the use of a bypass has been the recommended practice.
James V Dirkes II, PE, BEMP, LEED AP The Building Performance Team Inc
1631 Acacia Drive, Grand Rapids, MI 49504 616 450 8653
" A bypass is an EnergyPlus idiosyncrasy that helps E+ balance mass flows in a loop."
I disagree. I bypass path is in most real water systems. Air can be compressed and a fan will not fully blocking the flow. Therefore, a bypass is not generally provided. A variable balanced flow system cannot be implemented without some dedicated controller or computer control. For safety and other reasons, bypass are still provided in a real system.
For your SVG diagram, the constant speed pupmp has a constrant flow rate. The zone demand is addusted by varying the flow rate. The excess flow must go somewhere. Therefore, a by-pass path is provided. If there is only one branch in the loop, the system can use the on/off mode to control the supply capacity, because there is no other demand in the loop.
For the supply side by-pass, I visualize it as the link to the heating or cooling source. When the pump is off, the water can still be maintained at the set point temperature by cycling the source. For a coal furnace, it cannot be shut off quickly. The pump is usuallby fitted with a bypass so that the demand is not completely disconnected. The furnace air intake is reduced, and the file will then be slowly extinguished.
The tower has a by-pass, because it also have a setpoint temperature to meet, even when the condenser loop pump is turned off from the demand side. "By-pass" is not a redudent element for EPlus simulation purose only. It is also a reminder that they are in a real system.
Dr. Li
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: jim@xxxxxxxxxxxxxxxxxxxxxxxxxxxDate: Tue, 14 Aug 2012 09:36:54 -0500 Subject: RE: [EnergyPlus_Support] What ByPass component means?
Vaibhav,A bypass is an EnergyPlus idiosyncrasy that helps E+ balance mass flows in a loop. They are not always needed, but also, they don?t get used or affect results in a balanced loop. I think of them as a way to avoid certain problems in the simulation while I am solving other problems. I review the flows in the bypass after a simulation, and if there is flow when I don?t expect it, I investigate to determine its cause.
James V Dirkes II, PE, BEMP, LEED AP The Building Performance Team Inc
1631 Acacia Drive, Grand Rapids, MI 49504 616 450 8653
Hello Group! As I am not a mechanical engineer that's why I am curious to know - what does ByPass component means, which I see in both demand and supply side, and what is its function in real world systems, if any? I am attaching a picture (in line with text) to explain what exactly I mean. I somehow couldn't understand it very intuitively from documentation. Thank you!
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
__,_._,___
|