[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: Heating and Cooling Coil Control



Thank you for your help,

I am going to work on this thru the weekend then post the IDF on sunday evening.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, YuanLu Li <yli006@...> wrote:
>
> 
> Your questions are very good.  See if anyone will respoond.  I cannot answer them, as there is not  enough information on the system.
> 
> If you place the control at the wrong point or at a point already used by another setpoint manager, I do not know what will happen.   Once the supply air is set to 14°C say, it cannot be changed. The reheat heater can be controlled by the zone thermostat. The VAV system  overcool the zone at the minimum damper position, and then turn on the zone  reheat heater to heat the zone to the required temperature.  I suppose, you can re-associate the zone to the setpoint manager:reheat and not to use the zone thermostat directly.  More controller, schedules are required to implement this mode. I have said many times that I will never use this system control mode without a full computerised control for the building.  I have not read the ASHRAE document and guidelines.  Dr. Li   
>  To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> From: matthew.sverre.anderson@...
> Date: Fri, 17 Aug 2012 17:29:37 +0000
> Subject: [EnergyPlus_Support] Re: Heating and Cooling Coil Control
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
>  
> 
> 
> 
>   
> 
> 
>     
>       
>       
>       So in reading thru the I/O Manual the difference between the
> 
> 
> 
> (1) SetpointManager:SingleZone:Reheat
> 
> (2) SetpointManager:SingleZone:Heating
> 
> (3) SetpointManager:SingleZone:Cooling 
> 
> 
> 
> Are as follows:
> 
> 
> 
> (1) The reheat setpoint manager determines the supply air temperature (with upper and lower boundaries) required to meet zone load
> 
> 
> 
> (2) The heating setpoint manager only determines the supply air temp that will satisfy the heating load
> 
> 
> 
> (3) The cooling setpoint manager only determines the supply air temp
> 
> that will satisfy the cooling load
> 
> 
> 
> Now lets say I put a reheat setpoint at the zone inlet for supply air so that it will be able to generate a supply air temperature to meet either the heating or cooling load required. Presumably I wouldn't want to put it at the Air Loop Outlet because the Air Loop Outlet is the Cooling Coil Outlet How do I tie this into controlling the Coil:Cooling:Water and the Coil:Heating:Water?
> 
> 
> 
> The Controller:WaterCoil is meant to sense the temperature at the Air Outlet of the coil and adjust the flow of the fluid thru the coil correct? So if we put a setpoint at the outlet of the coil the coil flow will increase or decrease to reach that setpoint correct?
> 
> 
> 
> Is this correct logic?
> 
> 
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Jim Dirkes <jim@> wrote:
> 
> >
> 
> > How about SetPointManager:SingleZone:Reheat?  I use it frequently for packaged rooftop (single zone) systems.  No reheat is actually required.
> 
> > 
> 
> > James V Dirkes II, PE, BEMP, LEED AP
> 
> > The Building Performance Team Inc
> 
> > 1631 Acacia Drive, Grand Rapids, MI 49504
> 
> > 616 450 8653
> 
> > 
> 
> > From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of ntraughpee
> 
> > Sent: Friday, August 17, 2012 9:30 AM
> 
> > To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> 
> > Subject: [EnergyPlus_Support] Re: Heating and Cooling Coil Control
> 
> > 
> 
> > 
> 
> > 
> 
> > It is an air system with many diffusers and a single zone.
> 
> > 
> 
> > Does my question about how to setup the Setpoint:Manager make sense?
> 
> > 
> 
> > Right now my model is simultaneously cooling and heating and I know I can fix a lot of this by just shutting off the heating coil in the summer and the cooling coil in the winter but I'd prefer to figure out how to make it work in E+ without that work around.
> 
> > 
> 
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx<mailto:EnergyPlus_Support%40yahoogroups.com>, YuanLu Li <yli006@<mailto:yli006@>> wrote:
> 
> > >
> 
> > >
> 
> > > Whether you call it a AHU or a zone fan coil unit depends on the capacity. If you have a gym with many people, it will be an air system with many diffusers, although there are no seperate zones. The old fashioned thermostat master zone controlled AHU is what you need. I think there is example file for this, although I am not very sure now, as many of the 5Zone examples have been converted to setpoint control of the AHU. The system should have Type 4 theremostat with economiser function at the OA controller. OA flow rate can be linked to the people occupancy schedule and the minimum air valuevalue. So, no people, low air flow, or shut down altogether.. Dr. Li
> 
> > > To: EnergyPlus_Support@xxxxxxxxxxxxxxx<mailto:EnergyPlus_Support%40yahoogroups.com>
> 
> > > From: matthew.sverre.anderson@<mailto:matthew.sverre.anderson@>...
> 
> > > Date: Thu, 16 Aug 2012 22:07:38 +0000
> 
> > > Subject: [EnergyPlus_Support] Heating and Cooling Coil Control
> 
> > >
> 
> > >
> 
> > >
> 
> > >
> 
> > >
> 
> > >
> 
> > >
> 
> > >
> 
> > >
> 
> > >
> 
> > >
> 
> > >
> 
> > >
> 
> > >
> 
> > >
> 
> > >
> 
> > >
> 
> > >
> 
> > >
> 
> > >
> 
> > >
> 
> > >
> 
> > >
> 
> > >
> 
> > >
> 
> > >
> 
> > > Hey Everybody,
> 
> > >
> 
> > >
> 
> > >
> 
> > > So I currently have a zone which is controlled by a single air handler. The physical mechanics of the system are this:
> 
> > >
> 
> > >
> 
> > >
> 
> > > (Economizer) -> Fan -> Heating Coil -> Cooling Coil -> Zone
> 
> > >
> 
> > >
> 
> > >
> 
> > > Both the Heating Coil and Cooling Coil are on district plants. The system itself is a single zone CAV system.
> 
> > >
> 
> > >
> 
> > >
> 
> > > What would be the best way to go about modeling/organizing this?
> 
> > >
> 
> > >
> 
> > >
> 
> > > The HVACTemplate:System:VAV does not have the ability to list the coil as anything but electric/gas (for obvious reasons) or I could list it as a reheat coil and attempt to reorganize the nodes later. My first attempt was to list it as a reheat coil then reorganize the nodes, but it led to this question.
> 
> > >
> 
> > >
> 
> > >
> 
> > > How would I organize the controls, without using a schedule, so that the heating coil water massflow rates drop to zero when no heating is required and the chilled water mass flow rates drop to zero when no cooling is required?
> 
> > >
> 
> > >
> 
> > >
> 
> > > I currently have a mixed air set point scheduled at the fan outlet to control the economizer (is there a better way to do this to get maximum cooling out of the economizer?) but where can I put a setpoint in the SetpointManager(and what kind) combined with the ThermostatSetpoint:DualSetpoint (which is what the HVACTemplate expands to in the expidf) to add intelligence to the control layout. Currently I have the VAV airflow % set to 100% so it is a CAV system but I need to model the coil flow like what you would get with control valves on there that shut down when they are not needed and I seem to be spinning my wheels with this particular layout.
> 
> > >
> 
> > >
> 
> > >
> 
> > > The big problem with this building is that it is a gym so during cooling months we will always need to cool but during heating months we might need to heat and we might need to cool depending on the occupancy.
> 
> > >
> 
> >
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/