Dear All,
 
I have a problem that as I have a relatively high heat loss from window as shown in the table extracted from the html file.  The window heat gain removal is around half of the window heat gain addition.  The location is Singapore where it is hot and humid.  I have also checked that the time that the outdoor air temperature is lower than the setpoint is less than 2 hours for the entire year.  May I know what can cause the Window Heat Removal? This is probably causing me to obtain results that show that having a 50% window to wall ratio will have a cooling load lower than having no windows at all.
 
Thanks for any inputs.
 
  HVAC Input Sensible Air Heating [GJ] HVAC Input Sensible Air Cooling [GJ] HVAC Input Heated Surface Heating [GJ] HVAC Input Cooled Surface Cooling [GJ] People Sensible Heat Addition [GJ] Lights Sensible Heat Addition [GJ] Equipment Sensible Heat Addition [GJ] Window Heat Addition [GJ] Interzone Air Transfer Heat Addition [GJ] Infiltration Heat Addition [GJ] Opaque Surface Conduction and Other Heat Addition [GJ] Equipment Sensible Heat Removal [GJ] Window Heat Removal [GJ] Interzone Air Transfer Heat Removal [GJ] Infiltration Heat Removal [GJ] Opaque Surface Conduction and Other Heat Removal [GJ]
50% WWR SOUTH ZONE 0 -106.201 0 0 23.95 27.69 38.768 10.723 0 12.492 0.192 0 -6.206 0 -1.408 -0.002
WEST ZONE 0 -108.368 0 0 23.85 27.093 38.768 13.568 0 12.485 0.617 0 -6.514 0 -1.499 -0.005
EAST ZONE 0 -108.466 0 0 23.866 26.598 38.768 13.786 0 12.486 0.754 0 -6.303 0 -1.49 -0.001
NORTH ZONE 0 -105.651 0 0 23.978 27.747 38.768 10.659 0 12.492 0 0 -6.131 0 -1.379 -0.482
Total Facility 0 -428.687 0 0 95.644 109.128 155.071 48.737 0 49.956 1.564 0 -25.154 0 -5.776 -0.489
0% WWR SOUTH ZONE 0 -108.747 0 0 23.783 31.743 38.768 0 0 12.496 3.504 0 0 0 -1.547 -0.008
WEST ZONE 0 -109.619 0 0 23.735 31.743 38.768 0 0 12.492 4.466 0 0 0 -1.585 -0.003
EAST ZONE 0 -109.86 0 0 23.727 31.743 38.768 0 0 12.491 4.725 0 0 0 -1.595 -0.001
NORTH ZONE 0 -107.59 0 0 23.839 31.743 38.768 0 0 12.497 2.234 0 0 0 -1.491 -0.007
Total Facility 0 -435.816 0 0 95.085 126.973 155.071 0 0 49.976 14.929 0 0 0 -6.218 -0.019


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___