[EnergyPlus_Support] Re: Adding untreated outside air to a zone?
Have you thought about including a normal air handling unit and setting the coil availablilties to zero?
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "marko.ignjatovic1980" <marko.ignjatovic1980@...> wrote:
>
> Maybe my previous question wasn't clear enough.
>
> I have a two story office building with Double skin facade (DSF) attached to it. Building is conditioned with 4-pipe fan coils due to possibility that simultaneous heating and cooling needs may occur. I want to compare building energy consumption (thermal and electrical) when DSF zone is sealed (base case) and mechanically ventilated with 100% outside air. For the later I have a problem. I want to add only a Fan object (preferably variable volume) that will operate when the DSF zone temperature exceeds certain temperature (in my case 50 oC). Is this somehow possible?
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "marko.ignjatovic1980" <marko.ignjatovic1980@> wrote:
> >
> > Hi Guys,
> >
> > I need some help in adding fan object to a zone. Zone is unconditioned and I want to have a fan that will operate when the temperature in zone exceeds 50oC. Fan will supply only fresh air to the zone. I tried with fancoil object and kept heating and cooling coil unavailable but the fan(variable volume) wouldn't turn on. The same happened when I changed fan to OnOff type. I would appreciate any idea
> >
> > Thanks in advance
> >
> > Marko
> >
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/