Re: [EnergyPlus_Support] simulation of separate fancoils





Alberto,

I suggest the following procedure:

Create file with one FCU using the HVAC Templates, and run this file.

This will create an 'expanded idf' with file suffix .expidf

Rename this file as suffix .idf so you can edit and run this file directly

Using the template will show you which objects are necessary to model the FCU. Duplicate them individually and append some differentiator in the name of objects, for example, if you used f1:Zone1 FCU1 change the second one to f1:Zone1 FCU2

You will need to create a node list for the supply and exhust connections in the ZoneHVAC:EquipmentConnections object to allow for multiple zone air inlet nodes and return or exhaust nodes

In zonehvac:equipmentlist, you will have two fan coil units, set the priority of the ventilation only FCU to 1 so that it operated first. You will also need to hard size this fan coil unit.

In the recirculating FCU set the OA flow to zero.

While I haven't specifically tried to model this system, I think this should work okay.

Good luck,

Jason


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___