Hello,
I'm confused on how to interpret CHW pumps for App. G.  Specifically, item 7 and 8 and how the 22 W/gpm is defined for a primary secondary configuration.  Section G3.1.3.10  can be interpreted (at least) two different ways.

First, Section G3.1.3.10 Chilled-Water Pumps (Systems 7 and 8)
?The baseline design pump power shall be 22 W/gpm.  Chilled-water systems with a cooling capacity of 300 tons or more shall be modeled as primary/secondary systems with variable-speed drives on the secondary pumping loop.  Chilled-water pumps in systems serving less than 300 tons cooling capacity shall be modeled as primary/secondary systems with secondary pump riding the pump curve.?

The question:
Should each primary and secondary pump be sized for 22 W/gpm OR should this ?design pump power? be divided up (in some way) between the primary and secondary pumps?

Possibility A:
If the 22 W/gpm should be the TOTAL pumping power, there is no guidance on how to divvy up this requirement and the constant volume primary pumps could be sized for 20 W/gpm and the secondary (VSD or riding pump curve) can be allotted 2 W/gpm.  


Possibility B:
Sizing each primary pump and secondary pump to 22 W/gpm will over-estimate the baseline pump energy (VSD or riding pump curve) and this is not the intent of 90.1. How do you interpret (and model) 90.1 App. G chilled-water pump power requirement of 22 W/gpm? p.s. I'm clear on what parameters needs to be changed in order to get 22W/GPM but i'm curious in knowing the modeling approach. Should i consider it as Complete system approach OR individual loop/pump approach?

Thanks,

--


Javed Iqbal, LEED AP, CEA
Energy Analyst 




Set a goal SO BIG that you can't achieve it until you GROW INTO THE PERSON WHO CAN.. 




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___