RE: [EnergyPlus_Support] Re: Modeling a Packaged Rooftop Heat Pump according to Appendix G





Perfect!

 

James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Fabiano Domingues Ferreira
Sent: Thursday, September 27, 2012 2:35 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: RES: [EnergyPlus_Support] Re: Modeling a Packaged Rooftop Heat Pump according to Appendix G

 

 

Hi Jim,

 

So to comply with the requirement I need to set the supplemental heating coil object type to Coil Heating Eletric and  Maximum Outdoor Dry-Bulb Temperature for Supplemental Heater Operation to 4° C?

 

 

 

Thanks,
 
Fabiano Ferreira

 

De: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] Em nome de Jim Dirkes
Enviada em: Thursday, September 27, 2012 11:40 AM
Para: EnergyPlus_Support@xxxxxxxxxxxxxxx
Assunto: RE: [EnergyPlus_Support] Re: Modeling a Packaged Rooftop Heat Pump according to Appendix G

 

 

The AirLoopHVAC:UnitaryHeatPump:AirToAir object has made it easy for you!  Notice the “Supplemental Heating Coil Object Type”

 

 

AirLoopHVAC:UnitaryHeatPump:AirToAir

Name

AirLoop_UnitCool1_GymBaseSys4

Availability Schedule Name

SchCpct_FanOpern

Air Inlet Node Name

NodeOut_MA_GymBaseSys4

Air Outlet Node Name

NodeOut_Air_GymBaseSys4

Supply Air Flow Rate During Cooling Operation

Autosize

Supply Air Flow Rate During Heating Operation

Autosize

Supply Air Flow Rate When No Clg or Htg is Needed

Autosize

Controlling Zone or Thermostat Location

Gym

Supply Air Fan Object Type

Fan:ConstantVolume

Supply Air Fan Name

SFan_GymBaseSys4

Heating Coil Object Type

Coil:Heating:DX:SingleSpeed

Heating Coil Name

HtgCoil_GymBaseSys4

Cooling Coil Object Type

Coil:Cooling:DX:SingleSpeed

Cooling Coil Name

ClgCoil1_GymBaseSys4

Supplemental Heating Coil Object Type

Coil:Heating:Electric

Supplemental Heating Coil Name

SupplHtgCoil_GymBaseSys4

Max. Supply Air Temp. from Suppl. Heater

35

Max. Outdoor DB Temp. for Suppl. Htr Operation

7.2

Fan Placement

DrawThrough

Supply Air Fan Operating Mode Schedule Name

SchCpct_AlwaysOn

 

 

James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of direzionecontraria
Sent: Thursday, September 27, 2012 10:08 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Re: Modeling a Packaged Rooftop Heat Pump according to Appendix G

 

 

I have found a document:
http://www.google.co.uk/url?sa=t&rct=j&q=ashrae+heat+G3.1.3.1&source=web&cd=1&ved=0CCAQFjAA&url="">
I think I did confusion between defrost and "electric auxiliary heat"... The electric auxiliary heat shall be a specific electric coil. In EnergyPlus what is the best solution to model the control of electric auxiliary heat system according to G3.1.3.1?

--- In
EnergyPlus_Support@xxxxxxxxxxxxxxx, "FrancescoP" <direzionecontraria@...> wrote:
>
> Probably I'll impose the condition concerning the temperature for the activation of the auxiliary heat through the field "Maximum Outdoor Dry-Bulb Temperature for Defrost Operation" of the object Coil:Heating:DX:SingleSpeed
> Do you think that it could be a good solution?
> The biggest problem in the interpretation of G3.1.3.1 is that I don't understand what "multistage space thermostats" mean.
> Best Regards
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Fabiano Domingues Ferreira" <fabiano.ferreira@> wrote:
> >
> > Hi,
> >
> >
> >
> > I'm modeling a project on the DesignBuilder according to the Appendix G of ASHRAE 90.1-2007 Standard.
> >
> > According to the Standard the system that I need to model is a Packaged Rooftop Heat Pump. I have a problem to comply with the item G3.1.3.1 Heat Pump, follow bellow.
> >
> >
> >
> > "G3.1.3.1 Heat Pump. Electric air-source heat pump shall be modeled with electric auxiliary heat. The system shall be controlled with multistage space thermostats and an outdoor air thermostat wired to energize auxiliary heat only on the last thermostat stage and when outdoor air temperature is less than 4°C."
> >
> >
> >
> > I have already modeled the auxiliary heat, I just don't know how to set the thermostats. Could you tell me how can I set those thermostats on the system?
> >
> >
> >
> > Regards,
> >
> > Fabiano Ferreira
> >
> >
> >
> > </pre></font size=2 color=red face=Calibri>NOTIFICAÇÃO<font><br>
> > </font size=2 color=black face=Calibri>Esta mensagem destina-se exclusivamente às pessoas identificadas e pode conter informações confidenciais sujeitas a proteção legal de comunicação. A leitura, uso, divulgação, cópia, distribuição ou disseminação por qualquer meio ou forma desta mensagem ou seu conteúdo está terminantemente proibida e poderá caracterizar ilícito civil e penal, sujeitando o responsável às penalidades aplicáveis. Caso a mensagem tenha sido recebida por engano, solicitamos a gentileza de informar ao remetente por e-mail ou por telefone usando as informações de contato no final do correio eletrônico (e-mail) e apague do seu computador. Muito Obrigado.<font><br>
> > </font size=2 color=red face=Calibri>LEGAL<font><br>
> > </font size=2 color=black face=Calibri>This message contains information which is confidential and may be privileged. Unless you are the addressee (or authorized to receive for the addressee), you are expressly prohibited to use, copy, distribute, disseminate or disclose in any way or by any mechanism to anyone the message or any information contained. If you have received the message in error, please advise the sender by reply e-mail or by telephone using the information in the sender signature above and delete the message. Thank you very much.<font> <br>
> > </font size=2 color=red face=Calibri>AVISO Y NOTIFICACION<font><br>
> > </font size=2 color=black face=Calibri>Este mensaje de correo electrónico y su contenido son estrictamente confidenciales. Si usted no es el destinatario o persona debidamente autorizada y responsable por la entrega de este documento y su contenido al destinatario, por la presente se le notifica que la publicación, uso, copia, distribución o reproducción de este correo electrónico y su contenido por cualquier medio o mecanismo esta estrictamente prohibida. Si usted ha recibido este correo electrónico por error, le agradecemos notificarlo de inmediato al remitente por correo electrónico (email) o avisar por teléfono al remitente, e inmediatamente borrar esta comunicación de su computadora. Muchas gracias.<font>
> > <pre>
> >
>

The information contained in this communication is confidential, may be privileged and is intended for the exclusive use of the above named addressee(s). If you are not the intended recipient(s), you are expressly prohibited from copying, distributing, disseminating, or in any other way using any information contained within this communication. If you have received this communication in error please contact the sender by telephone or by response via mail.

We have taken precautions to minimize the risk of transmitting software viruses, but we advise you to carry out your own virus checks on any attachment to this message. We cannot accept liability for any loss or damage caused by software viruses.

 



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___