RE: [EnergyPlus_Support] Overwriting scheduled setpoint with EMS
I suspect the unary ?-? operator in ?IF SenzorTempSpoljasnjeg < - 12.0? may not get parsed properly. EMS only supports unary minus sign in some cases, like right after a ?=? in a SET statement (historically it wasn?t supported at all). Try replacing all instances of ?-x? with ?(0 ? x)?
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of marko.ignjatovic1980
Sent: Wednesday, October 03, 2012 11:55 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Overwriting scheduled setpoint with EMS
Hi all,
I am having trouble overwriting hot water loop scheduled setpoint temperature which is my case 90oC. I am leaving all object classes related to this. I am trying to put control in hot water loop, and that scheduled temperature varies with outside temperature, since this is the most common heating control in my country. Maybe I didn't understand EMS guide well, because whatever I do, setpoint remains 90
Here it comes!
Schedule:Compact,
HW Loop Schedule, !- Name
Temperature, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until:24:00, !- Field 3
90; !- Field 4
!- =========== ALL OBJECTS IN CLASS: BOILER:HOTWATER ===========
Boiler:HotWater,
Central Boiler, !- Name
NaturalGas, !- Fuel Type
autosize, !- Nominal Capacity {W}
0.95, !- Nominal Thermal Efficiency
LeavingBoiler, !- Efficiency Curve Temperature Evaluation Variable
Boiler Efficiency, !- Normalized Boiler Efficiency Curve Name
90, !- Design Water Outlet Temperature {C}
autosize, !- Design Water Flow Rate {m3/s}
0, !- Minimum Part Load Ratio
1.2, !- Maximum Part Load Ratio
1, !- Optimum Part Load Ratio
Central Boiler Inlet Node, !- Boiler Water Inlet Node Name
Central Boiler Outlet Node, !- Boiler Water Outlet Node Name
99.9, !- Water Outlet Upper Temperature Limit {C}
ConstantFlow, !- Boiler Flow Mode
__._,_.___
Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov
The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=27018/stime=1349289125>
Your email settings: Individual Email|Traditional
<http://groups.yahoo.com/group/EnergyPlus_Support/join;_ylc=X3oDMTJmamh0MjhlBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3N0bmdzBHN0aW1lAzEzNDkyODkxMjU->Change settings via the Web (Yahoo! ID required)
Change settings via email: <mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx?subject=Email Delivery: Digest>Switch delivery to Daily Digest | Switch to Fully Featured
<http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJkcjM4YzQ4BF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2hwZgRzdGltZQMxMzQ5Mjg5MTI1>Visit Your Group | <http://docs.yahoo.com/info/terms/> Yahoo! Groups Terms of Use | <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe> Unsubscribe
__,_._,___