Is the VRF capacity in the two simulations identical? If not make it so If so, I suspect that the VRF control algorithm causes it to respond more slowly than EnergyPlus. It will be difficult or impossible to make these match. Consider, however, that once the room reaches its setpoint, there is only a small capacity change at any given time. Major changes occur only at night or morning., so 90% of the time the two models should be very close in performance. James V Dirkes II, PE, BEMP, LEED AP From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of soohyeunyang I am constructing the Cooling and Heating System using VRF(Variable Refrigerant Flow) example file(Version 7.0). __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.