Hi, here is an advanced hint for accomplishing #2: it is now possible to use EMS and the user-defined component models called Coil:UserDefined and ZoneHVAC:ForcedAir:UserDefined together to model some very imaginative configurations. The basic air loop limitations still apply to the first zone, but you can model the rest using these custom objects. The entire energyplus zone model becomes the user defined model for a “coil.” The user defined coil appears in the AirLoop’s Branch (or outdoor equipment list) and each “coil” represents one of the downstream zones. The user defined ZoneHVAC unit appears in the zone equipment list and gets connected to other zones by the “coil” connections (modeled on the supply side of the air loop) . The user ZoneHVAC “units” have both an inlet and an outlet node which get their nodes wired to an associated user coil using EMS programming. The programming is simple, just directly map node conditions so that the same conditions entering the coil enter the zone, and the same conditions leaving the zone leave the coil. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of gosset_serge Thanks for the hints... Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |