RE: [EnergyPlus_Support] Exceeded Max Iterations Trouble Shooting




Version 7.2 was changed to revamp the information reported in such warning messages (if you use Output:Diagnostics, DisplayExtraWarnings ).



It can now detect some types of numerical oscillation that show which part of the solution is not converging and causing it to keep on iterating up to the maximum limit.  If the messages indicate it found oscillations then there is probably nothing to be done to fix it but you can narrow down which device is the one not finding a unique solution.  If the magnitude of the oscillations seem reasonable then the results can be trusted. 



It can also now detect if some results are changing monotonically over iterations.  If the messages indicate monotonic changes have been found it is probably worthwhile to try to address the issue by raising the limit which can be set in the ConvergenceLimits object input field called Maximum HVAC Iterations.  



One main cause for these that I know of occurs when VAV air terminal units are just lifting off the minimum stop and air side economizer cooling is available.  The fluctuations in damper position, return air temperatures, OA fraction, and mixed supply air temperature form a nasty numerical problem.  You can test without economizer on to see if it clears up.  This is a known issue and there doesn?t seem to be anyway to fix the problem on input, but the results should be okay.  



From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Jim Dirkes
Sent: Tuesday, October 23, 2012 6:50 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: RE: [EnergyPlus_Support] Exceeded Max Iterations Trouble Shooting




__._,_.___

Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=27323/stime=1351097128>

Your email settings: Individual Email|Traditional
<http://groups.yahoo.com/group/EnergyPlus_Support/join;_ylc=X3oDMTJmcTduajM5BF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3N0bmdzBHN0aW1lAzEzNTEwOTcxMjg->Change settings via the Web (Yahoo! ID required)
Change settings via email: <mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx?subject=Email Delivery: Digest>Switch delivery to Daily Digest | Switch to Fully Featured
<http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJkc3U0Z3Y5BF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2hwZgRzdGltZQMxMzUxMDk3MTI4>Visit Your Group  | <http://docs.yahoo.com/info/terms/> Yahoo! Groups Terms of Use  | <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe> Unsubscribe

__,_._,___