|
This air handler has a setpoint manager for the supply air deck temperature that is totally separate from the thermostats in the zone. Whenever the air handler is running it will run the cooling coil to target a deck temperature of 12.8C and thereby load the chiller. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of HJ I just changed the setpoint to 27 C and still the chiller is running when air temperature is 19 C. I also noticed the idf file in the email is wrong. I attached the new idf file and the output file here. The output file contains the room air temperature, setpoint temperature and chiller energy consumption
|