RE: [EnergyPlus_Support] OutdoorAirSummary dissagrees with Controller:OutdoorAir minimum outdoor air





This can happen with cycling fan operation, as opposed to continuous fan operation.

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of moe_wilensky
Sent: Tuesday, October 30, 2012 11:10 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] OutdoorAirSummary dissagrees with Controller:OutdoorAir minimum outdoor air

 

 

I have a model that has the OA set to 0.041 m3/s Flow/Zone in the Sizing:Zone object.

Controller:Outdoor Minimum Outdoor Air Flow Rate is set to auto size and returns 0.041 in the the eio.

everything runs 24 hrs. the OutdoorAirSummary in the html report give the minim air flow rate for this same zone as 0.070 ACH, which comes out to about 7 cfm (as apposed do the expected ~86 cfm)

Any insight would be very much appreciated.

-Will



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___