Why do you want to control the chiller water temperture, from the zone thermostat?
You can use a small chiller and/or large chiller to save energy, when the demand changes. When there is no cooling demand, the chiller is cycled on and off by itself to maintain the water temperature you have specified. (7°C to 12.5°C in plant sizing). You can this temperature. The master zone theremostat configuration controls the complressor of the air to air AHU system with DX cooling coil. If you use the zone theremostat to turn off the chlller and let the water temperature to rise to the ODT, there may be a long delay to cool the water down again. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: wanghaojie630@xxxxxxxxx Date: Wed, 31 Oct 2012 12:14:41 -0400 Subject: [EnergyPlus_Support] VAV AHU with Reheat Control
Hi all,
I wonder if there is a way to control the chiller based on the zone air temperature when I use VAV AHU with reheat system. People told me that the the thermostat will only control the damper. The chiller is controlled by the setpoint manager for deck temperature. If I only want to control the chiller by zone air temperature, how can I config this system? Or I can only do this with CAV? Thanks, HJ __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |